Sunsynk 5.5 please help!!

Featured Replies

Hi Wisemen of the Powerforum.

Need help with with a Sunsynk 5.5

I have my own Sunsyk and am reasonably comfortable with the settings needed to utilize solar for the "grid side"

however with a friends inverter the settings seem to be operating in reverse.  

When I tick "limit to load" then it pushes power to the grid side.

when I untick  "limit to load" then it pushes NO power to the grid side

See the pictures below.

Settting 1.jpg

20 minutes ago, Dani said:

2028558922_Result1.thumb.jpg.d6e596690bef57273ef3e5624c73404f.jpgResult it pushes to the grid side.

There are two current coils. The one is internal, and is reflected by the value LD. 

 

The CT coil is the one in your DB. That should read 0W when you're not pulling or exporting, which here looks fine. I assume you have a load on the grid side, between the CT coil and the inverter pulling 1104W. 

 

Adding the power consumption together we have 627W+1104W which adds up to the 1721W output of the inverter. Either way, you want 0W on CT when your solar is covering all your utilisation, and that is what I see above.

22 minutes ago, Dani said:

491124272_Result2.thumb.jpg.7838d4c61bf4b9457b34a037939b755c.jpgNo power goes to the grid side??

Here you appear to be using 1124W from Eskom which is correct as you've now limited the inverter power to the inverter outputs, not the grid side. Whats on your grid side using 1124W? Pool pump perhaps or heat pump?

 

As a test I quickly did the same on my inverter and ticked the limit to load. Immediately I saw 34W on the CT coil which is the expected power consumed by my electric fence which is on the grid side.

 

As far as I can tell your system is working exactly as it should. Untick limit to load if you want the grid side to be fed from solar and battery as well. Power should not push back further than the CT coil.

Your system is configured incorrectly. There's a wiring issue somewhere or the CT is at the incorrect location or connected to the incorrect pins on the inverter. 

  • Author
40 minutes ago, Paul Greeff said:

As far as I can tell your system is working exactly as it should. Untick limit to load if you want the grid side to be fed from solar and battery as well.

Thats the weird thing.

the tick seems to be working in reverse??

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.