Axpert MAX II 8KVA

Featured Replies

On 2023/12/02 at 8:41 AM, Kurtbe said:

Hi Rozsda,

SBU: Utility only starts working when battery and solar are 'out'. It will then charge the batteries at the speed set in program program 11. It will also provide power to the house. When solar power is generated, this power will be sent to whatever demands power: this can be the batteries or the house. Only when batteries have sufficiënt power, you will return to battery mode.

Two remarks however:

  • EVEN in battery mode The Axpert will continuously take 70W from the grid. That is why I (and you) use the dry contact and a relay to avoid that.
  • But then (in SBU mode) it is ONLY the settings from program 12 and 13 that make the Axpert switch to and from the grid. (Unless you cut off manually)

I thought that in Line mode you connect the input to the output. The solar only charges the battery.
I looked at the block diagram. The output and input are connected to the DC/AC converter in line mode.
One more question! In SBU mode, with a discharged battery, is there no risk of feeding back to the network?

  • Replies 115
  • Views 17.8k
  • Created
  • Last Reply

Top Posters In This Topic

Most Popular Posts

  • Wait, this is actually an Axpert Max II with the round non-removable display? I based my assumptions on my notes that 46.xx is an Axpert Max 1 firmware. I suppose it's possible that Max 1 and Max

  • AFAIK the inverter will only switch to grid when reaching a low battery level. If you look at the table you you will with the relay switch to grid the moment you reach the alarm level.  Unless I

  • No, the two amps is at the battery end of the "battery charger". So it's about 2 A x 50 V (assuming a 48 V model) x 8 h = 800Wh. For a 24 V model halve that. But the self consumption is about an

Posted Images

7 hours ago, Rozsda said:

In SBU mode, with a discharged battery, is there no risk of feeding back to the network?

I would think that there is always a slight risk of grid feeding whenever the battery is charging and the DC<->AC converter is operating, and the AC side of the DC<->AC converter is connected to AC-in, which it would be in the above configuration.

  • 2 weeks later...
On 2023. 12. 11. at 13:53, Coulomb said:

Igen. Ez a lehetőség a kijelző firmware-verziója (1) 22.16 és 22.20 között jelent meg. Tehát csak frissítsen a firmware 22.20-as verziójára, és működtesse a BMS-kábelt. 22.20 van ebben a bejegyzésben ; ott ne használja a fő firmware-t, mert az egy 10 kW-os Max II modellhez tartozik. A 22.20 egy "egységes" firmware, bármelyik kijelzőlapkakészleten működnie kell, szóval ne aggódj amiatt, hogy a firmware-számból hiányzik az első 1.

Lehetséges, hogy frissítenie kell a fő (U1) firmware-t is. A SOC funkció működéséhez dokumentálatlan QDOP parancsot kell küldenie a kijelzőnek.

Hello.
Merry Christmas!
Now I have time to deal with my hobby!:))
I use the SOLTARO protocol and for me the 12-13 programs can still be set based on voltage! It is not possible to set based on SOC! What am I messing up?
I use display firmware 22.20.

17 hours ago, Rozsda said:

I use the SOLTARO protocol and for me the 12-13 programs can still be set based on voltage! It is not possible to set based on SOC! What am I messing up?

My analysis of the display code (I happen to have 22.20 to analyse) is that the DSP has to respond correctly to the undocumented command QDOP in order for settings 12, 13 and 29 to work in SoC instead of voltage. So it's possible that your main firmware isn't recent enough for this.

What is you main (U1) firmware version?

Edited by Coulomb

2 hours ago, Coulomb said:

A megjelenítési kód elemzése (nekem történetesen 22.20 van az elemzéshez) az, hogy a DSP-nek megfelelően kell reagálnia a nem dokumentált QDOP parancsra, hogy a 12, 13 és 29 beállítások SoC-ben működjenek feszültség helyett. Tehát lehetséges, hogy a fő firmware nem elég friss ehhez.

Mi a fő (U1) firmware verziód?

Hello.
At my request, you modified it for me!
This is it.

 

14 hours ago, Rozsda said:

At my request, you modified it for me!
This is it.

