June 8, 20224 yr 13 hours ago, Solarcrazy said: Got this from my Deye inverter manual. So it seems it does not need a earth bond relay as per Sunsynk setup? That is not a legal installation in South Africa - you cannot have the input and output neutrals hard-bonded like that, it has to be done with a relay.
June 8, 20224 yr Author 39 minutes ago, P1000 said: That is not a legal installation in South Africa - you cannot have the input and output neutrals hard-bonded like that, it has to be done with a relay. If you look at the manual, there is 2 diagrams shown. The one above this on the manual (shown below) does not bond the N and E. Maybe this is more of a better installation?
June 8, 20224 yr 5 minutes ago, Solarcrazy said: If you look at the manual, there is 2 diagrams shown. The one above this on the manual (shown below) does not bond the N and E. Maybe this is more of a better installation? Yes, that is correct, but you have to add the bonding relay to bond N and E when the grid fails.
June 8, 20224 yr Author I spoke to our company electrician who is certified and advises as per SANS rule, we can bond the E and N via the bridge wire on the diagram. He actually prefers this as apposed to the relay as he says being a mechanical device, failures can happen with these relays whereas direct connection there is no failure.
June 8, 20224 yr 2 hours ago, Solarcrazy said: I spoke to our company electrician who is certified and advises as per SANS rule, we can bond the E and N via the bridge wire on the diagram. He actually prefers this as apposed to the relay as he says being a mechanical device, failures can happen with these relays whereas direct connection there is no failure. I'm a little confused. If you are not using a relay, then how will it switch? You want only one earth at all times.
June 8, 20224 yr Author 3 minutes ago, YellowTapemeasure said: I'm a little confused. If you are not using a relay, then how will it switch? You want only one earth at all times. The earth bond device is a relay/contactor type of device. It gets activated by the inverter when the Eskom grid is lost. The earth is one correct.
June 8, 20224 yr 4 minutes ago, YellowTapemeasure said: I'm a little confused. If you are not using a relay, then how will it switch? You want only one earth at all times. Basically by tying the input and the output neutrals together. I'm pretty sure that breaks at least NRS-097 requirements.
June 11, 20224 yr On 2022/06/07 at 9:50 PM, phidz said: I suggest you get another installer who has worked with these kind of inverters before. Deye and Sunsunk are actually the same product. Deye is just the OEM manufacturer. Sunsynk is a rebranded version of Deye inverters. In South Africa Deye and Sunsynk actually have the same support company. I believe the Sol-Ark products in the US are also rebranded versions. The MCU (Inverter) firmware is done by Deye and each licensee manages their own HMI (The LCD display) firmware.
June 11, 20224 yr On 2022/06/04 at 7:43 PM, Solarcrazy said: Hello.. I got a Deye hybrid inverter, for now I don't have panels as yet. My installer put a auto changeover switch(attached pic) which switches automatically when grid is lost. That works perfectly. Only challenge when in grid mode(I.e, Eskom is there) my inverter does not show any usages of grid or house. Surely this is not correct? How do I get usages to show on my inverter when grid is there? I actually have two very similar ATS's on my setup. As other have said, you don't really need the transfer switch if your loads are all connected to the UPS output of the Deye... BUT there is a caveat. In my case my loads can easily exceed the maximum passthrough current of the inverter. Imagine the dishwasher, tumble dryer and washing machine all running at once. This is where such a switch comes in handy. The loads are still on mains, and even when the loads are at 7kW, the inverter feeds back it's maximum 5kW. If you were to 7kW through the inverter, it would shut down. I feed my ATS's with Grid on Source A and Inverter on Source B, so it will automatically switch back to grid when loadshedding ends so that my loads aren't passed through the inverter. These switches make a hell of bang due to their fast switching so sometimes I just put in manual and switch over to Source B when I know loadshedding is coming. My setup definitely shows the load of the house whether the ATS is on grid or inverter. Like others have said, your installer probably didn't install the CT correct... most likely connected it to the wrong spring terminals in the inverter if you get a zero measurement all the time. Edited June 11, 20224 yr by recre8
June 11, 20224 yr On 2022/06/08 at 9:25 AM, P1000 said: That is not a legal installation in South Africa - you cannot have the input and output neutrals hard-bonded like that, it has to be done with a relay. Yeah, I believe that according to SANS the earth-neutral bond may not be done past the point of supply (i.e. Eskom or municipality). I opted to rather have a contactor in my DB board to do the earth-neutral bond instead of a relay with the inverter's outputs. The contactor closes and bridges earth-neutral whenever grid is lost.
June 11, 20224 yr Author 13 minutes ago, recre8 said: Yeah, I believe that according to SANS the earth-neutral bond may not be done past the point of supply (i.e. Eskom or municipality). I opted to rather have a contactor in my DB board to do the earth-neutral bond instead of a relay with the inverter's outputs. The contactor closes and bridges earth-neutral whenever grid is lost. So you are doing the E/N bonding on the Eskom main DB before the Earth leakage and not on the inverter load output? Edited June 11, 20224 yr by Solarcrazy
June 11, 20224 yr 25 minutes ago, Solarcrazy said: So you are doing the E/N bonding on the Eskom main DB before the Earth leakage and not on the inverter load output? I'm doing the E/N bond in the main DB. Definitely before any E/L. In my case I bond the neutral of the UPS side of the Deye to earth using a normally closed contactor. My primary reason for this is because I find it neater having a DIN rail mounted contactor in my DB than a relay of dubious origin in the inverter's panel. Secondly, the Deye/Sunsynk only switches off the relay output after it synchronizes to the grid. By default this is 60 seconds after grid is restored. I just prefer not having the earth-neutral bond made for longer than is really necessary. Here is a diagram of my DB if helps https://drive.google.com/file/d/1jR_KdiXjaSKleup5vDDYBpVIsFYQQkRp/view
August 7, 20223 yr On 2022/06/11 at 8:35 PM, recre8 said: Deye and Sunsunk are actually the same product. Deye is just the OEM manufacturer. Sunsynk is a rebranded version of Deye inverters. In South Africa Deye and Sunsynk actually have the same support company. I believe the Sol-Ark products in the US are also rebranded versions. The MCU (Inverter) firmware is done by Deye and each licensee manages their own HMI (The LCD display) firmware. Hi @recre8, I’ve heard versions of this on the internet, is there any official source for this? Trying to understand how far apart the Deye and Sunsynk are Edited August 7, 20223 yr by SolarNovice88