Solar problem

Featured Replies

Hi Kamlesh you have to change your PV strings so the strings match in voltage. If I understand you correctly you have 6 x 450w panels in series (+/- 240VMP)and 4 x 540w panels in series (+/- 160VMP). The 540w string will draw the 450w string down. When the charge controller start it can not find the mppt point and then can draw the bus voltage down for a moment then error 52 will show up as your inverter charge on the DC high voltage bus and not on the 48V Bus.   

On a 48V LIFePo4 battery you need to set bulk and float to a max voltage of 53.8V. if set too high the BMS will open the charge mosfet's and stop charging before the BMS have time to balance the cell's. most BMS's will stop charging if a cell get above 3.65V. You have a 15 cell battery and 53.8V work out to 3.58v per cell. 

Hope this help

 

  • Replies 60
  • Views 9k
  • Created
  • Last Reply

Top Posters In This Topic

Most Popular Posts

  • Ask him to swap it for a Sunsynk with a cash difference

  • As you indicated a panel fuse blew with 2 parallel string it is to be expected if the fuse was 20A. Both panels could be Vfullpower of 40V. Thus one string could provide 10A and the new 13A. The

  • I believe I did point that out in an earlier post. So he is aware of that. "On the sellers website the data contradicts that which is on the battery, as yours is a 4800 and this one is advertised

Posted Images

28 minutes ago, Irocmaster said:

Pin out for Ultra Energy 48100PW are RS485 only  RJ45 1&9 to B  2&8 to A and  3&9 to ground.

Battey side Pin1&9 to Growatt pin1 Pin 2&8 to Growatt Pin 2

Pin out for Ultra Energy 48100PW are RS485 only  RJ45 1&8 to B  2&7 to A and  3&6 to ground.

Battey side Pin1&8 to Growatt pin1 Pin 2&7 to Growatt Pin 2

 

Got it wrong RJ45 have only 8 Pins

  • Author

I am now looking for somebody who could connect it up for me, somebody who know these inverters.I have removed the Gro watt so all the cables are still in place. I also, don’t want to feed back into the grid. 

  • Author
On 2022/04/25 at 6:39 AM, Leshen said:

Ask him to swap it for a Sunsynk with a cash difference

I have swooped it for sunsynk, can you recommend a guy to set it up for me.

  • 11 months later...
On 2022/05/09 at 5:28 PM, Irocmaster said:

Pin out for Ultra Energy 48100PW are RS485 only  RJ45 1&8 to B  2&7 to A and  3&6 to ground.

Battey side Pin1&8 to Growatt pin1 Pin 2&7 to Growatt Pin 2

 

Got it wrong RJ45 have only 8 Pins

Hi @Irocmaster will these pinouts also work on a luxpower? Is there a colour image to show these. I'm not so bright and can't follow the numbers. I have the same battery and can't get it to communicate with a luxpower. Thanks

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.