[ 281.05 ]

Sorry, so many respondents to remember.

The problem is, none of the x81.xx firmwares support QDOP! It seems that this is a fairly recent development.

The latest 81.xx that I have is 81.07 from September 2023. 82.06 has it (for 10 kW model), and it's hex file is dated November 2023. So it looks like you'll have to wait for a more recent 81.xx firmware to appear, and then wait for me to patch it. I had a quick look at the usual suspects; nothing new.

Edit: Or you could complain to your supplier that you don't have the SoC functionality that others have, and ask if there is a firmware update available to fix it.

Edited by Coulomb

On 2023/12/28 at 5:51 AM, Coulomb said:

The latest 81.xx that I have is 81.07 from September 2023. 82.06 has it (for 10 kW model), and it's hex file is dated November 2023. So it looks like you'll have to wait for a more recent 81.xx firmware to appear, and then wait for me to patch it.

Merry Christmas to all and a happy new year!

 

I am running 81.07 too on the max ii 8kW. I now understand that users of that type are "the odd ones" out, since most others DO have the option to use SOC instead of Voltage. 😟😡

Complaining to the (local) supplier here (Valencia Spain) will have no effect. They could not care less.

For now, I have left Spain for an indefinite period and the Axpert is on its own. Disconnected from the gid by a relay. I have no monitoring capacity now because the Network is also down... I cross my fingers that it may remain properly working till I return.

May I be so curious Coulomb as to ask what it is that you "patch" in the software?

Greets to all.

Kurt

On 2023/12/11 at 1:53 PM, Coulomb said:

So just update to display firmware version 22.20 and get your BMS cable working.

Unfortunately, this is NOT the solution...

And I guess that running the firmware for the 10kW would also be the wrong choice to make...?

9 hours ago, Kurtbe said:

May I be so curious Coulomb as to ask what it is that you "patch" in the software?

I patch the hex file, a loooong string of 0-F characters plus a few spaces and a colon. These characters represent machine code (instructions and data, mostly instructions) that implement the firmware.

I have a disassembler, so I can work in assembly language. Few programmers know any assembly language these days, and even fewer know the C2000 DSP assembly language. I have a few tools to help me automate the patching process. If you're curious, you can read the .asm file that I put into the more recent patched firmware zip files. But that doesn't show the 90% of the work, which is working out what changes to make, and how the firmware works in the first place.

There is also my JTAG post, though it's not directly relevant.

9 hours ago, Kurtbe said:

Unfortunately, this is NOT the solution...

Yes, I've edited that post now. Thanks for reminding me.

 

9 hours ago, Kurtbe said:

And I guess that running the firmware for the 10kW would also be the wrong choice to make...?

I've never heard of anyone trying it. I assume it would be a huge disaster; there are all sort of control system constants in there that depend sensitively on the hardware and the power level. And of course, you could overload your inverter and it would not protect itself, thinking that it's running on 10 kW hardware.

So yes, that would be the wrong choice.

12 hours ago, Coulomb said:

I patch the hex file, a loooong string of 0-F characters plus a few spaces and a colon. These characters represent machine code (instructions and data, mostly instructions) that implement the firmware.

Thanks for the info...

But my knowledge of coding is just about null and void. Nor do I have any experience. 

The question actually was: what is the difference between the 'Patched' version and the regular one? Do they work differently on a practical level, what is actually patched? (sort of hoping that you might be able to "patch" program 12 & 13 and get the SOC in there...) 🫢

I am now in correspondence with the seller.
I complained that the 12-13 program does not work based on SOC and I would like to receive the latest firmware.
Now we are at the point where your engineer wants to look at the inverter remotely. And enter the wifi password of the inverter. But nothing like that!
This is going to be a long process! :((

21 hours ago, Kurtbe said:

what is the difference between the 'Patched' version and the regular one? Do they work differently on a practical level, what is actually patched?

Well, that depends on the patch. It's a bit like saying if you edit a document, how does the meaning change? 

