Deye 8kw

Featured Replies

Hi guys, anyone with a Deye 8kw and 2x5.5 Hubbles. Could someone advise what the charge and discharge AH be? Hubble says 110AH on the website but if you have two batteries should it still be 110AH. Also mines always revert to 100AH even if I try 110AH.

  • Author
On 2022/08/06 at 12:04 AM, Jaxone said:

Try to put the settings like in the manual.
Your Low Power , Shutdown and restart might be to close to each other.

image.thumb.png.1895f6ea7e99f8961fcc8eb3bc96b88b.png

What would the correct AH be once I do the above

I wouldn't panic about the charge rate, you do not need or probably want to charge the batteries at such high a rate, if you are using solar panels to recharge, let them take 4 to 6 hours, kinder on the batteries as well and will allow you some of the solar to be used to run whatever else is consuming electrons around the place.

My battery is set for 80A, which is C/2 app. and this graph for right now, shows you it nearly fully charged by now... and briefly the charge rate reached 50A at 09:10 this morning, but overall, getting to 1C or C/2 charge rates is usually not neccesary, after all, C/2 would imply fully charged in 2 hours, but since you have many more daylight hours, I'd say, moenie panic nie... even if you were to be able to set it to 1C, mostly between the inverter and the BMS of the battery, they likely will be choosing a lower charging rate, over which you have no control...

Screenshot 2022-08-11 at 13.21.43.png

  • Author

Thank you for this. I had an issue with a F56 fault error but it only occurs when there's load shedding and if my discharge is say at 6kw or so it gives me that error

  • 2 weeks later...

AM-2 are 1C rated.

The Deye 8k has a limit of 185A for Charge/Discharge @48V so 8.88kW

I have 4 batteries amd 6.4kWp solar and use 150A/7.2kW.

Edited by system32

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.