Narada NPFC Tian Power BMS protocol


SolarConvert

Recommended Posts

Hi all, I thought I would document my findings of the Tian Power BMS protocol used in my Narada 48NPFC100 battery whilst I was attempting to establish why it did not work with my Deye inverter. Of note is that the exact same battery model is known to use a Shinwa BMS as well, but mine uses a Tian Power one, specifically TP-ND1530.

Firstly I wanted to thank @shanghailoz for documenting the same thing here for the Revov batteries, which also use a Tian Power BMS, without which I would have struggled a lot more. Also thank you @zivva for pointing me in the right direction for the BMS manufacturer.

I also peeked at the code of the BMS software to decipher how certain fields are calculated.

The protocol follows.

 

Preamble

Firstly, all data sent appears to have a header, body and CRC check. For example:

7e 01 01 00 fe 0d

The first byte is either 7c or 7e according to the software. In my case it is always 7e.

The second byte is the DIP switch setting on the battery and corresponds to the following in the software:

image.png.5bfa076f6f2d4d684c6e235c855ce4b6.png

The third byte is the function code, which you will see several examples of below, such as "read data", "read BMS time", "read BMS version", "read serial number".

The fourth byte is the length of the payload supplied as part of the function call - most "read" type functions will not include a payload and this parameter will be 00, but the "write" functions would have a payload. If there is a payload, it would follow this byte.

The last two bytes are the CRC check.

The response is structured in a similar way:

7e 01 01 56 ... f2 0d

The first three bytes are an echo of what the request was, the fourth byte indicates the response length followed by the response bytes, and finally we have the CRC check.

 

Function 1 - Read data

7e 01 01 00 fe 0d

This allows you to read almost everything that is displayed on the first tab of the BMS software.

The response will look as follows:

7e 01 01 56 01 0f 0c e1 0c e2 0c e2 0c e3 0c e3
0c e5 0c e5 0c e4 0c e4 0c e4 0c e2 0c e2 0c e2
0c e3 0c e5 02 01 75 30 03 01 16 74 04 01 27 10
05 06 00 44 00 45 00 45 00 44 40 46 20 45 06 05
00 00 00 00 00 00 00 00 00 00 07 01 00 81 08 01
13 54 09 01 27 10 0a 01 00 00 f2 0d

The response body for this function is a data map structured as follows: data entry index, number of high/low byte pairs, the high/low byte pairs.

Data 1 - Cell count and cell voltages

01 0f 0c e1 0c e2 0c e2 0c e3 0c e3 0c e5 0c e5 0c e4 0c e4 0c e4 0c e2 0c e2 0c e2 0c e3 0c e5

The second byte is the number of cells - this is 15 for a 15 cell battery like mine or 16 cells for Revov. The individual cell voltages follow as high/low pairs which need to be divided by 1000, for example, 0ce1 maps to 3297 which means 3.297V. Since my battery has 15 cells, there would be 15 individual cell voltages.

Data 2 - Current

02 01 75 30

This is a tricky one. 7530 hex maps to 30000 decimal. The BMS software works it out as:

current_in_amps = (30000 - value_of_item_2) / 100

This item therefore has an offset of 30000 and a scaling factor of 0.01. So when the charge current is 0, the BMS will return 30000, therefore (30000 - 30000) / 100 = 0 amps. When the charge current is 10 amps, the BMS would return 29000, therefore (30000 - 29000) / 100 = 10 amps. When the charge current is -10 amps, the BMS would return 31000, therefore (30000 - 31000) / 100 = -10 amps. Furthermore, charge/discharge time remaining is calculated based on max battery capacity in amps divided by current in amps.

Data 3 - Remaining capacity

03 01 16 74

This value needs to be divided by 100 to get Ah. In this case I have 1674 hex or 5748 decimal, so 57.48Ah left of my 100Ah battery, therefore the SOC is 57.48%.

Data 4 - Full capacity

04 01 27 10

Divide by 100 to get full battery capacity in Ah. 2710 in hex is 10000 in decimal, so I have a 100Ah battery.

Data 5 - Temperatures

05 06 00 44 00 45 00 45 00 44 40 46 20 45

In my case there are 6 temperatures corresponding to the following screenshot:

image.png.a3819eaf342c03a3b421c9da01608e41.png

In the Revovs the number of temperatures listed are different. The last two appear to be important ones.