Let's take a simple patch: fixing the premature float bug. This can be done by changing two characters in the hex file (one is so that the checksum is still valid given the other change). The effect is that a branch will be taken where in the original firmware it would not be taken. The high level effect of that is that the battery will charge until both the current is low, but also the battery voltage must be near the bulk voltage setting. Previously it only had to be near the float voltage setting. In practice, I usually change the code so that the version number reported by the QVFW command is different, so you can quickly tell that you are running the patched firmware, and the patched firmware you thought you were updating to. 

A contrasting case: fully patched firmware. Now the display behaves differently, the firmware responds to one of the commands very differently, and you need a pair of manuals for all the changes. Yet still 99% of the firmware is the same. You can diff the new and old hex files to prove it. 

21 hours ago, Kurtbe said:

sort of hoping that you might be able to "patch" program 12 & 13 and get the SOC in there...

That's actually very hard, because it involves several new commands (not impossible by itself), but these commands are not documented. So at least for the foreseeable future, that's not practical. Sorry. 

Edited by Coulomb

On 2023. 12. 28. at 5:51, Coulomb said:

[ 281.05 ]

Sajnálom, sok válaszadót kell emlékezni.

A probléma az, hogy egyik x81.xx firmware sem támogatja a QDOP-t! Úgy tűnik, ez egy meglehetősen friss fejlemény.

A legújabb 81.xx, ami nálam van, a 81.07 2023. szeptemberi. A 82.06-os rendelkezik (10 kW-os modellhez), a hexa fájlja pedig 2023. novemberi. Úgy tűnik tehát, hogy várnia kell egy újabb 81.xx-re. firmware jelenik meg, majd várja meg, amíg kijavítom. Gyorsan megnéztem a szokásos gyanúsítottakat; semmi új.

Szerkesztés: Vagy panaszt tehet a szállítójának, hogy nem rendelkezik olyan SoC-funkcióval, mint másoknak, és megkérdezheti, hogy van-e elérhető firmware-frissítés a javításhoz.

Hello.
I received firmware from the supplier.
DSP.: 81.07
Display: 22.21
I already read that 81.07 exists, but 22.11 is still new to me.
What I complained about is that there is no SOC-based switching. I got the new firmware for this.
Do you have any information about these firmwares?
I haven't done the update yet. I'm planning for the weekend because the electricity needs to be disconnected from the apartment.

13 minutes ago, Rozsda said:

Display: 22.21
I already read that 81.07 exists, but 22.11 is still new to me.

22.21 is new to me too. Please post it here, or PM me a link to it, or just attach it in a PM if that works.

14 minutes ago, Rozsda said:

What I complained about is that there is no SOC-based switching. I got the new firmware for this.
Do you have any information about these firmwares?

As I mentioned in the post you quoted, none of the 81.xx firmwares up to 81.07 support the QDOP command, which by my analysis is required for the SoC support to work. My guess is that 22.21 adds the display end support (it's not present in 22.20). But my understanding is that you need both ends for it to work. To be sure, you should reflash these two, let is know, and if I'm right, ask for a later DSP firmware. Probably don't tell them that pesky Coulomb says so 🤔, just that you already had 81.07, so it seems like that's what needs to change.

On 2024/01/04 at 12:06 PM, Coulomb said:

That's actually very hard, because it involves several new commands (not impossible by itself), but these commands are not documented. So at least for the foreseeable future, that's not practical. Sorry. 

Thanks for the info! At least I now know.

Let's hope that Rozsda gets somewhere with his negotiations with the Axpert people...

Greetings, Kurt

15 minutes ago, Coulomb said:

Probably don't tell them that pesky Coulomb says so 🤔, just that you already had 81.07, so it seems like that's what needs to change

I don't mind putting in my bit of pressure, only who is "them"? If anyone can give me an e-mail address on how to reach Axpert, I'd be happy to oblige. 

I sent this to Voltronic Power Contact Us:

"Hi, 

I recently installed an Axpert max ii 8kW. I am contemplating installing more units in different locations, but I am missing an important feature wich seems to be working on other Axpert inverters: programming program 12 & 13 by SOC rather than Voltage.
The present firmware does not allow this. Is there any chance that this might change anytime soon (like in 3-4 months)?

Greetings, Kurt"

Wonder whether I will get a reply. I'll keep you posted.

16 hours ago, Kurtbe said:

Wonder whether I will get a reply.

