Posted February 8, 20205 yr Good day Connecting Pylon tech to 2 or more inverters(parallel or 3 phase) Do you connect each inverter to a separate Pylon battery or all inverters to one battery bank? Latter how do you deal with pylon 100a max output? Seems kinda useless having only 100a DC input on 15kw inverer setup? Edited February 8, 20205 yr by Peter Woest
February 8, 20205 yr Hi @Peter Woest, Please mention the make and model of inverter of your setup, but in general, 1 battery bank, many inverters.
February 9, 20205 yr Author For example kodak or mecer 5kw inverter.. 3 inverters in parallel 15kw. Roughly 60A max AC output. Will never reach 60A output with only 100A DC input available?
February 10, 20205 yr 21 hours ago, Peter Woest said: Roughly 60A max AC output. Will never reach 60A output with only 100A DC input available? No, they won't. Usually you need several PylonTechs for one 5 kVA inverter, so for 3 inverters, you would be extremely battery constrained if only 100 A was available. Edited February 10, 20205 yr by Coulomb added "5 kVA"
February 10, 20205 yr Author Thanks for your reply My understanding is even with a stack of 6 pylons, one is still limited to 100A battery discharge?
February 10, 20205 yr 33 minutes ago, Peter Woest said: one is still limited to 100A battery discharge? That might be a supplied cable limitation. I'm sure that there are ways to overcome this, for example with busbars.
February 10, 20205 yr Author As far as I know Pylon bms limits 100A discharge even with 7 units connected with comms