Each temperature value is calculated as:

temp_value = (bms_temp_value & 0xFF) - 50

Data 6 - Alarm bits

06 05 00 00 00 00 00 00 00 00 00 00

These can be mapped to (a) very specific alarm code(s). I can get these if there is interest.

Data 7 - Cycles

07 01 00 81

This represents the number of cycles of the battery, so 129 in my case.

Data 8 - Voltage

08 01 13 54

The total voltage of the battery. The number needs to be divided by 100, so 49.48V in my case.

Data 9 - State of Health

09 01 27 10

The SOH of the battery. Needs to be divided by 100, so 100% in my case.

Data 10 - ALM bytes

0a 01 00 00

This corresponds to the ALM light on the battery and what it means.

 

Function 67 - Read protection parameters

Request:

7e 01 43 00 fe 0d

Response:

7e 01 43 94 00 02 0e 10 01 02 03 e8 02 02 0d ac
03 02 0a f0 04 02 03 e8 05 02 0c 1c 06 02 15 4a
07 02 03 e8 08 02 14 c8 09 02 11 94 0a 02 03 e8
0b 02 13 88 0c 02 1f 40 0d 02 03 e8 0e 02 1b 58
0f 02 1f 40 10 02 03 e8 11 02 1b 58 12 02 00 69
13 02 0f a0 14 02 00 5f 15 02 00 32 16 02 0f a0
17 02 00 3c 18 02 00 69 19 02 0f a0 1a 02 00 5f
1b 02 00 32 1c 02 0f a0 1d 02 00 3c 1e 02 00 8c
1f 02 0f a0 20 02 00 87 21 02 00 0a 22 02 00 0f
23 02 03 20 24 02 01 f4 de 0d

This is another data map which ultimately gets translated into the following, with the necessary scaling factors applied:

{
  "cell_ov_start": 3.6,
  "cell_ov_delay": 1000,
  "cell_ov_stop": 3.5,
  "cell_uv_start": 2.8,
  "cell_uv_delay": 1000,
  "cell_uv_stop": 3.1,
  "pack_ov_start": 54.5,
  "pack_ov_delay": 1000,
  "pack_ov_stop": 53.2,
  "pack_uv_start": 45.0,
  "pack_uv_delay": 1000,
  "pack_uv_stop": 50.0,
  "charge_oc_start": 80.0,
  "charge_oc_delay": 1000,
  "charge_oc_stop": 70.0,
  "discharge_oc_start": 80.0,
  "discharge_oc_delay": 1000,
  "discharge_oc_stop": 70.0,
  "cell_ot_start": 55,
  "cell_ot_delay": 4000,
  "cell_ot_stop": 45,
  "cell_ut_start": 0,
  "cell_ut_delay": 4000,
  "cell_ut_stop": 10,
  "env_ot_start": 55,
  "env_ot_delay": 4000,
  "env_ot_stop": 45,
  "env_ut_start": 0,
  "env_ut_delay": 4000,
  "env_ut_stop": 10,
  "mos_ot_start": 90,
  "mos_ot_delay": 4000,
  "mos_ot_stop": 85,
  "capacity_low_start": 10,
  "capacity_low_stop": 15,
  "volt_diff_start": 800,
  "volt_diff_stop": 500
}

 

Function 51 - Read BMS version

The request is as follows:

7e 01 33 00 fe 0d

The response body is a string, such as:

7e 01 33 18 54 50 2d 4e 44 31 35 33 30 2d 31 35 53 31 30 30 41 2d 56 31 2e 30 2e 30 2e 0d

Which in my case maps to: TP-ND1530-15S100A-V1.0.0

 

Function 66 - Read PCB barcode

Request:

7e 01 42 00 fc 0d

Response body is a string as above.

 

Function 220 - Read serial number

Request:

7e 01 dc 03 06 00 00 c2 0d

Response body is a string as above.

 

Function 69 - Read BMS time

Request:

7e 01 45 00 fe 0d

Response:

7e 01 45 06 16 07 08 14 3b 16 48 0d

To convert the above to a valid date time, prepend "20" and then concatenate the rest of the bytes which represent yy, MM, dd, hh, mm, ss, so in the above example: 2022-07-08 20:59:22.