I doubt it. Voltronic's customers are the resellers, not the inverter owners. I think that they're expecting contact along the lines of "How much will 100 units cost, and when can I have them?"! 

On 2024. 01. 05. at 12:17, Coulomb said:

22. 2 1 nekem is új. Kérlek tedd fel ide, vagy küldj egy linket PM-ben, vagy csak csatold PM-ben, ha működik.

Ahogy az idézett bejegyzésben említettem, a 81.xx firmware 81.07-ig egyike sem támogatja a QDOP parancsot, amely elemzésem szerint szükséges az SoC támogatás működéséhez. Szerintem a 22.21 hozzáadja a kijelzővég támogatását (22.20-ban nincs). De úgy tudom, hogy mindkét végére szükség van, hogy működjön. Az biztos, hogy újra kell frissítenie ezt a kettőt, jelezze, és ha jól gondolom, kérjen egy későbbi DSP firmware-t. Valószínűleg ne mondd el nekik, hogy a bosszantó Coulomb ezt mondja  🤔, csak azt, hogy már megvolt a 81.07, tehát úgy tűnik, ezen kell változtatni.

Hello.
I updated the inverter!
22.21
81.07
Unfortunately, it is still not possible to set the battery SOC-based switching in menu 12 - 13! It only works on a voltage basis!
I will continue to correspond with the supplier.

2 hours ago, Rozsda said:

Hello.
I updated the inverter!
22.21
81.07
Unfortunately, it is still not possible to set the battery SOC-based switching in menu 12 - 13! It only works on a voltage basis!
I will continue to correspond with the supplier.

A little interesting!
I updated the inverter to the 81.07 factory firmware.
The weather is bad now.
Solar cable is disconnected in the inverter.
120v voltage stuck!
81.07 you won't be on the inverter for long!:)
281.05 fixed firmware not stuck!

Képernyőkép 2024-01-06 153223.png

  • 2 weeks later...
On 2024/01/06 at 5:02 AM, Coulomb said:

I doubt it. Voltronic's customers are the resellers, not the inverter owners. I think that they're expecting contact along the lines of "How much will 100 units cost, and when can I have them?"! 

You are quite right, so far they have given me the silent treatment.

On 2024/01/06 at 3:49 PM, Rozsda said:

A little interesting!
I updated the inverter to the 81.07 factory firmware.
The weather is bad now.
Solar cable is disconnected in the inverter.
120v voltage stuck!
81.07 you won't be on the inverter for long!:)
281.05 fixed firmware not stuck!

Képernyőkép 2024-01-06 153223.png

It may boil down to translation, but I understand very little of your feedback...

Anybody can shed some more light on this?

Greets, Kurt

On 2024/01/06 at 5:02 AM, Coulomb said:

I doubt it. Voltronic's customers are the resellers, not the inverter owners. I think that they're expecting contact along the lines of "How much will 100 units cost, and when can I have them?"! 

Maybe I should write to them: "How much will 1000 units that can read SOC cost, and when can I have them?"😆

4 hours ago, Kurtbe said:

Lehet, hogy ez a fordításon múlik, de nagyon keveset értek a visszajelzéseiből...

Valaki tud erre bővebb felvilágosítást adni?

Üdvözlöm, Kurt

Sorry my English is bad.
The voltage of MPPT1 can be seen in the picture.
Cloudy day. The factory firmware could not keep the panels at their working point. And from 330V it is stuck at 120V.
Coulomb modified firmware never freezes on 120v. I am grateful to him for that!
Unfortunately, my supplier cannot provide a new firmware. 81.07 is currently the latest for the 8Kw model.

12 hours ago, Rozsda said:

Sorry my English is bad.
The voltage of MPPT1 can be seen in the picture.
Cloudy day. The factory firmware could not keep the panels at their working point. And from 330V it is stuck at 120V.
Coulomb modified firmware never freezes on 120v. I am grateful to him for that!
Unfortunately, my supplier cannot provide a new firmware. 81.07 is currently the latest for the 8Kw model.

Got it now Rozsda! Thank you for taking the trouble to explain one more time.

Greetings, Kurt

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.