Just a few things to remember when installing a Ziehl 

  • You will need the following:

Ziehl1.JPG.0ff10d32e25b5f7f23a77b1f27724fb6.JPG AND One or two 63A contactors  Schn.JPG.610aff8b461f678081e725cf29d38795.JPG

 

  • Install using the following connection diagram.
  • Ziehl.JPG.0915de11bf8da48b9e3f529290bcdb54.JPG  
  • Please remember to bridge L1 - L2 - L3 when single phase are used. 
  • Return wires (Feedback from Contactors) are not required in SA.
  • I have used 48VDC to power the unit, but you can can chose to use the grid voltage.
  • I have used grid voltage to switch the contactors. 
  • I have Chosen 63Amp Din rail mount DB contactors (Schneider) 

 

  • Putting the unit into programming mode:
  • Switch the supply on. 
  • Look at the following picture. Set.JPG.82d0e2c114f6ebe81cd6cb235cc7f597.JPG
  • The unit comes with the seal not in place. 
  • If the Led between the 2 locks are Red, slightly lift the key cover and turn it 180 degree. While turning you will see a Small blue pin like switch behind the key cover. 
  • Use the key cover and press down firmly on the blue pin for 2 seconds. 
  • The Led should turn to Green now. 
  •  Once the LED is Green you can continue with the configuration. 

 

  • Configuration:
  • There are 2 Programs to chose from
  • PRG5 is used for 230Volt Phase to Neutral, 1 or 3 Phase
  • PRG6 is used for 400Volt phase to phase systems with no Neutral. 
  • Press the UP arrow 1 time to display "InFo."
  • Press the RIGHT button 5 times to display "PR 1"
  • Press the UP button till you reach "PR 5" or "PR 6
  • Press the RIGHT button 1 time to display "no"
  • Press the DOWN button 1 time to display "YES"
  • Press the Right button.
  • The Device will reset and start with the new program. 
  • Every time a new program is selected, all the settings revert to the default settings. 
  • Changing Settings: 
  • ONLY after you selected the relevant program for your installation, you should continue to the settings. 
  • Press the UP button 2 times to get to the first Menu on the Settings LIst. 
  • Use the Right Button to Scroll through the 5 settings of each Parameter.
  • Use the UP and Down buttons to change the setting to mach the settings on the list. 
  • Once done with all 5 settings, use the UP button to scroll to the next Parameter on the list.  
  • The settings for South Africa are as follows. 
  • 1522307569_Settings1.thumb.JPG.7420bd91bdb1588d1d3bb9776e7b5ab8.JPG
  • 585382934_Settings2.JPG.dd3f82061694b313b582e7cf976e6e45.JPG
  • Once you done, remove and re-apply the power, the unit will go through a 60 Second "self check" that might be followed by another count down. 
  • Once that is complete and all conditions are within spec, the Contactors should energize. 
  • Once you are satisfied with the settings, press the blue pin till the LED turns red. 
  • Apply the seal, but dont crimp it till you are sure no one wants to check your settings.  

 

Link to comment
Share on other sites

When combined with a Victron inverter, you need only one contactor. The NRS097 requirement is that you must have two relays in series and that a single failure must not break the system (ie there must be some redundancy). The Multi already has one such relay and LOM-detection (loss of mains). Adding the Ziehl with just one relay is sufficient to tick the second box.

Link to comment
Share on other sites

  • 1 year later...

I noticed that the Victron Pre-Built Anti Islanding Box for this has a D-Curve Legrand D63 6000 MCB (10 * In) for an Inverter that only supports 2*In (e.g. 2 * 100A on the Quattro), anyone got any idea why this is, since the requirement is to make sure the inverter input connection is compliant, I would have thought that a C-Curve (5 * In) is all that is needed if the box is going to sit in front of a Quattro AC Input, this becomes particularly important ($$) when you move up the Current ladder to 60kVA and 90kVA installations

Link to comment
Share on other sites

  • 2 months later...
On 2019/06/23 at 8:14 AM, Jaco De Jongh said:

Just a few things to remember when installing a Ziehl 

  • You will need the following:

Ziehl1.JPG.0ff10d32e25b5f7f23a77b1f27724fb6.JPG AND One or two 63A contactors  Schn.JPG.610aff8b461f678081e725cf29d38795.JPG

 

  • Install using the following connection diagram.
  • Ziehl.JPG.0915de11bf8da48b9e3f529290bcdb54.JPG  
  • Please remember to bridge L1 - L2 - L3 when single phase are used. 
  • Return wires (Feedback from Contactors) are not required in SA.
  • I have used 48VDC to power the unit, but you can can chose to use the grid voltage.
  • I have used grid voltage to switch the contactors. 
  • I have Chosen 63Amp Din rail mount DB contactors (Schneider) 

 

  • Putting the unit into programming mode:
  • Switch the supply on. 
  • Look at the following picture. Set.JPG.82d0e2c114f6ebe81cd6cb235cc7f597.JPG
  • The unit comes with the seal not in place. 
  • If the Led between the 2 locks are Red, slightly lift the key cover and turn it 180 degree. While turning you will see a Small blue pin like switch behind the key cover. 
  • Use the key cover and press down firmly on the blue pin for 2 seconds. 
  • The Led should turn to Green now. 
  •  Once the LED is Green you can continue with the configuration. 

 

  • Configuration:
  • There are 2 Programs to chose from
  • PRG5 is used for 230Volt Phase to Neutral, 1 or 3 Phase
  • PRG6 is used for 400Volt phase to phase systems with no Neutral. 
  • Press the UP arrow 1 time to display "InFo."
  • Press the RIGHT button 5 times to display "PR 1"
  • Press the UP button till you reach "PR 5" or "PR 6
  • Press the RIGHT button 1 time to display "no"
  • Press the DOWN button 1 time to display "YES"
  • Press the Right button.
  • The Device will reset and start with the new program. 
  • Every time a new program is selected, all the settings revert to the default settings. 
  • Changing Settings: 
  • ONLY after you selected the relevant program for your installation, you should continue to the settings. 
  • Press the UP button 2 times to get to the first Menu on the Settings LIst. 
  • Use the Right Button to Scroll through the 5 settings of each Parameter.
  • Use the UP and Down buttons to change the setting to mach the settings on the list. 
  • Once done with all 5 settings, use the UP button to scroll to the next Parameter on the list.  
  • The settings for South Africa are as follows. 
  • 1522307569_Settings1.thumb.JPG.7420bd91bdb1588d1d3bb9776e7b5ab8.JPG
  • 585382934_Settings2.JPG.dd3f82061694b313b582e7cf976e6e45.JPG
  • Once you done, remove and re-apply the power, the unit will go through a 60 Second "self check" that might be followed by another count down. 
  • Once that is complete and all conditions are within spec, the Contactors should energize. 
  • Once you are satisfied with the settings, press the blue pin till the LED turns red. 
  • Apply the seal, but dont crimp it till you are sure no one wants to check your settings.  

 

The OverFrequency 1 bar is specified above and in the manual as a default Hysteresis 1.45 when it is actually a default of 1.95, do not change this parameter, it is a "copyedit error/typo" in the manual and is not intended to be changed from the default value

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

 Share

×
×
  • Create New...