I bought a 5kva Hibrid inverter and a 48v lithuim battery what size cable do I use from the inverter to the distribution board and back to the inverter? I bought a 16mm twin earth cable but the installer say it should be 6mm the supplier sold me the 16mm. Which is the right cable to use

Link to post
Share on other sites

5 answers to this question

Recommended Posts

  • 0
14 hours ago, Rallybert said:

I bought a 16mm twin earth cable but the installer say it should be 6mm the supplier sold me the 16mm.

16 mm² is giant for twin-and-earth house cable. You likely can't get that into the inverter terminals. 6 mm² (that's cross-sectional area, not linear width) is good for 38 A (~8.7 kVA) in all conditions, so that should be plenty.

Link to post
Share on other sites
  • 0

I was advised that drawing 10mm (if you have 63amp breakers) for the backbone in your house is better. If at some point you want to upgrade the inverter to something that can transfer more than 40A (the limit on 6mm), then you are stuck. It isn’t much more expensive, so just draw 10mm from the get go, then you don’t place a bottle neck into your infrastructure.

Link to post
Share on other sites
  • 0
59 minutes ago, jykenmynie said:

I was advised that drawing 10mm (if you have 63amp breakers) for the backbone in your house is better.

16mm for 63 Amp, 10mm for 50Amp, 6mm for 40Amp, 4 mm for 30Amp, 2,5mm for 25amp and 1.5mm for 15Amp. Over normal residential distances, for longer distances you would upsize the cable. This is SANS in a nutshell, different mounting methods might have different current carrying capacity ratings. 

Link to post
Share on other sites
  • 0
11 minutes ago, Jaco de Jongh said:

16mm for 63 Amp, 10mm for 50Amp, 6mm for 40Amp, 4 mm for 30Amp, 2,5mm for 25amp and 1.5mm for 15Amp. Over normal residential distances, for longer distances you would upsize the cable. This is SANS in a nutshell, different mounting methods might have different current carrying capacity ratings. 

In that case, definitely put in the 16mm. You’ve got nothing to lose and you have a hybrid inverter, so rather be safe than sorry.

Link to post
Share on other sites
  • 0
On 2020/07/18 at 7:18 AM, Coulomb said:

16 mm² is giant for twin-and-earth house cable. You likely can't get that into the inverter terminals. 6 mm² (that's cross-sectional area, not linear width) is good for 38 A (~8.7 kVA) in all conditions, so that should be plenty.

Thank you much appreciated

Link to post
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Answer this question...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...