F20Tz_Dc_OverCurr_Fault

Featured Replies

I created this topic here as it got no response when I joined the forum.

I have a 5.1 kW Deye hybrid inverter and a 5 kW.hr Dyness battery. I have 6.3 kW solar panels on my roof. About 2 months ago I started reverse feeding my excess solar back to the grid. All well and good.

I have a question about F20Tz_Dc_OverCurr_Fault that I get once a day (some days, there is no fault but most days there is).

My battery has a 50A Max Charge and 50A Max Discharge limit.

However, I have discovered that the battery charge current limit (red line) changes as the battery nears fully charged.

The battery charge current limit line below steps down as the battery nears fully charged.

What happens each day is that the charging current gets very close to this limit and there is an overstepping of this limit. Today, the trip occurred at 09h35. The screenshot shows 09h33 where the current limit is 20A and the battery current is 19.99A. I am at a loss to explain this but I get a trip most days around about this time of the day and it always happens within an hour or two of the this part of the day. In the initial part of the day, my battery is set to charge to 40%, after being used down to 40% during the night (well point pumps for garden).

Are there any suggestions as to how to avoid this. As far as I can see, there are no settings on the inverter that can be tweaked.image.png.26cd0265434b857a3f78dfc7894380f7.png

2 hours ago, TimJohnson said:

Are there any suggestions as to how to avoid this. As far as I can see, there are no settings on the inverter that can be tweaked.

Not sure if my suggestion will avoid or prevent the error you are getting... you are aware that you do not realistically have enough battery capacity for this inverter, I am sure... I'd suggest you slow down the charging of the battery to, let's say 20A or maybe even 15A, maximum, you seem to have enough time in hand to fill up the battery even at this lower charge rate and you'd be doing the battery more of a favour by not hitting it with quite some many electrons in the shorter time period... then see what happens with the error you are getting...

  • Author

Thanks for the getting involved.

Your answer is what I am asking.

Firstly, it came as a surprise to me that there was a variable limit for battery charging. 

There does not appear to be a way to lower the charging rate at these lower charging limits.

How do I change the charging rate to comply with these lower charging limits. The Deye interface does not provide this.

19 minutes ago, TimJohnson said:

Thanks for the getting involved.

Your answer is what I am asking.

Firstly, it came as a surprise to me that there was a variable limit for battery charging. 

There does not appear to be a way to lower the charging rate at these lower charging limits.

How do I change the charging rate to comply with these lower charging limits. The Deye interface does not provide this.

On the Battery Setting screen there's a setting for Max A Charge. As above, setting it to 15-20A should be okay since you've got lots of solar panels relative to battery power to keep charging throughout the day. A further benefit of this, since you're exporting, is that if you can set it up to still do some battery charging at around 15-20A at mid day, you can hopefully make use more of the full 6300W. If your batteries are already full by 9am, you'll only be generating 5000W of power for self-use and export at noon. 

  • Author
On 2024/11/16 at 1:18 PM, Kalahari Meerkat said:

Not sure if my suggestion will avoid or prevent the error you are getting... you are aware that you do not realistically have enough battery capacity for this inverter, I am sure... I'd suggest you slow down the charging of the battery to, let's say 20A or maybe even 15A, maximum, you seem to have enough time in hand to fill up the battery even at this lower charge rate and you'd be doing the battery more of a favour by not hitting it with quite some many electrons in the shorter time period... then see what happens with the error you are getting...

Just to be clear about my panels. I have set the inverter to only take 4.1kW from the roof. I installed more than 5 kW because of the orientation of my house (East west facing roof).

10 hours ago, TimJohnson said:

Just to be clear about my panels. I have set the inverter to only take 4.1kW from the roof. I installed more than 5 kW because of the orientation of my house (East west facing roof).

I'd let the inverter take as much as it can from the panels, but on the battery side, limit the charge current, all your loads should, I'd think be covered by the panels, assuming enough sunlight and whatever is left over  you can let it feed to the grid, I guess...

On 2024/11/16 at 10:49 AM, TimJohnson said:

I have a question about F20Tz_Dc_OverCurr_Fault that I get once a day (some days, there is no fault but most days there is).

My battery has a 50A Max Charge and 50A Max Discharge limit.

However, I have discovered that the battery charge current limit (red line) changes as the battery nears fully charged.

The battery charge current limit line below steps down as the battery nears fully charged.

 

I assume you have comms to your battery (which I'd guess is where you're getting that red Charge Current Limit graph from, right?)

My setup does the same, where my master battery BMS changes the charge limit (it updates in realtime on the BMS Info screen); depending on things like charge level or when one of the batteries in my bank gets to full before the other (it'll drop from the 2-battery-in-parallel charge limit to the single-battery limit in that case).

Perhaps your battery BMS isn't waiting long enough for the inverter to respond to the change in limit; or maybe it's providing a limit that's just a touch too high?

Have you updated the battery BMS firmware? The behavior I describe in my setup only started happening after a battery software update.

 

Failing that, setting the global battery charge limit to below the trip value as suggested above is also a workable solution (one that'll likely increase the longevity of your batteries); assuming you don't have partly-cloudy days where you need some faster charging to get to full before it rains or the like.

 

  • Author

You raise some interesting points.

Question 1:  I assume you have comms to your battery?

I assume I have battery comms. I have a wifi dongle in the inverter and I use Solarman. Really very nice as I can toggle the inverter/battery settings from Solarman as well as graphically scrutinise various inverter and battery/BMS parameters.

