April 22, 20197 yr I connected 3 x 5kva Mecer inverters in parallel. My problem is that one inverter doesnt show "slave". The voltage on that one is also different from the other two inverters. One shows master and one shows slave but the other one doesnt show anything in the centre of the screen. They are connected as described in the manual. Any sugestions where to start? Edited April 22, 20197 yr by George Posted before i completed typing
April 22, 20197 yr check the battery connection to the third inverter first Edited April 22, 20197 yr by ibiza
April 22, 20197 yr Author Checked it. Voltage is exactly the same as the other two. Cabling is secured. Also checked the settings. All settings are the same except for 28. Inverter 1 =PAL. inverter 2=PAL and inverter 3= S1G. But inverter 3 does not adjust nr 28. So it seems like it reads inverter 1 as the master.
April 22, 20197 yr strange, incerter no 3 should be set to "pal" too. sometimes helps if you disconnect the batts from the inverters and connect them again (restart) Edited April 22, 20197 yr by ibiza
April 22, 20197 yr 1 hour ago, George said: Checked it. Voltage is exactly the same as the other two. Cabling is secured. Also checked the settings. All settings are the same except for 28. Inverter 1 =PAL. inverter 2=PAL and inverter 3= S1G. But inverter 3 does not adjust nr 28. So it seems like it reads inverter 1 as the master. Just remember setting no 28 can only be adjusted with the inverter switched of .
April 23, 20197 yr Author This morning i switched off everything. Tried the 3td inverter again and it took the PAL setting. Switched back on and so far everything is working normal. Thanks for the guidance and info. Regards.