 

There are many "write"-type functions too but I would be wary of using those.

I hope the above is useful to someone. I will post more useful ones if I find any.

Edited by SolarConvert
Clarified charge current and temperatures, added protection data
Link to comment
Share on other sites

  • 1 month later...

Thanks @shanghailoz

One command that the Deye inverter does issue is the following, but I have yet to decipher what this one does.

Command:

7e 01 43 00 fe 0d

Response:

7e 01 43 94 00 02 0e 10 01 02 03 e8 02 02 0d ac
03 02 0a f0 04 02 03 e8 05 02 0c 1c 06 02 15 4a
07 02 03 e8 08 02 14 c8 09 02 11 94 0a 02 03 e8
0b 02 13 88 0c 02 1f 40 0d 02 03 e8 0e 02 1b 58
0f 02 1f 40 10 02 03 e8 11 02 1b 58 12 02 00 69
13 02 0f a0 14 02 00 5f 15 02 00 32 16 02 0f a0
17 02 00 3c 18 02 00 69 19 02 0f a0 1a 02 00 5f
1b 02 00 32 1c 02 0f a0 1d 02 00 3c 1e 02 00 8c
1f 02 0f a0 20 02 00 87 21 02 00 0a 22 02 00 0f
23 02 03 20 24 02 01 f4 de 0d                  

I can see the data map but do not yet know what each item means.

Reformatted:

7e 01 43 94
00 02 0e 10
01 02 03 e8
02 02 0d ac
03 02 0a f0
04 02 03 e8
05 02 0c 1c
06 02 15 4a
07 02 03 e8
08 02 14 c8
09 02 11 94
0a 02 03 e8
0b 02 13 88
0c 02 1f 40
0d 02 03 e8
0e 02 1b 58
0f 02 1f 40
10 02 03 e8
11 02 1b 58
12 02 00 69
13 02 0f a0
14 02 00 5f
15 02 00 32
16 02 0f a0
17 02 00 3c
18 02 00 69
19 02 0f a0
1a 02 00 5f
1b 02 00 32
1c 02 0f a0
1d 02 00 3c
1e 02 00 8c
1f 02 0f a0
20 02 00 87
21 02 00 0a
22 02 00 0f
23 02 03 20
24 02 01 f4
de 0d

Since this is the first call that the inverter makes to the BMS, these must be the parameters that the inverter expects back from the BMS.
When I have time I will try to dig deeper, just posting it here for now.

Link to comment
Share on other sites

  • 4 weeks later...

So to get the current in amps, you need the following formula

Current = (30000 - value_of_item_2) / 100

30000 is a static value from which you need to subtract the value of item 2 returned by the BMS. I assume that Tian Power did this so that only unsigned values are returned by the BMS when queried, therefore some items not only have a scaling factor but also an offset to subtract from, if that makes sense?

I'll update the first post with the latest info I have - there is a lot of new info.

Link to comment
Share on other sites

3 hours ago, SolarConvert said:

So to get the current in amps, you need the following formula

Current = (30000 - value_of_item_2) / 100

30000 is a static value from which you need to subtract the value of item 2 returned by the BMS. I assume that Tian Power did this so that only unsigned values are returned by the BMS when queried, therefore some items not only have a scaling factor but also an offset to subtract from, if that makes sense?

I'll update the first post with the latest info I have - there is a lot of new info.

Awesome, got it now .. thx

Link to comment
Share on other sites

  • 3 months later...
  • 1 month later...
On 2022/07/12 at 3:08 AM, SolarConvert said:

Hi all, I thought I would document my findings of the Tian Power BMS protocol used in my Narada 48NPFC100 battery whilst I was attempting to establish why it did not work with my Deye inverter. Of note is that the exact same battery model is known to use a Shinwa BMS as well, but mine uses a Tian Power one, specifically TP-ND1530.

Firstly I wanted to thank @shanghailoz for documenting the same thing here for the Revov batteries, which also use a Tian Power BMS, without which I would have struggled a lot more. Also thank you @zivva for pointing me in the right direction for the BMS manufacturer.

I also peeked at the code of the BMS software to decipher how certain fields are calculated.

