Earth Leakage Tripping
23 minutes ago, Çangara said:
Hi All
Please I would like to ask Installers, How do you deal with tripping earth leakage when wiring your inverter, does one have to bypass the earth leakage?
 After main breaker before earth leakage through a current breaker to inverter input. The rating of the breaker depending on inverter size.
It's after the inverter, when it trips the plugs go off. Power still remains in other areas supplied by the inverter.
The kodak 4.6kw is supposed to do the neutral earth bond automatically.
After a few seconds the earth leakage can be switched back on and alls good in the interim. It's a intermittent thing as well.
Correct, I take it you mean 5.6kW machine. But it is still a good measure to take a voltage reading between earth and output neutral when grid is off (islanding). That reading should be close to 0Vac when the neutral is properly anchored.
Edited by BritishRacingGreen
https://segensolar.co.za/product/kodak/pv-inverter-kodak/main-unit-pv-inverter-kodak/kodak-4-6kw-grid-tied-inverter/
That's the one
Thank you for your response, will check that out