Phillip87 Posted October 3, 2022 Share Posted October 3, 2022 The Sans Regulations supersedes the inverters installation manual, the documents state that all installs should adhere to Sans10142 the bonding relay would make this a non compliant installation as the regulations require a permanent earth neutral bond on the output side of an alternate supply source before it is wired to the changeover switch input. Non essential/essential loads needs a separate neutral bar, the inverter must have a separate grounding rod, reason being if the changeover is switched to the inverter the Bond is broken on the utility side and effectively on all essential loads if there is no earth spike with a bond the inverter wont have a zero voltage reference. Sipproxy 1 Quote Link to comment Share on other sites More sharing options...
Surge Posted October 13, 2022 Share Posted October 13, 2022 (edited) I haven't installed solar yet but I was thinking about this whole earthing issue and it seems to be overly complex with regards to regulations. I am wondering if an isolation transformer would not be simpler option and avoid violating any regulations? In other words install a 230 to 230 VAC transformer between the supply/grid and the inverter with it's own supply DB (and RCD if required). Then permanently ground the output of the inverter to earthing spikes so that the downstream RCD in the main DB always works on the local earthing point. Then there is always an earth reference even though it is not connected to the grid earth. If one is practically off-grid and only needs say 1kVA to top up batteries on cloudy days then the "shore power" to be imported from the grid can be limited on the inverter settings. This keeps the isolation transformer small and cheap enough. It shouldn't matter if the two earths or neutrals on each side are not referenced to each other. If Eskom/Muni screws up and has a floating neutral on their side (I've seen that happen more than once) it also won't cause any issues on the inverter side because the voltages are decoupled and float relative to each other. Would something like that work and still be legal or is there specific wording which forces one to carry the grid earth into the main DB for earthing requirements? Edited October 13, 2022 by Surge Quote Link to comment Share on other sites More sharing options...
jraydoran Posted April 2, 2023 Share Posted April 2, 2023 On 2021/03/22 at 6:17 PM, ianm said: Okay, thanks, so then the circuit would be: Thank you ianm for a great drawing! I know this is an old Post, but this is how I plan to wire mine up. It makes perfect sense. My question is regarding the Earth Wire 1) I assume that the main earth wire from the Grid is wired to the Grid "Input" terminal on Inverter. 2) I am confused about the Earth wire on the Load Side. Must this be wired from the Load terminal on the Inverter to the Earth bar? OR should I use the "DB earth" that was bonded on the load side? Any help will be appreciated! Kind Regards Jason Quote Link to comment Share on other sites More sharing options...
Karl Daschner Posted April 14, 2023 Share Posted April 14, 2023 Jason good question I also want to know. On Sunsynk documents it says not to connect anything to the load earth terminal if you in SA. jraydoran 1 Quote Link to comment Share on other sites More sharing options...
Karl Daschner Posted April 28, 2023 Share Posted April 28, 2023 I rang it out Jason, all 3 earth terminals on the 5kW Sunsynk is internally connected. So u only need to connect to one of them with your house earth. jraydoran 1 Quote Link to comment Share on other sites More sharing options...
PowerUser Posted April 28, 2023 Share Posted April 28, 2023 On 2023/04/14 at 10:23 AM, Karl Daschner said: Jason good question I also want to know. On Sunsynk documents it says not to connect anything to the load earth terminal if you in SA. Which SunSynk document is that? Do you have a link? Quote Link to comment Share on other sites More sharing options...
Karl Daschner Posted April 29, 2023 Share Posted April 29, 2023 this one Quote Link to comment Share on other sites More sharing options...
PowerUser Posted April 29, 2023 Share Posted April 29, 2023 1 hour ago, Karl Daschner said: this one This diagram is a bad example. The inverter does not get wired like this in South Africa. The load and grid neutrals have to be split. The diagram shows them wrong as connected together. Quote Link to comment Share on other sites More sharing options...
jraydoran Posted April 29, 2023 Share Posted April 29, 2023 2 hours ago, Karl Daschner said: this one This is the drawing I was also using that was confusing me. I agree, this is not how a typical installation in SA is done. I followed the drawing from @ianm but the earthing was not show. Thank you so much for all the advice and input. Really appreciated. Kind Regards Jason Quote Link to comment Share on other sites More sharing options...
Vaal Posted May 7, 2023 Share Posted May 7, 2023 On 2021/03/22 at 6:17 PM, ianm said: What would the reason be to install the four 25A MCB in front of the SPD's? Quote Link to comment Share on other sites More sharing options...
Scorp007 Posted May 7, 2023 Share Posted May 7, 2023 7 hours ago, Vaal said: What would the reason be to install the four 25A MCB in front of the SPD's? So that they can trip and cause a break to the surge unit. Once tripped the surge will have to jump the gap to go further to cause damage. My own way of reasoning. Quote Link to comment Share on other sites More sharing options...
