Everything posted by Coulomb
-
Need Firmware sunlife inverter 4kw dual output inverter
I'm not aware of any genuine Axperts with the round screen and 4 kW Twin. But there are so many models these days. Can you post your present main (U1) and display (U2) version numbers. Sorry for the late reply.
-
Need Firmware G Power inverter 6kw dual
This looks like it might be an Axpert or clone. Can you post the main (U1) and display (U2) firmware versions, if they are so called?
-
AXPERT MAX II 11KW (MKS2-11000) -F90 Error-
Fault code 90 is specifically designed to thwart clone makers who steal Voltronic firmware and undercut their sales. Unfortunately it is the purchaser that gets punished, not the clone manufacturer. I'm away from my main computer at present, but I may have a solution. PM me as I'm really busy at present. Edit: It looks like merely updating to factory firmware version 73.78 will work, or patched firmwares based on that. All available here: This seems to be a clone, and they appear to be using E firmware with a II display. I don't know what the ramifications of this are; perhaps the RGB lighting won't work, perhaps something serious. I'd say you have nothing to losing trying one of the above firmwares.
-
Extra batteries
450mA? These units make no sense. Perhaps you mean 450 V and 200Ah? For the battery capacity setting, it's not specified directly, but will affect the maximum charging current setting.
-
Axpert Firmware
Sorry, I'm running extremely late with replies. Your inverter claims to be a VM III, but I'm not seeing a removable display. Is there one? Without a removable display, there is no ARM processor to talk to the BMS and to offer battery types of PYL and so on. I would also expect the U2 firmware version number to be 02.xx.
-
Hi Coulomb, what are the advantages of 400v PV input if the 400v is converted to 48-50v for battery input
I very much doubt it, that's a very low voltage. Also, the high PV voltage models require pulses from the DSP, and it would be trying to regulate bus voltage, not battery voltage. So almost certainly you can't use the "wrong" type of solar charger. As for which models do which, just check the PV charging specs. The voltages will tell the story.
-
Hi Coulomb, what are the advantages of 400v PV input if the 400v is converted to 48-50v for battery input
Sorry for the very late reply. No, the Voltronic high PV voltage models (450-500 V max PV) boost the PV voltage (if needed, else pass through) and it's used as the DC bus voltage. To charge the battery from PV, this power is then pushed back to the battery by running the DC-AC converter in reverse (effectively making it an AC to DC converter). It also runs the DC-DC stage (bus to/from battery voltage) in reverse. The power flow can change dynamically as loads and available PV power go up and down. If necessary, the buck stage will reduce the voltage to the DC-DC converter stage when charging the battery. Only the 145 V max (and lower) Voltronic models buck directly to the battery voltage. The reason for this disparity is efficiency. Transformerless power converters (which in an Axpert is all of them except for the DC-DC stage) work more efficiently when the ratio of input to output voltage isn't too large. So bucking directly from say 400 VDC panels to 50 VDC battery is an 8:1 difference; it would not be efficient. 130 V bucking down to 50 V (2.6:1) or 120 V up to 360 V (1:3) is acceptable, but you get better performance when bucking down from 80 V or boosting up from 320 V.
-
Max 8000
The problem is that this is a clone inverter, using stolen firmware. Voltronic got sick of this and put traps in the firmware to cause fault code 90 to come up after 60 days of running, if it detects that it's running in a clone. How long the inverter is running as a clone is stored in the EEPROM. That's why erasing the EEPROM gives it another 60 days. But you also lose all your settings and calibrations.
-
Error 08
It's usually panel leakage to earth that is the problem. Though it should not matter if the grid is present or not; only if the inverter is producing AC from any source. Try isolating the PV input to see if that stops the problem. Note that it can still happen at night, as it's the voltage from the PV wires to earth that is the problem, not the voltage from one PV wire to the other. In fact, many users find that this fault only happens at night, and some use a relay to isolate the panels automatically every night.
-
RCT InfiniSolar V2/Vii 5kw-48V failure
The service manuals don't appear in normal web sites. They occasionally appear in the same places that firmware can be found. I checked my present locations and don't find any for Infini VIIs, sorry.
-
RCT InfiniSolar V2/Vii 5kw-48V failure
Sorry, I know next to nothing about the Infinisolars. There are enough Axpert (off-grid) models to keep me busy and tizzy. Unfortunately, fault code 09 is usually not an easy or inexpensive fix, at least for Axperts. Especially after a burning epoxy smell. Usually it means that IGBTs and/or MOSFETs have fried, usually plus a handful of small components that if not fixed fry the next set of power transistors. Check the file section for Infinisolar manuals. Some Infinis, especially the Infini V series, use similar or nearly identical hardware to the Axperts; if so, the various Axpert schematics and guides can be helpful. Others are totally different in basic circuitry.
-
AXPERT MAX II 8kw firmware
That means that the display firmware no longer talks to the main firmware. What was the main firmware before the update? You might be attempting to use the wrong firmware. It might also just be a glitch due to the cheap and sometimes slow opto-couplers. See If You Think Your Inverter is Bricked.
-
Axpert King II bypass function in parallel connection
There is some functionality, I think to do with ECO mode, that goes away when Kings are paralleled. Read the manual carefully, in the section describing each setting.
