Axpert VM III
TL;DR: the power factor is indeed extremely low and my unit consumes very close to 50W at standby (not 35W as stated in the datasheet)
I recently bought a RCT Axpert VM III-3000-24. Upon my initial power measurements I was very concerned about the standby power usage as my clamp current meter was measuring between 1.2A and 1.3A. Upon reading this thread I decided to invest in two Kill-A-Watt units to measure the true power usage.
I currently have no solar and am running this simply as a backup UPS. After running one on the AC input and one on the inverter output I can now share my results.
  • Total test run time: 7d 10h
  • Total power in: 34.7kWh
  • Total power out: 25.2kWh
  • Ave load: 140W
  • Max load: 700W
  • Min load: 30W
  • Inverter standby power: < 50W (AC in and battery, doesn't seem to make much difference)
  • Inverter power factor with no load: 0.17
Attached are images of the power factor and standby power usage over one hour.
  • 4 months later...
  • Replies 101
  • Views 48.2k
  • Well they call it an Axpert, but it is a Hybrid inverter (hence the no-battery option) so it is probably more like the next-Gen Infini. So they have an "InfiniSolar V" which is more like an Axpert, an
  • I think you need to realize you are a bit biased. There are many manufacturers of cheap inverters and people aren't just jumping on that band-wagon. The Axpert inverters are actually incredi
  • pilotfish
    pilotfish
    This Inverter looks awesome, I WANT! Had a quick glance at the user guide, 5kVA version adds the following; 5000VA / 5000W inverter 4000W 500V MPPT BMS comms for LiFe04
Hi guys!
I have an Axpert VMIII 5Kw. No solar, just batteries - used as a backup UPS for the house. Do you know why it shuts down on overload while in the bypass mode? Why would it care? Is there a way to stop it from rebooting on overload while in bypass?
Before this model I had a 5Kw MKS and it continued to work overloaded in bypass with no issues.