January 18, 20251 yr I'm busy with a parallel installation with two of these - so far just connected to the batteries via a bus bar. Communiaction and current sharing cables not installed yet and PAL setting not activated. Voltage reading at terminals for both inverters are 52.6 V via a multimeter, but one inverter reads 53.0 V and the other 52.1 V. I'm suspecting that this will cause an issue once I activate the parallel settings. Anyone have guidance for calibrating these inverters - the manual seems to refer to such a possibilty. Much appreciated in advance!
January 20, 20251 yr These instructions need cleaning up, but all the information is there: https://forums.aeva.asn.au/viewtopic.php?p=71631#p71631 Being MAX models, you will need the ATE1 command. Use the communications tool.
January 20, 20251 yr 3 hours ago, Shadders said: I shared the SOP I wrote up using the information linked above Hey, neat! I have linked your file at the top of the calibration post. Thanks for doing that; it was sorely in need of a clean up.
February 2, 20251 yr Author Thank you @Coulomb and @Shadders. Can confirm that this works on my Kodak 7.2 kW by following Shadders PDF and using the communication tool link in the same doc.