NE F73 Error on AXPERT MKSIII

Featured Replies

Good day all, there is a fault or warning with code NE F73 on axpert MKSIII inverter, I have tried to troubleshoot but yet to fix out the cause of the issue and no solution. The 2 units connected to work in parallel but not working. Please advise 

49 minutes ago, Abbas Olatayo said:

Good day all, there is a fault or warning with code NE F73 on axpert MKSIII inverter, I have tried to troubleshoot but yet to fix out the cause of the issue and no solution. The 2 units connected to work in parallel but not working. Please advise 

Have you isolated both inverters ac output via isolation and tested each inverter in standalone (SIG) mode? You may also have to cold restart by disconnecting ac in and battery. 

F73 is unusual, i cannot see one in the manual. 

NB : wether you may know this or not, please, NEVER combine ac outputs when one or more inverter is in single mode.  I will never sleep if i am in the remotest manner responsible for this. 

Edited by BritishRacingGreen

  • Author
18 minutes ago, BritishRacingGreen said:

F73 is unusual, i cannot see one in the manual. 

 

Yes, it’s very unusual, and that’s the main reason I sought for assistance. All other connections are good, inverter works as single mode. 

1 hour ago, Abbas Olatayo said:

there is a fault or warning with code NE F73 on axpert MKSIII inverter,

According to my notes, it means output voltages inconsistent. For example, one is set to 220 V, the other set to 230 V. Obviously, this won't fly when paralleling.

Note that to change the output voltage, the inverter switch has to be OFF (so there is no output generated). Make sure you have a charging source (AC-in or PV), or do it quickly so that the inverter doesn't shut down before or as it is writing the new value to EEPROM.

The NE part just means it's a NEw machine, not yet decided if it will become a master or a slave.

Edit: Sorry it took so long to respond 😎🙃

Edited by Coulomb

  • 1 month later...

I

On 2023/03/19 at 3:07 PM, Coulomb said:

According to my notes, it means output voltages inconsistent. For example, one is set to 220 V, the other set to 230 V. Obviously, this won't fly when paralleling.

Note that to change the output voltage, the inverter switch has to be OFF (so there is no output generated). Make sure you have a charging source (AC-in or PV), or do it quickly so that the inverter doesn't shut down before or as it is writing the new value to EEPROM.

The NE part just means it's a NEw machine, not yet decided if it will become a master or a slave.

Edit: Sorry it took so long to respond 😎🙃

I can confirm this is 100% correct.

Just had the issue now on a site and one inverter was at 230v and the rest at 220v

Adjusting them all to the same voltage solved the fault.

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.