April 10, 20215 yr 7 hours ago, Frost said: O okay so just a guideline then, if you generate more that 5.5 kw and your batteries are not full do the extra generation get wasted or does it still goes to the batteries? Do you also have the problem with the high pitched noise form your 5kw sunsynk? Batteries will always get charged first, unless there are loads and "priority loads" is ticked. If batteries are full, then the inverter does not "waste" the excess, it will only draw whatever it needs, so if loads are at 600W, it will draw 600W (or slightly more to compensate for inefficiency). Agreed that technically it is wasted "potential", but as discussed before this potential can be directed to a smart load, like your geyser. The Sunsynk Super Hybrid is very flexible. If the panels generate more than 5.5Kw then you will have one of two problems: 1) either the voltage will exceed the 500V max limit, in which case it will probably blow the MPPT (volts are very important in array sizing), or 2) the amperage will exceed the specs and the MPPT will clip it. This is wasted potential. The 5.5K Sunsynk is (anecdotally) known to clip at 9.9A even though the specs state 11A and maximum DC input power is stated at 6500W. See the Sunsynk tech forum thread here.
April 12, 20215 yr 12 hours ago, Vassen said: Well not really. Even if the voltage is 400V and the current on both string 9.9A, let’s say 10, that’s still 8kw. I saw on the sunsynk forum Keith mentioned something about 2.75kw per mppt, but that doesn’t make sense as my 1 gives around 2.9kw and has a lot more room. Thanks for the correction, I was thinking about per MPPT.
April 12, 20215 yr Author 13 hours ago, Vassen said: Well not really. Even if the voltage is 400V and the current on both string 9.9A, let’s say 10, that’s still 8kw. I saw on the sunsynk forum Keith mentioned something about 2.75kw per mppt, but that doesn’t make sense as my 1 gives around 2.9kw and has a lot more room. So does this mean I have to look for panels with 9.9lmp or less to get the max out of the pv array, the higher rated panels will clip? Does this then also apply to the 8kw when using 2 strings per mppt, I see the max input 18Amp so its 9amp per string?
April 12, 20215 yr 6 minutes ago, Frost said: So does this mean I have to look for panels with 9.9lmp or less to get the max out of the pv array, the higher rated panels will clip? Does this then also apply to the 8kw when using 2 strings per mppt, I see the max input 18Amp so its 9amp per string? You've already stated that you want to oversize for bad solar days, so I'd recommend that you try and get the latest 8K Sunsynk with 22A MPPT to allow sufficient latitude with a wide range of panels / configs. The amps doesn't matter too much because it will be clipped by the MPPT, but voltage is critical, Sunsynk recommend not exceeding 450V per MPPT. Alternatively you can wait for the newer 10 and 12K Sunsynks, specs and details may be available this week still.
April 13, 20215 yr Author 22 hours ago, YellowTapemeasure said: You've already stated that you want to oversize for bad solar days, so I'd recommend that you try and get the latest 8K Sunsynk with 22A MPPT to allow sufficient latitude with a wide range of panels / configs. The amps doesn't matter too much because it will be clipped by the MPPT, but voltage is critical, Sunsynk recommend not exceeding 450V per MPPT. Alternatively you can wait for the newer 10 and 12K Sunsynks, specs and details may be available this week still. Yes that's my plan to oversize think i will go the 8kw route, just need to balance my loads during the day.
April 13, 20215 yr Author 22 hours ago, Vassen said: Don’t get something with too high current as the losses will be more. The Mono panels seem to have a higher voltage and lower current compared to the poly cells or this was my observation based on the few I looked at. I’m also looking for some panels for another string. I’ve come across some 78 cell JA panels. JAM78S10 range is around 450W and current is in the range of the 9.9A. Will work well for the sunsynk. I can’t seem to find local stock though. Okay i went for the 8kw with 22A mppt and 24 x 455 Mono = 10920W they are rated 10.84A so will be just in the limit on 2 strings. Not enough stock on the 410 or 415 pannels so best option thats in the range was the 455w. They will come install the brackets tomorrow then the rest of the stuff Friday and Saturday. Thanks for all the help.
April 13, 20215 yr Author 1 hour ago, Vassen said: Wow. Where did you find the 22A version. He send me this on the ones he have available, so i really hope it is 22A per mppt
April 13, 20215 yr 7 hours ago, Frost said: He send me this on the ones he have available, so i really hope it is 22A per mppt When you get it post a pic of the label on the inverter. That max DC power is incorrect as it can take 10 500w of solar panels.
April 14, 20215 yr Author 13 hours ago, Achmat said: When you get it post a pic of the label on the inverter. That max DC power is incorrect as it can take 10 500w of solar panels. Okay i will as soon as it arrives. If its not 22A it means i will loose on the production side when it clips?