The protocol follows.

 

Preamble

Firstly, all data sent appears to have a header, body and CRC check. For example:

7e 01 01 00 fe 0d

The first byte is either 7c or 7e according to the software. In my case it is always 7e.

The second byte is the DIP switch setting on the battery and corresponds to the following in the software:

image.png.5bfa076f6f2d4d684c6e235c855ce4b6.png

The third byte is the function code, which you will see several examples of below, such as "read data", "read BMS time", "read BMS version", "read serial number".

The fourth byte is the length of the payload supplied as part of the function call - most "read" type functions will not include a payload and this parameter will be 00, but the "write" functions would have a payload. If there is a payload, it would follow this byte.

The last two bytes are the CRC check.

The response is structured in a similar way:

7e 01 01 56 ... f2 0d

The first three bytes are an echo of what the request was, the fourth byte indicates the response length followed by the response bytes, and finally we have the CRC check.

 

Function 1 - Read data

7e 01 01 00 fe 0d

This allows you to read almost everything that is displayed on the first tab of the BMS software.

The response will look as follows:

7e 01 01 56 01 0f 0c e1 0c e2 0c e2 0c e3 0c e3
0c e5 0c e5 0c e4 0c e4 0c e4 0c e2 0c e2 0c e2
0c e3 0c e5 02 01 75 30 03 01 16 74 04 01 27 10
05 06 00 44 00 45 00 45 00 44 40 46 20 45 06 05
00 00 00 00 00 00 00 00 00 00 07 01 00 81 08 01
13 54 09 01 27 10 0a 01 00 00 f2 0d

The response body for this function is a data map structured as follows: data entry index, number of high/low byte pairs, the high/low byte pairs.

Data 1 - Cell count and cell voltages

01 0f 0c e1 0c e2 0c e2 0c e3 0c e3 0c e5 0c e5 0c e4 0c e4 0c e4 0c e2 0c e2 0c e2 0c e3 0c e5

The second byte is the number of cells - this is 15 for a 15 cell battery like mine or 16 cells for Revov. The individual cell voltages follow as high/low pairs which need to be divided by 1000, for example, 0ce1 maps to 3297 which means 3.297V. Since my battery has 15 cells, there would be 15 individual cell voltages.

Data 2 - Current

02 01 75 30

This is a tricky one. 7530 hex maps to 30000 decimal. The BMS software works it out as:

current_in_amps = (30000 - value_of_item_2) / 100

This item therefore has an offset of 30000 and a scaling factor of 0.01. So when the charge current is 0, the BMS will return 30000, therefore (30000 - 30000) / 100 = 0 amps. When the charge current is 10 amps, the BMS would return 29000, therefore (30000 - 29000) / 100 = 10 amps. When the charge current is -10 amps, the BMS would return 31000, therefore (30000 - 31000) / 100 = -10 amps. Furthermore, charge/discharge time remaining is calculated based on max battery capacity in amps divided by current in amps.

Data 3 - Remaining capacity

03 01 16 74

This value needs to be divided by 100 to get Ah. In this case I have 1674 hex or 5748 decimal, so 57.48Ah left of my 100Ah battery, therefore the SOC is 57.48%.

Data 4 - Full capacity

04 01 27 10

Divide by 100 to get full battery capacity in Ah. 2710 in hex is 10000 in decimal, so I have a 100Ah battery.

Data 5 - Temperatures

05 06 00 44 00 45 00 45 00 44 40 46 20 45

In my case there are 6 temperatures corresponding to the following screenshot:

image.png.a3819eaf342c03a3b421c9da01608e41.png

In the Revovs the number of temperatures listed are different. The last two appear to be important ones.

Each temperature value is calculated as:

temp_value = (bms_temp_value & 0xFF) - 50

Data 6 - Alarm bits

06 05 00 00 00 00 00 00 00 00 00 00

These can be mapped to (a) very specific alarm code(s). I can get these if there is interest.

Data 7 - Cycles

07 01 00 81

This represents the number of cycles of the battery, so 129 in my case.

Data 8 - Voltage

08 01 13 54

The total voltage of the battery. The number needs to be divided by 100, so 49.48V in my case.

Data 9 - State of Health

09 01 27 10

The SOH of the battery. Needs to be divided by 100, so 100% in my case.

