My understanding: in series, the entire series will run at the amps of the lowest rated panel.

So effectively, presuming similar specs, your 470w panels will be "de-rated" to 460w, no other issue. 

But as previous poster pointed out, compare the spec sheets, specifically the amp ratings.

 

To my understanding, all panels will then run as if they were all 460w panels (although 470s might offer slighly higher voltage). 

So definitely can do with a very slight loss (presuming of course the combined voltage fits the MPPT range max).

Would welcome some other expert input though 😉

Edited by markus_m2

59 minutes ago, markus_m2 said:

To my understanding, all panels will then run as if they were all 460w panels (although 470s might offer slighly higher voltage). 

So definitely can do with a very slight loss (presuming of course the combined voltage fits the MPPT range max).

Would welcome some other expert input though 😉

On a HV input inverter this should really be no issue. Less than 1% loss at peak output. Although, if it's a 5kW Deye with a 13A limit on the input, oh horror, it may be a little more.

46 minutes ago, GreenFields said:

On a HV input inverter this should really be no issue. Less than 1% loss at peak output. Although, if it's a 5kW Deye with a 13A limit on the input, oh horror, it may be a little more.

The 1st part is spot on. Due to the maximum current of 460/470W being around 10A make specific it will cause no horror on a Sunsynk with 13A allowed to each MPPT. 

The derating on amps hold true due to the lower amps of the 460W. The small higher volts of the 470W will be retained in the series string. 