Everything posted by Flouw
-
For Sale: Solar panel mount kit
Item: Solar mounting rails kit 4 × 2.74 m, 30 × 30 mm aluminium solar rails — 10.96 m total 4 × Volta mid clamps 4 × Volta end clamps 6 × heavy-duty roof/rafter brackets 17 m red 6 mm² PV cable 17 m black 6 mm² PV cable 34 m PV cable total All brand new / unused Rail joiners not included Enough rail for a 4rh panel. Will require 2 x more mid clamps. Age: New Price: R2000 Payment Method Accepted: EFT Cash Warranty: None Packaging: As per photos Condition: New Location: Centurion/Gauteng Reason: Got it with the panels i purchased. Not the same as my existing rail system. Shipping: Prefer not due to size Collection: Yes.
-
For sale: Kodak 3.24OG Plus Inverter
Item: Kodak 3.24OG Plus inverter.(Axpert King) Age: unsure Price: R4000 Payment Method Accepted: cash/EFT Warranty: No Packaging: No Condition: second hand. Well looked after and in fully functioning condition Location: Centurion/Gauteng Reason: upgraded to bigger system Shipping: can be discussed Collection: prefered
-
For Sale: Axpert King 3kw
Item: Full Circle Solar 3kw inverter. 24v. (Axpert King) Age: unsure Price: R4000 Payment Method Accepted: cash/EFT Warranty: No Packaging: No Condition: second hand. Well looked after and in fully functioning condition Location: Centurion/Gauteng Reason: upgraded to bigger system Shipping: can be discussed Collection: prefered
- Please remove - Duplicate
-
Wanted : Hestia 560w HTS-144M10H560
Item Wanted: Hestia 560w HTS-144M10H560 Packaging Essential: no Desired Age: NA Location: Centurion/Gauteng Willing to accept a shipped item: prefer collection or delivery Ballpark/Budget Amount: Open to what is available Im expanding my PV array. And have space for one more panel. Rail wise aswell as inverter capacity wise. And would like to add one more of the same panels to either of the strings.
-
Wanted : Jinko 550w bifacial JKM550M-72HL4-BDVP
Item Wanted: Jinko 550w bifacial panel. JKM550M-72HL4-BDVP Packaging Essential: no Desired Age: New or used Location: Centurion/Gauteng Willing to accept a shipped item: prefer collection or delivery Ballpark/Budget Amount: Open to what is available Im expanding my PV array. And have space for one more panel. Rail wise aswell as inverter capacity wise. And would like to add one more of the same panels to either of the strings
-
Kodak Inverter & 2 Giter Batteries for sale
You will have to provide more details.
-
7x Voltronic Axpert 5kVa inverters for sale
Ok. Will wait for photos. But if its the older units. And all requires refurbishment and repairs. Then the price doesnt realy make sense.
-
7x Voltronic Axpert 5kVa inverters for sale
Are any of them the plus/king units?
-
Luxpower and Solar Assistant
does anyone have feedback regarding the automation on the Luxpower units using Solar Assistant as yet? im looking at upgrading my inverter to a Luxpower unit. but is essential to my system that the automation still works
-
Axpert inverter with Hubble AM2 - battery cycling
perhaps post the exact Axpert inverter model you have. alot of the issues/challenges you have mentioned, i have been able to resolve with Solar assistant. And a Victron smart shunt, as this monitors the SOC correctly, unless your battery communicates correctly with the inverter. Solar Assistant does have some automation options aswell now, that makes it alot less IT intensive than having to set up home assistant and and and. BUT, the likely best change i made was to an Axpert Plus model, that has better blending options. (SUB being one of the more important ones)
-
For Sale: KODAK 4.6KW GRID TIED INVERTER (2x Output, 2x MPPT 6kw) (SOLD)
HI. what is all included? bracket? cables? meter? and do you have any idea if Solar assistant supports this inverter for monitoring purposes?
-
GROWATT 3kva with Esener 25.6v
1. i have the inverter set to USE. 2. only have essentials connected, i run from UTI from sunset to around 22:00. base loads that time is varying as the fridge goes on and off. but it consumes 6/7% per hour. solar assist helps me to maintain the battery. i choose to cycle the battery, as it makes space to harvest PV. the next day- i need to add another battery, as mine is fully charged by 10:00 in the morning already, and the PV system is then just idling. 3. i set the float and bulk the same, as the float bug is a reality if your voltage doesnt go low enough, especially charging on PV. it only charges to float voltage. BUT, once the PV drops, it tops it off from Utility till it reaches the SOC maintainer. that is why i raised the float to where i want it to be. the 3.4v resting voltage is exactly that. resting voltage. and what i have learned with the LiFePo4, Voltage doesnt tell you much. i use to think my battery is almost empty after 4 hour load shedding, lights on, TV on. fridge running. till i fitted the Smart Shunt. then realized after a 4 hour outage, that my battery was still at least 50%.