Vaal Posted May 7, 2023 Share Posted May 7, 2023 (edited) 2 hours ago, Scorp007 said: So that they can trip and cause a break to the surge unit. Once tripped the surge will have to jump the gap to go further to cause damage. My own way of reasoning. But if the breaker trips, then there is no spd in that line. That sounds counter productive. There is no mcb in front of my spd's. The spd is a sacrificial device. Edited May 7, 2023 by Vaal Quote Link to comment Share on other sites More sharing options...
Scorp007 Posted May 7, 2023 Share Posted May 7, 2023 (edited) 29 minutes ago, Vaal said: But if the breaker trips, then there is no spd in that line. That sounds counter productive. There is no mcb in front of my spd's. The spd is a sacrificial device. You are spot on. Then there is no surge to clamp and no surge to get to the MPPT. As unproductive as you see it if you look into power supplies you will see it is very common. Only fuses are normally used as it creates a much longer gap. Fuse between connector and MOV. Edited May 7, 2023 by Scorp007 Quote Link to comment Share on other sites More sharing options...
Scorp007 Posted May 7, 2023 Share Posted May 7, 2023 14 minutes ago, Scorp007 said: You are spot on. Then there is no surge to clamp and no surge to get to the MPPT. As unproductive as you see it if you look into power supplies you will see it is very common. Only fuses are normally used as it creates a much longer gap. Fuse between connector and MOV. I would take a lead from one of our great installers. It does not mean if you don't have fuses/MCBs yours is done the better way. Yes cheaper for sure. Quote Link to comment Share on other sites More sharing options...
frivan Posted May 7, 2023 Share Posted May 7, 2023 39 minutes ago, Vaal said: But if the breaker trips, then there is no spd in that line. That sounds counter productive. There is no mcb in front of my spd's. The spd is a sacrificial device. If you install breakers before a SPD, someone can easily restore power if the device shorted. There won't be surge protection on the system but someone sold four more breakers and a larger DB. Quote Link to comment Share on other sites More sharing options...
Vaal Posted May 7, 2023 Share Posted May 7, 2023 Now I missed you. You get a surge from grid side, due to what ever reason. As soon as the spike hits the spd it divert it down to earth and no more spike and possible the spd is no more anymore. On the drawing there isn't any mention of pv input but I would think it will work the same way. If you get more than one decent spike and the spd is blown then the next "soft/sensitve" spot in line will take it on the nose and go poef. Quote Link to comment Share on other sites More sharing options...
Scorp007 Posted May 7, 2023 Share Posted May 7, 2023 (edited) 21 minutes ago, Vaal said: Now I missed you. You get a surge from grid side, due to what ever reason. As soon as the spike hits the spd it divert it down to earth and no more spike and possible the spd is no more anymore. On the drawing there isn't any mention of pv input but I would think it will work the same way. If you get more than one decent spike and the spd is blown then the next "soft/sensitve" spot in line will take it on the nose and go poef. Yes I agree. But once the fuse is blown then no 2nd spike and no poef either SPD can take a number of spikes it depends on the intensity. What about the solar panels? They are the example used. Edited May 7, 2023 by Scorp007 Quote Link to comment Share on other sites More sharing options...
jraydoran Posted May 7, 2023 Share Posted May 7, 2023 12 hours ago, Vaal said: What would the reason be to install the four 25A MCB in front of the SPD's? SPD’s fail in 2 ways. 1) open circuit 2) Short circuit These MCB’s on there to protect against short circuit scenario 2) The sizing is related to the cable size. It is there to protect cable. It is also in the Sunsynk manual, but on the earth wire. Does the same thing. Kind Regards Jason Quote Link to comment Share on other sites More sharing options...
Vaal Posted May 8, 2023 Share Posted May 8, 2023 10 hours ago, jraydoran said: SPD’s fail in 2 ways. 1) open circuit 2) Short circuit These MCB’s on there to protect against short circuit scenario 2) The sizing is related to the cable size. It is there to protect cable. It is also in the Sunsynk manual, but on the earth wire. Does the same thing. Kind Regards Jason Aha. Thank you Jason. I thought they all expired in a open circuit condition. Quote Link to comment Share on other sites More sharing options...
Denver Posted September 11, 2023 Share Posted September 11, 2023 Please send me clear picture s of your wiring diagrams Quote Link to comment Share on other sites More sharing options...
Greglsh Posted September 29, 2023 Share Posted September 29, 2023 Just wanted to ask is it okay if I use a 40A MCB on the supply and output of the SunSynk 5kw inverter Quote Link to comment Share on other sites More sharing options...
TaliaB Posted September 29, 2023 Share Posted September 29, 2023 Just wanted to ask is it okay if I use a 40A MCB on the supply and output of the SunSynk 5kw inverter Yes but use correct wire size 10mm² Greglsh 1 Quote Link to comment Share on other sites More sharing options...
Recommended Posts
Join the conversation
You can post now and register later. If you have an account, sign in now to post with your account.