Newbie needs help with solar panel planning

Featured Replies

Open circuit voltage cannot be higher than 150v,  max voltage on a system is 72 vdc . Need help in finding the best  suited solar pannels with proffered setup whether in parallel or series or series parallel.

 

I have 2 x 360w and 1 x 350w pannels.

 

Thank you in advance.

You will need to supply the voltages of the panels to make an informed answer. You might get all 3 in series if the voltage is low enough, but maybe only 2 with a low voltage scc.

@ANDREWOSMOND,

Your Voc on those panels should be around 47V (I have 365W CanadianSolar). 

2P will give you 94V @ 25 Deg C. That you will see early mornings/late afternoons. However, you also need to compensate for some minus 5 deg temps here on the highveld.

Temp Co-eff. = +- 0.28%/Deg C. Thus 25 to (max) -5 Deg (extreme) = 30 deg. 

0.28 * 30 = 8.4%. Thus 94V + 8V = 102V. So still within the Voc max of your system. 3S should be around 153V, so not a good plan.

Under load, you will see a voltage drop (in theory 44V x 2 = 88V) for 2S. Also too much for your system. 

So 1P/2P/3P may be the only option, depending on the max current that your system can handle. The Imp for my 365W panels is 7.21 Amp, so your should be close/less that that.

Hope this helps somewhat.

6 minutes ago, Sidewinder said:

@ANDREWOSMOND,

Your Voc on those panels should be around 47V (I have 365W CanadianSolar). 

2P will give you 94V @ 25 Deg C. That you will see early mornings/late afternoons. However, you also need to compensate for some minus 5 deg temps here on the highveld.

Temp Co-eff. = +- 0.28%/Deg C. Thus 25 to (max) -5 Deg (extreme) = 30 deg. 

0.28 * 30 = 8.4%. Thus 94V + 8V = 102V. So still within the Voc max of your system. 3S should be around 153V, so not a good plan.

Under load, you will see a voltage drop (in theory 44V x 2 = 88V) for 2S. Also too much for your system. 

So 1P/2P/3P may be the only option, depending on the max current that your system can handle. The Imp for my 365W panels is 7.21 Amp, so your should be close/less that that.

Hope this helps somewhat.

Full details of panels on this topic.

 

  • Moderator2 changed the title to Newbie needs help with solar panel planning

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.