Hi - Hope the forum can offer guidance. I had a Sunsynk 5.5 installed during the week. There is a problem in surplus power feeding to the grid. During high PV production the flow back to the grid reaches 3.5kw (and over). As I am not sure where the "grid" reading takes places (at the inverter or at the board) I switched off all non critical loads at the board to check whether flow reduced. Unfortunately the negative flow continued. So, the power from PV banks does not reduce in cases where AC1, AC2 and non critical loads are less than production and the balance flows to the grid. Also my Eskom P160 Customer Interface Unit has also stopped reading. A few questions to help me understand where the problem might be

- which sensor provides the "grid" reading on the sunsynk? is this read at the CT or at the grid input on the inverter?

- are there settings, in the management system, to prevent feedback to the grid?

- alternately, are there settings that enable the reduction of PV generation when the CT detects a negative flow? (i.e. power being returned to the grid)

 

If there have been similar experiences in overcoming power returning to the grid, I'd greatly appreciate your guidance on problem areas to investigate.

 

Lastly, what is Eskom's stance on this. I know returning power to the grid is not allowed. Is there some tolerance allowed in setting up a new inverter and working through snag lists. Or should I shut down the whole system until the installer is able to solve the problem?

 

Thanks

Link to comment
Share on other sites

3 hours ago, Warren Porteous said:

Hi - Hope the forum can offer guidance. I had a Sunsynk 5.5 installed during the week. There is a problem in surplus power feeding to the grid. During high PV production the flow back to the grid reaches 3.5kw (and over). As I am not sure where the "grid" reading takes places (at the inverter or at the board) I switched off all non critical loads at the board to check whether flow reduced. Unfortunately the negative flow continued. So, the power from PV banks does not reduce in cases where AC1, AC2 and non critical loads are less than production and the balance flows to the grid. Also my Eskom P160 Customer Interface Unit has also stopped reading. A few questions to help me understand where the problem might be

- which sensor provides the "grid" reading on the sunsynk? is this read at the CT or at the grid input on the inverter?

- are there settings, in the management system, to prevent feedback to the grid?

- alternately, are there settings that enable the reduction of PV generation when the CT detects a negative flow? (i.e. power being returned to the grid)

 

If there have been similar experiences in overcoming power returning to the grid, I'd greatly appreciate your guidance on problem areas to investigate.

 

Lastly, what is Eskom's stance on this. I know returning power to the grid is not allowed. Is there some tolerance allowed in setting up a new inverter and working through snag lists. Or should I shut down the whole system until the installer is able to solve the problem?

 

Thanks

Hi 

The CT sensor will limit the flow back to the grid. First is to make sure it's installed in the right location. You can check this by the information on the display when clicking on the load icon on home screen 

Can you share this screen. 

There are settings that you can use to limit any feedback. You will need to share a screen of settings page. 

If you have an old spinning meter then the meter will spin backwards. This can be an issue if your current reading is less than the previous reading. 

If you have a prepaid meter then it could either trip and go into tamper mode or it will bill you usage when feeding back. 

What kind of meter do you have? 

Link to comment
Share on other sites

5 minutes ago, Achmat said:

Hi 

The CT sensor will limit the flow back to the grid. First is to make sure it's installed in the right location. You can check this by the information on the display when clicking on the load icon on home screen 

Can you share this screen. 

There are settings that you can use to limit any feedback. You will need to share a screen of settings page. 

If you have an old spinning meter then the meter will spin backwards. This can be an issue if your current reading is less than the previous reading. 

If you have a prepaid meter then it could either trip and go into tamper mode or it will bill you usage when feeding back. 

What kind of meter do you have? 

Thanks Achmat, gladly problem solved.. the (rather confusing) options on the "System Mode" panel were the key. Although the "Zero Export" button was checked there are two conditions under which this is overridden underneath the check box, "Sol exp bat full" and "Limit to load only". Both of these were checked and therefore allowed power to flow to the grid. 

"Sol exp bat full" means it will allow solar to be exported when the battery is full (even though "zero export" is checked).. so its a conditional function.

"limit to load only" means solar will be available for solar loads only (i.e. critical loads) anything else, is pushed back to grid.

I have unchecked both and the push back has stopped. The flow from grid is now the min 20w and the panels are throttling back.

 

Re the meter, I have a digital meter but its not prepaid, rather debit order. In my house I have a CIU (customer interface unit). The CIU is used by prepaid customers to load credits. 

I think the meter was charging me for the solar being pushed back to grid as the reading was increasing. 

 

 

Thanks

Link to comment
Share on other sites

2 hours ago, Warren Porteous said:

Thanks Achmat, gladly problem solved.. the (rather confusing) options on the "System Mode" panel were the key. Although the "Zero Export" button was checked there are two conditions under which this is overridden underneath the check box, "Sol exp bat full" and "Limit to load only". Both of these were checked and therefore allowed power to flow to the grid. 

"Sol exp bat full" means it will allow solar to be exported when the battery is full (even though "zero export" is checked).. so its a conditional function.

"limit to load only" means solar will be available for solar loads only (i.e. critical loads) anything else, is pushed back to grid.

I have unchecked both and the push back has stopped. The flow from grid is now the min 20w and the panels are throttling back.

