Sunsynk inverter shut down cant start up

Featured Replies

Hi all

 

Something odd happened tonight

My sunsynk inverter shut down a couple of minutes into loadshedding tonight. I have a LBSA battery connected to it, showing SOC 57%. Shut down is 20%.

I cant start the inverter up at all. 

The blue light around the on/off button illuminates when i switch it on, but thats it.

The screen on the battery is not showing any faults either.

Any ideas?

  • Author

Update

Power came back on and it started up but showed no load on any screens

Went to the battery settings and ticked "activate" under the lithium and it showed load again, but no charging to the batteries.

Couple of minutes later it made a tick like a switch went off and the red alarm light came on, and it showed grid and load as zero again.

Again ticked and unticked the battery activate box and the alarm light went away and started showing grid and load values again.

Still no charging of the battery though

 

Also to note, there's been no change in my settings since previous rounds of loadshedding nor firmware updates.

Is the battery of the inverter at fault here?

Will see tomorrow whether it charges from solar or not

  • Author

Further update

Looks like this problem started a few days ago

Also have F56 dc low voltage errors coinciding with that time, but only showing on the app and not the inverter

 

For some reason it also shows "no battery" on the home screen, though it reads SOC correctly and gets the right readings from the li-bms screen

Screenshot_20220620-224602_Sunsynk Logger.jpg

Screenshot_20220620-225008_Sunsynk Logger.jpg

20220620_225558.jpg

  • Author
1 hour ago, Steve87 said:

Looks like the battery might be giving this problem. Any protection on the LBSA display? 

The battery screen isn't showing any faults or warnings, looks like the BMS and BMS comms to the inverter is off. Not sure what causes this if the SOC is read correctly.

Battery showing 52.68V, inverter showing 9.67V

 

20220621_084444.jpg

20220621_084752.jpg

Screenshot_20220621-085447_Sunsynk Logger.jpg

Edited by eagerllama
Including screenshots

  • Author
8 hours ago, Steve87 said:

I'm picking at straws here, but how is the battery terminal connection security. If not this then a sure test if it's a Comms issue is to setup AGM settings & see if the problems persist. If it resolves then it's a battery Comms issue.

Battery connection is good. I switched to both AGM %  and AGM V and no success. 
I'm waiting for a firmware update, doubt that'll help but want to try that before I do a factory reset.

LBSA says it sounds like an inverter issue, Sunsynk manual says F56 errors are the batteries fault...

Not having much luck!

Try checking your battery terminal with voltage tester. It seems like the inverter cannot sense voltage from your battery. How about checking isolators/breakers between the inverter and battery if there is?

If all good, I suspect inverter is at fault, something hardware related.

  • Author

Thanks, tested the terminals directly on the battery and its reading 9v, same as what the inverter is reading.

Battery BMS is reading 52v so maybe just a dodgy connection within the battery itself?

Will give LBSA a shout today

11 minutes ago, eagerllama said:

Thanks, tested the terminals directly on the battery and its reading 9v, same as what the inverter is reading.

Battery BMS is reading 52v so maybe just a dodgy connection within the battery itself?

Will give LBSA a shout today

Yes it seems so. It might be an easy fix. Good luck.

  • Author

Took the battery to LBSA.

Damn that thing is uncomforable to carry!

They confirmed there was something wrong - I think the circuit breaker between the BMS and the terminals and fixed it while I was waiting

Quite impressed by them

Mounted the battery and all working perfectly again!

26 minutes ago, eagerllama said:

Took the battery to LBSA.

Damn that thing is uncomforable to carry!

They confirmed there was something wrong - I think the circuit breaker between the BMS and the terminals and fixed it while I was waiting

Quite impressed by them

Mounted the battery and all working perfectly again!

Now the next question is, what caused it? Loose connections? If so, has it not burn anything due to arcs?

  • Author
Just now, power.esrl3 said:

Now the next question is, what caused it? Loose connections? If so, has it not burn anything due to arcs?

They said this is a very rare fault, but it's most likely a part fault as opposed to being caused by something.

They checked the rest of the unit anyway for other potential faulty bits so that I don't have to make another trip and didnt mention any loose wires or arcs or burns, so I think it's just that bad luck of that single component failure

  • 11 months later...

i have the same problem as described above. The system shuts down during load shedding and restarts after minute or 2. The battery was at 33% shutdown threshold is 20%

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.