April 3Apr 3 Good evening AllI trust that you are all well.I have 3 of the 7.2Kw Kodak inverters in parallel on a single phase supply and I would like to know if the timers for the Output Source Priority and Charger Source Priority must be set on all 3 the inverters or only the Master inverter?Kind RegardsGerhardK83
May 15May 15 Author Good evening AllI trust that you are all well.Since I have not received any feedback regarding the Output Source Priority and Charger Source Priority timers I decided that I will post my findings here.If the timers are set on any of the units the Output Source Priority and Charger Source Priority would change according to the timers and there must be a time difference of one hour between the timers e.g. if the SBU timer is set from 00:00 to 15:00 then the USB timer must be set from 16:00 to 23:00 otherwise the settings does not change.Kind RegardsGerhardK83
May 21May 21 Yes, I believe that 00 to 15 means starting at 00:00 and ending at 15:59:59. So from the start of the start hour to the end of the end hour, if you like. It's a strange way to specify things to me, and I suspect to a lot of people.So that means that in your example, you have all 24 hour periods covered, and there are no one hour "gaps". Edited May 21May 21 by Coulomb