Preferred method of connecting two wires to circuit breaker?

Featured Replies

Is there a preferred method of connecting two or three wires to a single terminal of a circuit breaker?  I have seen installations where two wires are twisted around each other and then clamped in the terminal, but have also seen comments that this is very bad practice.

I see that SANS 10142-1 does not allow more than 3 wires to be connected to a single terminal.

I pretty much shove both of them in there side by side and clamp it down. End of story :-)

If one wire is multi-stranded and the other is not, then sometimes this practice yields less than optimal results (ie the thicker wire takes away most of the clamping force and the other one might not be properly clamped.

Some breakers (ABB for example) have two insertion points. This is actually there so that you can have a busbar in the one, and an additional connection on the other one, but also helps when you need to connect more than one wire.

F5354188-01.jpg.c9a3b297c787c5859a9a200dd9d572e6.jpg

 

Sparkies generally twist the wires together as it's easier to get them in and both wires are secure better together. It's better and safer to use ferrules, though there's no regulation for it (yet?) and they only cost a few rand

  • 2 years later...

Hi, I need to know according to SANS,two circuits connected under one single breaker,in coc you can count it one circuit or two,because I can't see SANS reffenrence any helpe.

 

  • 2 years later...
On 2021/11/14 at 1:25 AM, Daddy said:

Hi, I need to know according to SANS,two circuits connected under one single breaker,in coc you can count it one circuit or two,because I can't see SANS reffenrence any helpe.

 

Reviving Old Post
"
What you are looking for is SANS 10142-1:2020 Edition 3 
6: Installation Requirements
6.1.5 A Maximum of three conductors may be connected to any one terminal...
"
No Copywrite Violation intended. 
 

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.