Increasing C Rate of Dyness batteries

Featured Replies

Hi all,

I've recently ventured into a backup system to get past loadshedding and have had a Sunsynk 5 kw inverter and two Dyness 48 v 4.8kw batteries installed (parallel).

Everything works great except, when I pull around 2600 - 2800 watts the inverter shuts down. I suspect there are too many amps being pulled and, as the batteries are 0.5 C rated, only discharge half the available power. 

Is there any way to increase the available power for discharge i.e. a third battery ? 

My 5kw inverter is effectively only providing half of its input as a result of the C rating of the batteries.

How can I get closer to around 4400 watts etc for use? Is the only way to change batteries?

Thanks,

 

Maybe post some of your settings.
That does not sound correct that you are being shutdown when you do 2600-2800 watts.
Unless you are doing that usage constant for a good many hours.
At that high usage rate you should be getting close to 4 hours run time if the batteries are nicely balanced and fully saturated on the previous charge cycle.

If you have 2 x 4,8kwh 0.5C batteries that means you should be able to pull about 4,8Kw for about 2 hours. Sounds like your settings on the inverter are incorrect. 

  • Author
1 hour ago, WannabeSolarSparky said:

Maybe post some of your settings.
That does not sound correct that you are being shutdown when you do 2600-2800 watts.
Unless you are doing that usage constant for a good many hours.
At that high usage rate you should be getting close to 4 hours run time if the batteries are nicely balanced and fully saturated on the previous charge cycle.

I've attached some photos of all the settings pages - not the neatest but difficult to get past the 3MB limit. 

Also, when the inverter does go off the relevant fault code is F56 - low DC voltage.1551337020_Sunsynksettings.thumb.jpg.ea8dae3b442e788729f89a058e3bcf5d.jpg

3 minutes ago, Balneuwes said:

I've attached some photos of all the settings pages - not the neatest but difficult to get past the 3MB limit. 

Also, when the inverter does go off the relevant fault code is F56 - low DC voltage.1551337020_Sunsynksettings.thumb.jpg.ea8dae3b442e788729f89a058e3bcf5d.jpg

Change your inverter battery settings to match what the BMS is sending to the inverter, from your images that would be 53.5v set that to all 3 settings on your battery charge screen.
Should not really make much diffs in your usage results but do that anyway just to be safe in case your bms comms go down.
You settings so far look ok.
Maybe also post your actual inverter timer settings and setup settings as the ones you posted are not altogether helpful for the issue you describe fully.

 

10 minutes ago, Balneuwes said:

I've attached some photos of all the settings pages - not the neatest but difficult to get past the 3MB limit. 

Also, when the inverter does go off the relevant fault code is F56 - low DC voltage.1551337020_Sunsynksettings.thumb.jpg.ea8dae3b442e788729f89a058e3bcf5d.jpg

The DC low warning points to the battery side so either the settings are not altogether correct or the state of charge of the battery is not correctly reflecting what is actually left in the battery.
Might be that you simply need a good full absorption cycle on the batteries.
May also be some of the cells are out of balance which could result in premature low voltage state being reported to the inverter during cycling.

Edited by WannabeSolarSparky

  • Author

I might only add that when the inverter did go off the amps being pulled were in the region of 56 (which were marked in orange) when the kettle was turned on. Watts remained around 2700 - 2800.

Edited by Balneuwes

1 hour ago, Balneuwes said:

These are the only remaining settings - any idea?

20221030_170346.jpg

20221030_170354.jpg

On the second image you have limit to load only.
Do you have the CT coil installed?
Maybe provide a scrrenshot of the inverter home screen where it shows your energy flows.
If you do and its installed correctly then you should uncheck limit to load only and then you can decide if you want to proritise the Load on the essential side by checking the Priority Load box.

On the 1st image setting you have SOC/V set to 100% all day so you will never use battery unless there is no grid.
Is that the desired working mode you want?

1 hour ago, Balneuwes said:

I've attached some photos of all the settings pages - not the neatest but difficult to get past the 3MB limit. 

Also, when the inverter does go off the relevant fault code is F56 - low DC voltage.1551337020_Sunsynksettings.thumb.jpg.ea8dae3b442e788729f89a058e3bcf5d.jpg

On your LiBMS screenshot the discharge amps is only 50A and that is your problem. It should say 100A. Looks like your batteries are not communicating with each other to tell the inverter that there is 2 batteries thus doubling your discharge capability. Check the comms cable between the batteries . When you get the LiBMS screeen to show 100A discharge limit its working correctly . Also change the discharge amps on you charging screen to 100A as 120A is too high. I also notice you dont have signal island mode ticked , make sure you have a neutral earth relay installed and then tick signal island mode. In your system mode settings you can untick the Use timer option as that will keep the batteries full ,kind of pointless to use the timer when you dont have solar...