 

Re the meter, I have a digital meter but its not prepaid, rather debit order. In my house I have a CIU (customer interface unit). The CIU is used by prepaid customers to load credits. 

I think the meter was charging me for the solar being pushed back to grid as the reading was increasing. 

 

 

Thanks

Just a correction on the limit to load function. 

If this is not ticked it can send solar generation to loads before the inverter of you have any. Normally high powered loads such as geysers and pool pumps are not put after the inverter. With the CT coil connected at the right location, the inverter can calculate the total coming from the grid and what the loads on the inverter is using. The difference between these two would be loads before the inverter. It can then send excess to these loads while trying to keep the meter close to zero. 

I'm not sure if you have any loads before the inverter or if your while house is connected to the inverter. 

Link to comment
Share on other sites

3 hours ago, Achmat said:

Just a correction on the limit to load function. 

If this is not ticked it can send solar generation to loads before the inverter of you have any. Normally high powered loads such as geysers and pool pumps are not put after the inverter. With the CT coil connected at the right location, the inverter can calculate the total coming from the grid and what the loads on the inverter is using. The difference between these two would be loads before the inverter. It can then send excess to these loads while trying to keep the meter close to zero. 

I'm not sure if you have any loads before the inverter or if your while house is connected to the inverter. 

Thank you Achmat, this evening I noticed the battery draining rapidly and your description explains this. with the limit to load unchecked and with no solar it was using battery for non critical loads. Now with it checked I presume battery depletion will reduce. looking forward to tomorrow to see if the grid feedback problem remains resolved.
 


 

 

 

Link to comment
Share on other sites

  • 2 years later...

Yesterday, my electricity meter was configured so that I could feed excess power back into the grid. However, upon doing some research, it seems that the CT coil on my Sunsynk 5kw inverter might have been installed the wrong way round? From what I understand, the feed from the should not have a minus in front of the value?

The first photo is where the grid supply to the inverter is switched off.

The second photo is where the grid is switched on.

The 3rd photo is where the grid is still on with the dishwasher running, and the grid value doesn't have the minus in front of it.

20230407_104631.jpg

20230407_104756.jpg

20230407_105448.jpg

Link to comment
Share on other sites

The way I see things as a non Sunsynk user is that on picture 2 you were exporting 1914W from the 2263W you were generating from PV. 

The last with the dishwasher on you were self using all that is generated so no power to export.

The CT will only show negative if you are using the grid power and it shows negative. Yours seems to show correctly.

Link to comment
Share on other sites

29 minutes ago, Scorp007 said:

The way I see things as a non Sunsynk user is that on picture 2 you were exporting 1914W from the 2263W you were generating from PV. 

The last with the dishwasher on you were self using all that is generated so no power to export.

The CT will only show negative if you are using the grid power and it shows negative. Yours seems to show correctly.

Thanks, that is the same feedback I've received from someone with a SunSynk inverter.

Link to comment
Share on other sites

2 hours ago, Scorp007 said:

The CT will only show negative if you are using the grid power and it shows negative. Yours seems to show correctly.

If the CT shows a negative value, then it is either incorrectly installed (needs to be swopped around) or the OP is exporting to grid. In normal operation it should be positive (i.e. when it is drawing current from grid).

image.thumb.png.829534290ed5deb8a05e69b63ea632ed.png

Link to comment
Share on other sites

33 minutes ago, YellowTapemeasure said:

If the CT shows a negative value, then it is either incorrectly installed (needs to be swopped around) or the OP is exporting to grid. In normal operation it should be positive (i.e. when it is drawing current from grid).

image.thumb.png.829534290ed5deb8a05e69b63ea632ed.png

I am feeding back into the grid.

Link to comment
Share on other sites

43 minutes ago, YellowTapemeasure said:

If the CT shows a negative value, then it is either incorrectly installed (needs to be swopped around) or the OP is exporting to grid. In normal operation it should be positive (i.e. when it is drawing current from grid).

image.thumb.png.829534290ed5deb8a05e69b63ea632ed.png

Just like @HennieB84 said he is feeding back to the grid. Refer to the 3 pictures. When not feeding into the grid the CT is positive.The moment he feeds 1914W into the grid only then does it change to negative. This indicates the CT is correct.

Link to comment
Share on other sites

46 minutes ago, HennieB84 said:

I am feeding back into the grid.

Yes, I know that.

35 minutes ago, Scorp007 said:

Just like @HennieB84 said he is feeding back to the grid. Refer to the 3 pictures. When not feeding into the grid the CT is positive.The moment he feeds 1914W into the grid only then does it change to negative. This indicates the CT is correct.

Yes, the issue I had was this statement of yours:

 

3 hours ago, Scorp007 said:

The CT will only show negative if you are using the grid power and it shows negative.

 

If you are using grid power, a correctly installed CT will show positive, not negative

Link to comment
Share on other sites

17 hours ago, Leshen said:

If no power is flowing past the CT then it will indicate 0. If the power is flowing from the grid to the inverter then the value should be positive and if you are exporting then it should be negative. 

If it’s doing anything else besides that then it’s either in the wrong position or the wrong way around. Regarding it’s position, it has to be around the main live wire BEFORE any splitting of that live. 

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...