Posted December 12, 20213 yr Hi all, Could someone please confirm whether the below scenario would be possible with a 5kW Sunsynk : a) No PV coming in (lets assume its night time) b) Inverter set to supply a maximum of 3kW from the battery c) Grid connected, supplying 1500W d) 4500W of power being delivered to the 'LOAD' output Thank you! Ryan Edited December 12, 20213 yr by ryanb
December 12, 20213 yr 9 minutes ago, ryanb said: Hi all, Could someone please confirm whether the below scenario would be possible with a 5kW Sunsynk : a) No PV coming in (lets assume its night time) b) Inverter set to supply a maximum of 3kW from the battery c) Grid connected, supplying 1500W d) 4500W of power being delivered to the 'LOAD' output Thank you! Ryan Yes By "Load" do you mean load only? If so No. You can't stop the inverter from supplying non essential from battery. Edited December 12, 20213 yr by phidz Adding more information
December 13, 20213 yr Author Thank you, I have one more question : Can the Sunsynk (5kW model) deliver more than 5kW to the LOAD port. For example : If the inverter is generating 3kW from the battery, and the grid is also supplying 3kW. If so, what would be the maximum continious output power on the LOAD output? Thank you Ryan
December 13, 20213 yr 1 hour ago, ryanb said: Thank you, I have one more question : Can the Sunsynk (5kW model) deliver more than 5kW to the LOAD port. For example : If the inverter is generating 3kW from the battery, and the grid is also supplying 3kW. If so, what would be the maximum continious output power on the LOAD output? Thank you Ryan I have the same question. Also the Sunsynk (also 5k). Edited December 13, 20213 yr by maxxis
December 13, 20213 yr If there is grid available the max passthrough current is 35 amp . So about 7.7-8kw .
December 13, 20213 yr 14 hours ago, ryanb said: Thank you, I have one more question : Can the Sunsynk (5kW model) deliver more than 5kW to the LOAD port. For example : If the inverter is generating 3kW from the battery, and the grid is also supplying 3kW. If so, what would be the maximum continious output power on the LOAD output? Thank you Ryan Max I have witnessed is 7.2kw
December 14, 20213 yr Author Excellent, thank you.. Good to know because the data-sheet doesn't seem to show this spec
December 14, 20213 yr 1 hour ago, ryanb said: Excellent, thank you.. Good to know because the data-sheet doesn't seem to show this spec See attached...not sure of exactly what your inverter code is, but the 5Kw inverter allows for 35A pass through