-
GROWATT 3kva with Esener 25.6v
my previous inverter didnt have the bulk timed charge function. and the floating bug is pretty much in all the inverters/batteries that cant communicate. im not running a big system. so i dont have to fast charge (less than 2 hours), so i set the bulk the same as float. 27.6 is safe. and its not in the upper curve of the voltage, so it wont run away with the PV system. i would not even use the equalization function, as i dont see the need for lithium. the esener battery BMS is apparently an active balancer, so it always balances. not only from a certain voltage. i cant give more details, as i have yet to open one to see. but i set my batteries to charge at 28.2v for 12 hours once a month. and it seems to be OK with that, lithium will only absort the power it needs, and you cant overcharge them, unless you over voltage them. do not charge them to the absolute max, and keep them there, they need to settle, otherwise it gets bloated and gas's i do have PV on the roof yes, that charges and supports all the essentials the whole day, and at night i let the battery run down to 40% SOC by 06:00. which ever comes first, as PV starts producing from there, although not much, but has enough power left for another 4 hours untill either PV is enough, or Eskom is back online if its rainy. Solar assistant helps maintain the battery, has that function. so if the battery drains faster than the graph, it switches to grid untill everything catches up. i dont charge from Eskom at all. unless the weather is really bad. IF i had to install a system again, as an backup, or for someone else, and dont have the capability to read SOC, i would again set the bulk and float to 27.6. and forget about it. ill do some tests on a lower voltage for bulk and float, to see when the "floating bug" starts setting in.
-
GROWATT 3kva with Esener 25.6v
i use a Axpert type inverter. and the battery setting is on USE. as i can set the float and bulk to whatever i want. and the bulk does have the timed bulk charge function aswell (not the equalize charge function). also no comms between inverter and battery. i also had alot of questions, and sat with multimeters and and and for days and hours. so i just bought a Victron smart shunt and a Raspberry, in loaded Solar assist. yes there is still flaws. but atleast i can try resolve this myself while i am not home, as i work out of country for weeks at end. even after installing the monitoring stuff, giving me a better idea of what is going on, and and and. i still run it on 27.6v. of bulk and float. and i play around ever so often with different settings to see what effect it has. again, i cycle the battery daily, so it doesnt sit at 27.6v the whole day, probably for 4 hours or so, and then solar decreases to where it starts using battery again.
-
GROWATT 3kva with Esener 25.6v
Ive set bulk and float on 27.6 v on my setup. And its been like that for some months. Yes i do cycle the battery every day. Discarge to 40% soc max.
-
Mecer inverter linked to PV panels problem
Edit two questions where answered by reading the inverter spec sheet. What are the settings? If the battery is fully charged. The panels wont do anything. Some inverters cant "blend" Unless you switxh over to battery only. Trip the mains and see what it does. And did you make sure (+) and (-) on the PV panels are not swiched around.
-
Mecer inverter
EDIT(ive added a screenshot of the setting) also known as power sensing. if the current draw is very low, the inverter swithces off what mecer model is it? and there is a "power saving" setting that you need to disable. check the manual. im not 100% sure what is is called. Power saving. Standby. or something like that
-
Kodak OG Plus 5.48 and solar not charging correctly.
send screenshot of your settings page on solar assistant. also, sign into the inverter with your phone's bluetooth, and screenshot the setting page of each. last but not least, can you confirm that both inverters are on the same firmware, and that they are "talking"to one another in parallel mode.
-
GroWatt battery charging/discharging issues
as a test. disconnect the batteries from one another. and see what the SOC indicators indicates for each battery.
-
GroWatt battery charging/discharging issues
Are the batteries communicating with one another? I would think that so many batteries is series, if not communicating, one of them could very easily go out of sync. Voltage can not be used to indicate SOC on lithium. Ive tried it. How is the equipment wired together? And where do you get the SOC reading from?
-
Impact of the increasing residential battery backup systems on load shedding
and the losses associated with inverter and batteries without solar is adding on to the grid load. so we are exactly where we where before loadshedding, in fact a little worse. some might have added panels and this reduced the loads. but the ones not having any panels, but added inverters and batteries have consumed that saving. Did eskom not see this coming? they want people to install solar to reduce demand, but scared they loose revenue. hence them pushing for the fixed connection fee. more and more paying customers are switching to solar, and reducing consumption. so revenue is reducing. but the demand does not reflect this. as their "base load" (read non paying legal and illegal connections) is not changing. Eskom is to look into their non paying consumers.
-
Please delete
thank you. i havent googled/searched solar panel prices since March this year when i bought some. seems like the prices has dropped rapidly.
-
Please delete
strange yes. as the general public is still struggling to get 545w panels for under R3200
-
Smart Changeover Switch (not automatic, just controllable through app, SolarAssistant etc.)
likely your easiest option here, as what @PsyWulf said. control the supply from the inverter instead of controlling the Eskom. take note, that the amp rating on the smart switch will have to be substantial, as you are trying to run geyser and oven on the same switch. my personal opinion, leave the oven on the grid. as these are normally used at night when there is no Solar anyway, and using battery for this purpose is is not smart. rather use a smaller air fryer or even a convectional oven that uses similar power, but for a much shorted duration. (is the lamb chop worth a battery) the geyser i would agree, put it on solar during daytime to get most out of you installation. and switch to grid in the evening, also incorporate a smart controller for the geyser, to control temps for when not needed.