Question 2: Perhaps your battery BMS isn't waiting long enough for the inverter to respond to the change in limit; or maybe it's providing a limit that's just a touch too high?

Your question/statement is what I think to be happening. The screen shot I posted seems to show that the BMS is reacting too quickly. I don't know enough about which values are controlled by the inverter or the BMS.

Question 3: Have you updated the battery BMS firmware? The behavior I describe in my setup only started happening after a battery software update.

I have not updated any firmware on the inverter or the battery. I don't know how to do it. I am fairly tech savvy but have not dived into that pond.

Last bit of info. Since I started back feeding to the grid, because the panels are giving 4.1 kW most of the day, the inverter DC temperature sits at about 72C or 74C during the day. I read in one of the forums that the high DC current is the reason for the high temperature. I have just installed a 3 x 14W fans below the inverter heat sink. There has been no trips for 2 days. I did say that the trips are always in the morning and always when the charge limit is lower.

Thanks for the interest. I have not lowered the battery charge limit from 50A to 15A yet. I think that it would be defeating the purpose of of exporting my surplus power.

I might try doing it for a few days to see whether it makes a difference.

  • 3 weeks later...
  • Author
On 2024/11/18 at 12:01 PM, JayMardern said:

I assume you have comms to your battery (which I'd guess is where you're getting that red Charge Current Limit graph from, right?)

My setup does the same, where my master battery BMS changes the charge limit (it updates in realtime on the BMS Info screen); depending on things like charge level or when one of the batteries in my bank gets to full before the other (it'll drop from the 2-battery-in-parallel charge limit to the single-battery limit in that case).

Perhaps your battery BMS isn't waiting long enough for the inverter to respond to the change in limit; or maybe it's providing a limit that's just a touch too high?

Have you updated the battery BMS firmware? The behavior I describe in my setup only started happening after a battery software update.

 

Failing that, setting the global battery charge limit to below the trip value as suggested above is also a workable solution (one that'll likely increase the longevity of your batteries); assuming you don't have partly-cloudy days where you need some faster charging to get to full before it rains or the like.

 

Some feedback. After a few days, I reduced the charging current to the battery from 50 A to 19 A. I have not had a F20 fault occur, for the last 5 days. So your suggestion works.I am still evaluating whether there are any negative consequences. I am in Cape Town and the weather is unpredictable. Initially it seemed to take longer to recharge the battery after the evening usage. However there has been some rain and clouds so not sure. Still monitoring whether this is the case. Anyway, thanks for your inpuy. Much appreciated.

There is a hardware fault in your inverter. You have tried and used the low battery ampire but when you put more load on it, it will again give the same f20 error. So it is better that you repair its internal hardware. 

  • Author
On 2024/11/18 at 12:01 PM, JayMardern said:

I assume you have comms to your battery (which I'd guess is where you're getting that red Charge Current Limit graph from, right?)

My setup does the same, where my master battery BMS changes the charge limit (it updates in realtime on the BMS Info screen); depending on things like charge level or when one of the batteries in my bank gets to full before the other (it'll drop from the 2-battery-in-parallel charge limit to the single-battery limit in that case).

Perhaps your battery BMS isn't waiting long enough for the inverter to respond to the change in limit; or maybe it's providing a limit that's just a touch too high?

Have you updated the battery BMS firmware? The behavior I describe in my setup only started happening after a battery software update.

 

Failing that, setting the global battery charge limit to below the trip value as suggested above is also a workable solution (one that'll likely increase the longevity of your batteries); assuming you don't have partly-cloudy days where you need some faster charging to get to full before it rains or the like.

 

Another twist to the story.

When reading the causes of the F20Tz_Dc_OverCurr_Fault the focus of the causes all zoom in on the DC current produced by the solar panels.

So, I decided to set the battery charge/discharge back to 50A as per the battery and inverter specs, and I also decided to reduce the Max Solar Power limit down from 4.2 kW to 3.5 kW. Since doing this the daily tripping has stopped

This has been the case for the last 2 day.

I will monitor how long this remains as is. If it stay like this, I will gradually up the Max Solar Power limit by 100 W and see how high it can be set before it initiates a trip.

I will then leave the Max Solar Power limit at that value.

I don't lnow why the solar panels are spiking but I can live with this.

  • 1 month later...
  • Author

Okay, it's 2025 and until a few days ago, I was still getting the F20 fault at least once a day.

Here, however, is the final outcome.

I contacted my original installer and told them that the fault had been going on for a long time (8 months).

They did some remote inverter setting changes, including an inverter firmware upgrade, but to no avail.

Eventually, they sent out a 12 year solar veteran installer. His mandate was to inspect the inverter, and if neccessary, take out the inverter for repairs or replacement.

He was outstanding and proceeded to check all of the DC connections inside and out side the inverter.

Eventually, he opened up the DC PV DB and lo and behold, one of my 2 solar arrays was not functional due to a wire from one of the solar arrays not being plugged in.

So for about a year, I have only had half of my solar capacity functional. That is is why I was getting an over current error.

He connected the wire and problem solved.

Now, I have my max solar power set to 6.5 kW (as per the Deye specifications for a 5 kW inverter). I was at some stage running the inverter at 3.5 kW. No settings are tweaked back.

The installer has waived any costs as the fault was caused by them.

Needless to say I am very happy.

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.