August 1, 20188 yr Project on the back burner. Got two installs going at the moment (one of them for myself) and a cattle trip to Zambia in the pipeline, so evenings are not so leisurely.
February 13, 20206 yr On 2018/06/04 at 9:11 PM, Chris Hobson said: I had the same trouble with a BEC23. Two solutions Have a constant 150W or so load and feed the wire supplying it the wrong way through the CT on the municipal supply side and this will trick the grid limiter that you import of grid power is 150W less than it really is and then your meter will not trip. Good Day Chris. I am struggling the same way with my Conlog prepaid meter and Goodwe inverter at the moment. I came across this post and I needed to respond. Can I perhaps make contact direct regarding your point 2 in your post and to email a sketch regarding my question to you? Thank you in advance
February 13, 20206 yr 2 minutes ago, Johan Gericke said: Good Day Chris Chris hasn't been around in months unfortunately. His trick is a kind of analog subtraction (the inverter reads 150W less than what is really in use), and it works well because the average power fluctuation at the site is never much larger than 150W. A large enough load change will still trip the meter. It also comes at the cost of an additional 2kWh per day to run that 150W lamp.
February 14, 20206 yr Thank you for the reply Plonkster. Possible any other suggestions regarding my scenario please? Or will the add of a Pylontech battery solve my problem much better? I am strongly thinking about that. Thanx
February 14, 20206 yr Adding a battery to the Goodwe won't stop the tripping. I am about 85% certain of that, even though I am not familiar with that inverter. The only solution that will work, and again I'm about 90% sure, is an energy diverter. This is a device that measures the power and diverts energy into a some kind of dump. Most people will divert it into a geyser, although I've done some calculations and found that a 10 liter bucket of water with a kettle element might well be sufficient. All the diverter does is detect the reverse flow of energy, and channels it into the heating element. Given that the amounts of energy we're talking about is maybe 100Wh per day, and that's about what you need to boil a liter of water, I'm fairly confident that a bucket of water will do it. The trouble is finding an affordable energy diverter. Commercial versions have to be imported and cost upwards of 3k. There is a DIY option (the one I linked above), using the arduino platform and code from the OpenEnergy project. A simple and affordable solution (for those without electronic skills) could be made using an eMonTx... but you can't buy one in this country. They are around 60USD (before import costs), and then you still need to rig up the TRIAC for switching.
February 14, 20206 yr On 2020/02/13 at 12:35 PM, Johan Gericke said: I am struggling the same way with my Conlog prepaid meter and Goodwe inverter at the moment. another option is to approach your municipality and try to get a token to deactivate the reverse flow/tampering feature of the meter.
February 17, 20206 yr On 2018/06/06 at 8:53 PM, Peter Woest said: Day 2 without any conlog trips, and a 160 watt lamp lighting up the garage during daytime..feels like a waste but it seems do do the trick. Thanx for your help Good Day Peter I have read you post and have a similar problem. Since your post - how is your system running with the 160w lamp. Any trips recently? Thanx
July 25, 20224 yr On 2020/02/14 at 12:58 PM, Fuenkli said: another option is to approach your municipality and try to get a token to deactivate the reverse flow/tampering feature of the meter. @Fuenkli has anyone managed to obtain one of these mythical tokens? I would very much like to get one, would I need to go via my electrician via the municipality? Or what would the process even be?