NOARK Ex9BP-JX 2P Wiring confirmation.


Ingo
 Share

Question

I got myself two NOARK Ex9BP-JX DC 2P MCB's for some rewiring over the December time period. I just want to confirm that I can use these between my Panels and MPPT PV Input and between my MPPT Battery Output and Battery.

The MPPT is 150V.

This diagram shows the 2P wiring. Can I safely use it like that? I've seen DC MCB's wired incorrectly on youtube and don't want to become a statistic.

image.png.f04b6e1dd54fa8e2bed74b983207beee.png

and

image.png.ca67a895def2fcda6634bab8e03d8332.png

 

Other NOARK documentation has the + and - swapped around like below:

image.png.c65a0ad35ee12204f134e9747258aa63.png

My breaker looks like this:

image.thumb.png.d9b29b2b053a93e731a4fb1779eb2e07.png

 

 

Link to comment
Share on other sites

10 answers to this question

Recommended Posts

  • 0

Morning you need to be careful wiring up DC breakers so that the magnetic field directs the DC spark into the catch cage. If the source is your PV you can bring the wire into the CB either at the top or at the bottom like an isolator but then you must be consistent and ignore the + and - on the other side. Your current flow between MPPT and battery is usually  bi-directional and DC circuit breakers  are not designed for bi-directional use.

The Amps you are going to draw from your battery is could  exceed what a DC breaker is able to switch. So I would recommend you have a DC breaker between PV and MPPT and a battery disconnect between battery and MPPT. You don't mention what size you PV array is and whether the array is made up of several strings or the size of your inverter. So my recommendation is made with incomplete facts.

https://www.youtube.com/watch?v=Cup5fMGaE2g

 

Edited by Chris Hobson
Link to comment
Share on other sites

  • 0
8 minutes ago, Chris Hobson said:

Morning you need to be careful wiring up DC breakers so that the magnetic field directs the DC spark into the catch cage. If the source is your PV you can bring the wire into the CB either at the top or at the bottom like an isolator but then you must be consistent and ignore the + and - on the other side. You wiring between MPPT and battery is usually  bi-directional and DC circuit breakers  are not designed for bi-directional use.

The Amps you are going to draw from your battery is could  exceed what a DC breaker is able to switch. So I would recommend you have a DC breaker between PV and MPPT and a battery disconnect between battery and MPPT. You don't mention what size you PV array is and whether the array is made up of several strings or the size of your inverter. So my recommendation is made with incomplete facts.

https://www.youtube.com/watch?v=Cup5fMGaE2g

 

Sorry for the incomplete information. The array is small, it's 1000W (5S/2P) of 10 100W 36Cell panels rated at  <12A Isc in total for the 2P combination. The Battery DC breaker is 40A as the MPPT is a 150/35. I've only shown the PV breaker for illustrative purposes to indicate the polarity markings.

My concerns was that magnetic direction with the two conflicting sets of information from NOARK.

Link to comment
Share on other sites

  • 0

Use the direction of current flow into the switch i.e. the source side (PV in this case). You understand why you cannot use a DC CB between MPPT and batteries as sometimes the MPPT is the source and sometimes the batteries are the source. If you have a separate set of wires directly from the battery to load then you can have a CB between MPPT and batteries but then you need a CB/battery disconnect on the load cables depending on the maximum possible draw. I think you have a Victron MPPT. Some Victron MPPTs have terminals for load and others do not.

I would be inclined to have a DC CB between PV and MPPT and a battery disconnect between batteries and load. A second DC CB would be superfluous between MPPT and batteries. Just make sure your cables are specced properly. 

Link to comment
Share on other sites

  • 0
27 minutes ago, Chris Hobson said:

Use the direction of current flow into the switch i.e. the source side (PV in this case). You understand why you cannot use a DC CB between MPPT and batteries as sometimes the MPPT is the source and sometimes the batteries are the source. If you have a separate set of wires directly from the battery to load then you can have a CB between MPPT and batteries but then you need a CB/battery disconnect on the load cables depending on the maximum possible draw. I think you have a Victron MPPT. Some Victron MPPTs have terminals for load and others do not.

I would be inclined to have a DC CB between PV and MPPT and a battery disconnect between batteries and load. A second DC CB would be superfluous between MPPT and batteries. Just make sure your cables are specced properly. 

You are correct, it's Blue. There is also no Load option for this MPPT, only PV and Battery so direction is always one-way. Thanks for your input.

Link to comment
Share on other sites

  • 0
1 hour ago, NigelL said:

I found this useful document that describes the correct wiring of DC Circuit Breakers in PV applications.  

Discussion-Paper-Correct-Wiring-of-Double-Pole-DC-Breakers-LVL2-131210-v2.pdf 1.67 MB · 2 downloads

Thanks @NigelL, it's exactly as Chris explained and I have it now - great reference document. It won't go up in flames this side...

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Answer this question...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

 Share

×
×
  • Create New...