Axpert charge controller board
Thanks for the kind words Brain.
-
Lithium Ion replacement for AGM batteries
Nasty people on this forums I see. O well not interested any more.
-
Lithium Ion replacement for AGM batteries
Yes true they can gas very bad if hot. Remember the picks of the exploded house. Yes they need good ventilation.
-
Lithium Ion replacement for AGM batteries
Cheap alternative is what I said not that lead acid is better than lithium. The flooded calcium batteries handle higher temp better than AGM batteries. (What I should have said.)
-
Axpert MKII error 03 into 57
Your inverter need to be repaired if your batteries are still fine.
-
RCT MP-T1000S Power Trolley - high voltage alarm question
As you describe the alarm that is normal 4 beeps silence the unit is in battery mode, 4 beeps in one second continues is battery over volt.
-
Sunsynk + Us3000C Pylon Communication
-
Growatt SPF3000 TLHVM-24 and Pylontech Up2500
Restart your inverter
-
Steering Diodes for Solar Panel Strings Question
If you're panels are on the same direction and angle you do not need any diods. Diods on the panels are for reverse protection.
-
Problème au niveau de mon onduleur GROWATT SPF5000TL-VHM
Pouvez-vous m'en dire plus sur le système complet, le nombre de panneaux photovoltaïques et le type de batteries.
-
Growatt SPF3000 TLHVM-24 and Pylontech Up2500
You can check this post.
-
Faulty 5Kw Axpert King
- Battery charging via MKS3kva 24v
I agree with Scorp your batteries are shot. Your settings for gel batteries is a bid high. The spec voltage on the batteries is @25 degrees. Voltage and charge rate must be lower at higher ambient temps in summer.- InfiniSolar 10kw
Repaired on last week, with no load on battery only the display showed around 100va X3 if remembered correctly. how ever it only draw 2.9A from the 48v power supply. That is +/_ 140W idle. I noticed that on very low on no load most inverters do not measure current very accurate.- Best setting for Growatt
Do you have the batterie BMS connected to the Inverter?- Axpert inverter sub DB
Are you pushing all your load thru the inverter? Stove geyser. The inverter can only handle 40A max in bypass and will trip at overload over 5KW. 4mm wire will work 100% for the AC connections.- Battery charging via MKS3kva 24v
Did you try setting 5 on the inverter it self?- Axpert problem
- Solar problem
- Lithium Ion replacement for AGM batteries
Shop for the best price, 12v lithium batteries are expensive for the watt hour capacity . Out of stock at the moment the Mercer 200a 12v 2.4 kWh are a better option for the money. ( Second live cells) These have no BMS communication to the inverter but so do your mercer 3kva inverter have no BMS communication. Load tested many of them and they deliver. can't say if they match the "10" year promise of some brands, which i do not believe in. They will all last at least 3 year. That is longer than warranty of 99% of most manufactures warranty duration. Cheap option are deep cycle silver calcium national auto batteries (Midas, Willard, Exide, No Name all manufactured by national auto batteries ). They can handle high ambient temps better.- Earth Leakage Trip
Check for bad Earth leakage, neutral split, appliance leakage of earth neutral bind at supply. The Earth leakage only trip with imbalance between live and neutral thru earth leakage. Check inverter settings for appliance or UPS, try appliance setting and see if this help.- How to & How often do you clean your Solar Panels?
Soapy water sunlight liquid or car shampoo, wash with a rag can reach my panels easy. Was them if to much pigeon sh#@t on them.- Limited roof space - 3 panel string
Yes 4 panels should be around 160V open and around 135V VMP. I see the spec for Sunsynk MPPT is 125 to 425V and start voltage of 150.V The MPPT should utilize the panels fully.- Limited roof space - 3 panel string
3 Panels will not work on the SunSynk inverter, you are correct. You can do what Coulomb suggest or try our best to fit 4 panels on the roof.- JA Solar / MC4 Connectors / PV cables and MC4: +ve and -ve, which is which?