Data 10 - ALM bytes

0a 01 00 00

This corresponds to the ALM light on the battery and what it means.

 

Function 67 - Read protection parameters

Request:

7e 01 43 00 fe 0d

Response:

7e 01 43 94 00 02 0e 10 01 02 03 e8 02 02 0d ac
03 02 0a f0 04 02 03 e8 05 02 0c 1c 06 02 15 4a
07 02 03 e8 08 02 14 c8 09 02 11 94 0a 02 03 e8
0b 02 13 88 0c 02 1f 40 0d 02 03 e8 0e 02 1b 58
0f 02 1f 40 10 02 03 e8 11 02 1b 58 12 02 00 69
13 02 0f a0 14 02 00 5f 15 02 00 32 16 02 0f a0
17 02 00 3c 18 02 00 69 19 02 0f a0 1a 02 00 5f
1b 02 00 32 1c 02 0f a0 1d 02 00 3c 1e 02 00 8c
1f 02 0f a0 20 02 00 87 21 02 00 0a 22 02 00 0f
23 02 03 20 24 02 01 f4 de 0d

This is another data map which ultimately gets translated into the following, with the necessary scaling factors applied:

{
  "cell_ov_start": 3.6,
  "cell_ov_delay": 1000,
  "cell_ov_stop": 3.5,
  "cell_uv_start": 2.8,
  "cell_uv_delay": 1000,
  "cell_uv_stop": 3.1,
  "pack_ov_start": 54.5,
  "pack_ov_delay": 1000,
  "pack_ov_stop": 53.2,
  "pack_uv_start": 45.0,
  "pack_uv_delay": 1000,
  "pack_uv_stop": 50.0,
  "charge_oc_start": 80.0,
  "charge_oc_delay": 1000,
  "charge_oc_stop": 70.0,
  "discharge_oc_start": 80.0,
  "discharge_oc_delay": 1000,
  "discharge_oc_stop": 70.0,
  "cell_ot_start": 55,
  "cell_ot_delay": 4000,
  "cell_ot_stop": 45,
  "cell_ut_start": 0,
  "cell_ut_delay": 4000,
  "cell_ut_stop": 10,
  "env_ot_start": 55,
  "env_ot_delay": 4000,
  "env_ot_stop": 45,
  "env_ut_start": 0,
  "env_ut_delay": 4000,
  "env_ut_stop": 10,
  "mos_ot_start": 90,
  "mos_ot_delay": 4000,
  "mos_ot_stop": 85,
  "capacity_low_start": 10,
  "capacity_low_stop": 15,
  "volt_diff_start": 800,
  "volt_diff_stop": 500
}

 

Function 51 - Read BMS version

The request is as follows:

7e 01 33 00 fe 0d

The response body is a string, such as:

7e 01 33 18 54 50 2d 4e 44 31 35 33 30 2d 31 35 53 31 30 30 41 2d 56 31 2e 30 2e 30 2e 0d

Which in my case maps to: TP-ND1530-15S100A-V1.0.0

 

Function 66 - Read PCB barcode

Request:

7e 01 42 00 fc 0d

Response body is a string as above.

 

Function 220 - Read serial number

Request:

7e 01 dc 03 06 00 00 c2 0d

Response body is a string as above.

 

Function 69 - Read BMS time

Request:

7e 01 45 00 fe 0d

Response:

7e 01 45 06 16 07 08 14 3b 16 48 0d

To convert the above to a valid date time, prepend "20" and then concatenate the rest of the bytes which represent yy, MM, dd, hh, mm, ss, so in the above example: 2022-07-08 20:59:22.

 

There are many "write"-type functions too but I would be wary of using those.

I hope the above is useful to someone. I will post more useful ones if I find any.

I want Alarm code message. from Alarm code byte and Alarm bit.  thank you

Link to comment
Share on other sites

  • 1 month later...

Thanks so much for this post @SolarConvert – this was key in getting prometheus hooked up to my system. Have you (or anybody else here) been able to reverse engineer the CRC or checksum algorithm? I've spent hours on this and have been totally defeated. Right now I have a hardcoded map of requests I care about for each battery address, which I just copied from the software... but it's a very dirty way to go about things.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...