November 16, 20241 yr Hi guys We recently added another Deye 8kW inverter to our existing Deye 8kW system and some additional solar panels After the work the latest company did, when I monitor using solar-assistant, the Grid used and Grid exported is swapped? Please see, e.g. on Nov 15 we used 4.6 and exported 10.3...: What can be done/checked to fix this please? Many thanks Ant
November 16, 20241 yr Do you have solar Assistant connected to both inverters, not just the master? I am also puzzled as to why you discharge and charge you're batteries if you can export to the grid, unless this is to offset higher charge rates at peak times?
November 16, 20241 yr Author 9 minutes ago, TimCam said: Do you have solar Assistant connected to both inverters, not just the master? I am also puzzled as to why you discharge and charge you're batteries if you can export to the grid, unless this is to offset higher charge rates at peak times? Hi I have it connected to both of them
November 16, 20241 yr 1 hour ago, anthonyhugo said: Hi guys We recently added another Deye 8kW inverter to our existing Deye 8kW system and some additional solar panels After the work the latest company did, when I monitor using solar-assistant, the Grid used and Grid exported is swapped? Please see, e.g. on Nov 15 we used 4.6 and exported 10.3...: What can be done/checked to fix this please? Many thanks Ant First thought is that the CT coil could have been fitted the wrong way around during the upgrade installation.
November 16, 20241 yr Author 3 minutes ago, GreenFields said: First thought is that the CT coil could have been fitted the wrong way around during the upgrade installation. Thanks, weird thing is the CT coil was not changed/moved (that I know of) during the upgrade but I should probably have it checked
November 16, 20241 yr 45 minutes ago, anthonyhugo said: weird thing is the CT coil was not changed/moved (that I know of) during the upgrade but I should probably have it checked Was your first inverter (with the CT coil) made Master, and the new inverter made slave?
November 16, 20241 yr Author 26 minutes ago, TimCam said: Was your first inverter (with the CT coil) made Master, and the new inverter made slave? Hi yes exactly, why?
November 16, 20241 yr If the new inverter without the CT coil was made master, this would have caused confusion, as the master must have the CT coil. 👍 Another query, on the inverter displays, is the Grid used (Paid) and Grid exported (Sold), correct or also mixed up?
November 17, 20241 yr Author 1 hour ago, TimCam said: If the new inverter without the CT coil was made master, this would have caused confusion, as the master must have the CT coil. 👍 Another query, on the inverter displays, is the Grid used (Paid) and Grid exported (Sold), correct or also mixed up? thanks! i'll check this much appreciated