Setting up 2 x sunsynk 8kW inverters
Looking into a system that consists of 2 x sunsynk 8kW inverters with maxed out solar panels and 2 x 5 kW batteries.
This is a follow up on my frail care question as this  could go a long way to alleviate the backlog of washing cased by load shedding.
How would this all be linked up; batteries on one inverter or one on each etc.
Maybe there is someone who has a similar setup that could share the layout.
Hi @JohanG,
As paralleled systems are seen as one, you should also only have one battery source - connected to both inverters.
PS, I think your guestimate of 2 x 5 kW units is way undersized - You may need to double or even triple that, in order to survive LS.
3 hours ago, Sidewinder said:
Hi @JohanG,
The demand is during working hours so unless it is cloudy it will not be necessary to use the batteries
ok, just keep in mind, if a 16kW draw is attempted with only or near only batteries as source, they're likely to trip and out go the lights... unless these batteries are rated 1.5C which would allow a 15kW draw and probably survive a 16kW spike...
also... to answer the original question, one inverter set as master, the other as slave, there should be a comms cable between them, refer to the manual... then the batteries should be paralleled up and connected to both inverters power wise and presumably with a CANbus interface to the master inverter, the batteries presumably also need to be set as primary and secondary with a communication cable between them...
both AC inputs paralleled up and connected to the source/grid side and both AC outputs of the two inverters paralleled up and connected to the load GFI/earth leakage switch, also remember the conatctor/relay driven by the master inverter to bind neutral and ground on the output side once the grid raises the white flag and surrenders....
Edited by Kalahari Meerkat
also...