April 14, 20215 yr 2 hours ago, Frost said: Okay i will as soon as it arrives. If its not 22A it means i will loose on the production side when it clips? Correct
April 20, 20215 yr Author On 2021/04/14 at 11:08 AM, Achmat said: Correct He is coming to do installation tomorrow, he waited for stock on the 22A inverter hopefully he gets one. What would be the max 455w panels I can add to this inverter and in what configuration? I now see that with the winter sun moving more to the north the neighbors tree will cast some shadow on my panels, and was thinking to add some panels on the western side but not sure what would my max be ?
May 6, 20215 yr Author So everything is up and running now for about 2 weeks, seems to work great so far. after waiting for new stock the unit was also a 18.8A but i have seen the amps go to 19.9A how can i see if it is clipping ?
May 6, 20215 yr 9 minutes ago, Frost said: So everything is up and running now for about 2 weeks, seems to work great so far. after waiting for new stock the unit was also a 18.8A but i have seen the amps go to 19.9A how can i see if it is clipping ? Put a constant load on it, observe the amps. Some of the older Sunsynk 8K inverter MPPTs are 22A capable after a firmware upgrade, I have seen Sunsynk support confirm it on the Whatsapp support group, they first need to check the side sticker though.
May 6, 20215 yr Author 12 minutes ago, YellowTapemeasure said: Put a constant load on it, observe the amps. Some of the older Sunsynk 8K inverter MPPTs are 22A capable after a firmware upgrade, I have seen Sunsynk support confirm it on the Whatsapp support group, they first need to check the side sticker though. Should i monitor the Pv amps, i cant see that it is clipping some days it idle for few minutes at 18.9 then some days when the sun comes through the clouds it jumps to 19.5- 19.9A.
May 6, 20215 yr 50 minutes ago, YellowTapemeasure said: Put a constant load on it, observe the amps. Some of the older Sunsynk 8K inverter MPPTs are 22A capable after a firmware upgrade, I have seen Sunsynk support confirm it on the Whatsapp support group, they first need to check the side sticker though. How would they know? Is it from a particular batch or series of serial numbers? Would love to know if mine is included in this list.
May 6, 20215 yr 4 minutes ago, Achmat said: How would they know? Is it from a particular batch or series of serial numbers? Would love to know if mine is included in this list. I am not sure. Ask Shabir to add you to your suppliers' Whatsapp support group and ask them.
May 6, 20215 yr 1 hour ago, Frost said: Should i monitor the Pv amps, i cant see that it is clipping some days it idle for few minutes at 18.9 then some days when the sun comes through the clouds it jumps to 19.5- 19.9A. Look at the graph of PV amps, if you have a constant load and clipping, the normally round curve will have a flat top instead.
May 6, 20215 yr 6 hours ago, YellowTapemeasure said: Look at the graph of PV amps, if you have a constant load and clipping, the normally round curve will have a flat top instead. Hrs the most useless support tech I've come across. Sent him a WhatsApp immediately after you posted and he still has not responded to my query. Edit Quoted the wrong post. Edited May 6, 20215 yr by Achmat
May 19, 20215 yr On 2021/05/06 at 1:31 PM, YellowTapemeasure said: I am not sure. Ask Shabir to add you to your suppliers' Whatsapp support group and ask them. @leshen sorted me out. He checked and confirmed that my inverter supports 22A per mppt and he is facilitating the firmware upgrade.
May 19, 20215 yr 2 minutes ago, Achmat said: @leshen sorted me out. He checked and confirmed that my inverter supports 22A per mppt and he is facilitating the firmware upgrade. Always glad to help. They are busy with your upgrade.
May 19, 20215 yr Author 1 hour ago, Achmat said: @leshen sorted me out. He checked and confirmed that my inverter supports 22A per mppt and he is facilitating the firmware upgrade. How do i get check and get my firmware updated, i have requested on the sunsynk whatsup no but still seems to be the same version? @leshenwould you be able to confirm my inverters max input also?
May 19, 20215 yr 2 minutes ago, Frost said: How do i get check and get my firmware updated, i have requested on the sunsynk whatsup no but still seems to be the same version? @leshenwould you be able to confirm my inverters max input also? Hi. Please send me your inverter serial number and logger number and I’ll check for you and request an upgrade.
May 19, 20215 yr 1 hour ago, leshen said: Always glad to help. They are busy with your upgrade. Got a panic call from my wife just after I left home as everything went off and nothing tripped on the DB. Told her to wait as I think they are busy with the upgrade. Everything seems to be back online again.
May 19, 20215 yr Author 3 minutes ago, leshen said: Hi. Please send me your inverter serial number and logger number and I’ll check for you and request an upgrade. Thanks alot, will pm you