-
Axpert King II need control panel firmware
King II firmwares are very confusing. My collection of King II main (U1) firmwares are only 50.xx and 70.xx. I have various display firmwares that are supposedly for King IIs, including one that seems to report as 51.02! So until I get some clarity, I can't make suggestions for what to update to. Sorry! Also sorry for the late response.
-
MPPT Patch for EAsun Inverter
I'm amazed and pleased that you didn't need a 128-bit password to unlock the firmware. On many other models you certainly do.
-
Update axpert vm iii 6kw
Sorry for the very late reply. Firmware version 68.04 is for Axpert VM III 4 kW or 6 kW models, with Twin outputs. I'm not sure if 55.03 is a Twin firmware or not, but 55.06 is for non-Twins. I don't know what the effect is of running Twin firmware on a non-Twin model; I would not recommend it. I assume that you have found the 68.04 firmware update file; if not, it's in this post. You are probably better off updating to 55.06, the latest 55.xx that I know of, despite the known issues. The VM IIIs don't seem to be very popular, and so firmware update files are rare for this model. Or simply ask your supplier for a firmware update, quoting your problems and perhaps also those reported for 55.06. The same firmware runs both 24 V 4 kW and 48 V 6 kW models, automatically adapting to the hardware it runs on.
-
Kodak OG5.6kw Parallel
Yes. sorry for the painfully late reply. It sounds like actually you may need the "capacitor mod", either do it yourself if you can do it safely, or get someone to do it. There is a small chance that it's firmware related. Here is the latest firmware in case you want to try it. 52.10 is about 8 months more recent than 52.00. Your Kodak seems to be a rebadge of an Axpert MKS IV. This is main (U1) factory firmware version 52.10 for the Axpert MKS IV 5.6kW '28066 Non-twin. Do not use with any other model or version. Use at your own risk. The hex file is dated 10/07/2024. Firmware upload instructions for models with a colour display. This firmware processes the QDOP command, so with suitably recent display firmware, it should support SoC% for settings 12,13, and 29 when connected to a suitable battery's BMS. The RAR file password is "flash", without the quotes. MKSIV_Inverter_Main_Reflash_Ver52.10 pw flash.rar
-
Beta Tester O N L Y AXPERT MAX 7.2KW MPPT improvement
Looks like 90.19 to me. No, it's "live" on this firmware. P.s. sorry for the very late reply, a whole month after you posted. I've been really busy on another project.
-
AXPERT MAX II 8kw firmware
My understanding is that it will work, but you won't call the calibrate function that is burned into your processor's Read Only Memory, and your readings may be inaccurate as a result. I don't know the consequences of that. So I don't recommend it, but my guess is that it won't be a disaster. Going the other way (attempting to use a '28066 firmware on an inverter with a '2809 processor) almost certainly WILL brick the inverter. It will attempt to call a calibrate function in non-existent (or at least unprogrammed) Read Only Memory, and this is very early on before even interrupts are enabled.
-
Need correct firmware for Sunpolo 8.2 kW / Axpert MAX 8 kW (only showing HID, no COM port, F90 fault)
Your photo shows U3 02 00; I need the U1 firmware version. Sorry for the late reply; I've been really busy.
-
Repair of Axpert Inverters : A Journey Started
Yes, battery side capacitors could be dry. But the battery should absorb most of that ripple; I suspect either the battery itself or the battery cables have high resistance. Actually, with the ripple on the DC bus, the DC bus capacitors could be dry as well. Unfortunately, I have no experience with the 12 V models.
-
Axpert MAX E Twin 11KW inverters firmware mismatch - To be working in parallel
Sorry for the late reply; it's been busy here. That's probably the same as running 11 kW firmware on a 7.2 kW model. It will likely work, except that it won't protect itself from loads over 7.2 kW. Twin means exactly that: it has hardware and firmware to support an extra relay and output terminals. You can adjust settings for how and when the extra output comes on.
-
Need correct firmware for Sunpolo 8.2 kW / Axpert MAX 8 kW (only showing HID, no COM port, F90 fault)
That's because the manufacturer stole the firmware and didn't contribute to the development costs. Voltronic firmware checks for clone-ness, and if so, brings up fault code 90 after 60 days of runtime. You might be able to rescue it. You should be able to find the existing firmware version by using the arrow keys until U1 appears at the bottom left of the display. Report any digits after that. I note that updating the firmware alone will not fix the issue. You need someone to patch the firmware to work around the clone test. Or get a legitimate firmware from whoever sold you the inverter, if they are still in business.
-
MPPT Patch for EAsun Inverter
74.01 has not been patched, but the more recent 74.04 has. Patched firmware version 374.04 implements only the lowered current threshold. I've come to doing the "full set" of patches for later patched firmwares. It's still the original perturb and observe algorithm, but there is a special test for low PV power that they get wrong, so it gets stuck at the low MPPT voltage limit. You can try the above, and if you don't like it, you can revert to the original factory firmware version 74.04, or I guess use the hex file you posted.
-
Axpert max 7200 issues
Please post the main (U1) firmware version for the other inverter. The 90.xx firmware versions are all over the place. Sadly, the 7.2 kW models are not very popular any more, so there's not a lot of work done for them now. Generally, the latest factory firmwares don't fix the "stuck at 90V" issue. However, 69.70 (from March 2024) has the "presumed good" algorithm, so that's as good as you will get with factory firmware. You could try patched firmware version 269.61, but that's based on even older firmware (November 2022).