Edited by Nexuss

  • Author
40 minutes ago, WannabeSolarSparky said:

On the second image you have limit to load only.
Do you have the CT coil installed?
Maybe provide a scrrenshot of the inverter home screen where it shows your energy flows.
If you do and its installed correctly then you should uncheck limit to load only and then you can decide if you want to proritise the Load on the essential side by checking the Priority Load box.

On the 1st image setting you have SOC/V set to 100% all day so you will never use battery unless there is no grid.
Is that the desired working mode you want?

This is a backup system only to get me through the bouts of loadshedding  - I am unsure what a CT coil is or its function.  

I'll ask my installer about this - the way I understand is that the inverter is wired directly to all circuits on the main DB except the stove, geyser and swimming pool. 

Screenshot_20221030-190310_Sunsynk Logger.jpg

  • Author
31 minutes ago, Nexuss said:

On your LiBMS screenshot the discharge amps is only 50A and that is your problem. It should say 100A. Looks like your batteries are not communicating with each other to tell the inverter that there is 2 batteries thus doubling your discharge capability. Check the comms cable between the batteries . When you get the LiBMS screeen to show 100A discharge limit its working correctly . Also change the discharge amps on you charging screen to 100A as 120A is too high. I also notice you dont have signal island mode ticked , make sure you have a neutral earth relay installed and then tick signal island mode. In your system mode settings you can untick the Use timer option as that will keep the batteries full ,kind of pointless to use the timer when you dont have solar...

I think this may very well be the issue.

I read on a different forum that the C rating of the batteries do not increase in parallel - i.e. a 100AH battery at 0.5 C coupled with another will still only provide 0.5 C. 

Does this however mean that it would be 0.5 C @ 200AH meaning I could draw 100 AH in an hour (thus the whole 4.8 KW)?

  • Author

Going through the history on the most recent bout of loadshedding it also appears that my batteries SOC went downt to about 78 % after roughly 2hours / 2,15hours of loadshedding with around a 560w -1KW draw - I think this is further confirmation that the inverter is not detecting two batteries?

Edited by Balneuwes

7 minutes ago, Balneuwes said:

This is a backup system only to get me through the bouts of loadshedding  - I am unsure what a CT coil is or its function.  

I'll ask my installer about this - the way I understand is that the inverter is wired directly to all circuits on the main DB except the stove, geyser and swimming pool. 

That is important info, thanks.

You should definitely enquire with your installer about the CT coil, that is a vital part of the Sunsynk inverter to ensure it operates optimally.

5 minutes ago, WannabeSolarSparky said:

That is important info, thanks.

You should definitely enquire with your installer about the CT coil, that is a vital part of the Sunsynk inverter to ensure it operates optimally.

It almost seems like the CT coil and earth/neutral bond relay is like the bane of most installers lives. 🤣

2 minutes ago, Nexuss said:

It almost seems like the CT coil and earth/neutral bond relay is like the bane of most installers lives. 🤣

So very very true, and ALL the manuals and instruction videos highlight the importance of both.
Most of these guys just wing it and hope it all works correctly 🤑 it's mostly called greed.

  • Author

Thanks very much @WannabeSolarSparkyand @Nexuss for the helpful advice.

My installer is a great guy and I'm sure he will sort it out now that we have a good idea what the issue is.

What a brilliant and helpful forum.

My first foray into solar was a couple months ago by burning out the MPPT controller in our camp trailer (panels in series just sounded so much cooler) and having to panic research and reinstall a new Victron unit the day before our camping trip.

Really enjoying the journey to a off grid system.

Edited by Balneuwes

28 minutes ago, Balneuwes said:

Thanks very much @WannabeSolarSparkyand @Nexuss for the helpful advice.

My installer is a great guy and I'm sure he will sort it out now that we have a good idea what the issue is.

What a brilliant and helpful forum.

My first foray into solar was a couple months ago by burning out the MPPT controller in our camp trailer (panels in series just sounded so much cooler) and having to panic research and reinstall a new Victron unit the day before our camping trip.

Really enjoying the journey to a off grid system.

In addition to checking the communication cable between the two batteries you also need to check if the dip switches on the batteries have been set up correclty for the master and the slave

22 minutes ago, GreenFields said:

Maybe just a side issue, but why is the inverter set up as a slave? From what I can see you are not running multiple inverters.

If you only have one inverter it doesnt matter . The default is slave . 

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.