  1. GM Pf, I have on many occasions found the Raspberry PI hanging.Result was a redo of he ICC image,update and reconfigure.I have lost count on the amount of times it has been done. I was considering using the Mecer tablet to the job. I bought a portable Adata battery bank to use this as a UPS only to find it won't charge and supply power at the same time. Are there any circuits or silver bullets out there I can put together use to have a shared 5v busbar to allow for continuity?I have also purchased a power cube from Builders with ac and 2 DC outputs. Thank you. FG
  2. Thank you @Fuenkli.I am going to show the circuit results when complete
  3. Gm PF, A circuit diagram is required for layout of your system.I have downloaded Designspark and Smartdraw on a trial. What are the good ones out there that don't cost any arm or a leg? Thanks.
  4. @Jaco de Jongh Thanks again for advice.I will display it once in operation.
  5. @plonkster@Jaco de Jongh Thank you for the valuable advice. Should I stay below the 520v mark to be safe? I have roof space and panels to add. These are my current levels.
  6. Model Solis-1P4.6K-4G Energy source PV Input Side Max.DC Power(kw) 5.3 Max.DC input voltage(V) 600 Start-up voltage(V) 120 MPPT voltage range(V) 90-520 Max.input current(A) 11+11 MPPT number/Max input strings number 2/2 I was under the impression that it was 600v per mppt. So .. my current west facing 270 x 5 = 1350 37.9 x 5 = 189.5 I want for west facing 270 x 6 = 1620 37.9 x 6 = 227.4 Proposed for west facing 270 x 7 = 1890 37.9 x 7 = 265 .3 Current east facing 330 x 6 = 1980 45.6 x 6 = 273.6 I want for east facing 330 x 7 = 2310 45.6 x 7 = 319.2 Proposed east facing 330 x 8 = 2640 45.6 x 8 = 364.8 Power is 1620 + 2310 = 3930 I get to voltage @ 319.2 + 227.4 = 546.6 (MPPT voltage range(V) 90-520) according to the spec sheet which is below the 600 DC mark or is that voltage to close? Or should I stick to six a side or 6/7 combo?
  7. How do you rate your SP's on the DC side? Is it for each strings voltage total sum or Inverters MPPT max voltage rating or expected/assumed max voltage induction from spikes ? On the AC side I can only assume a rating of say 380v and whatever induced voltage you would receive from Eskom or a lightning strike? I am only asking these questions as the "wizard" that installed my solar system never installed or mentioned anything of sort and I want to implement these necessary changes.
  8. Thanks @SilverNodashiI did split it . I bought another small one just for the DC breaker and its load(element) Thank you @GVC I have a few CB's I can still use in that db for lighter load circuits .
  9. flamegrilled posted a topic in Solar Power
    Hi PF, My load is both AC and DC.Can I share the DB? Iow have both AC and DC components on the same din rail to save costs and space? Thanks
  10. Hi Jaco, Could you not spot the issue with one of those Ellies red plugs with leds to indicate a lack of or a state of a circuit?Or even make up an extension with that plug in it to test the light circuits individually?
  11. The grid/inverter live/neutral separation is covered with this switch ? yes/no? https://www.acdc.co.za/products/4p-63a-din-changeover-switch?variant=30483376140 and the council wants this in place and the alias is a "Interlocked switch" ?
  12. Where would you suggest I send a faulty Axpert to for repair ? The local supplier RCT ? What other reputable electronics dealer repairs Voltronics Inverters? Thanks.
  13. I am trying to determine whether this avenue is an option to be "off grid "with the Axpert and the sign off will be a simple one. There be no grid connection and you will get a "grey day" battery charge from the generator whether a manual or electrical start/stop. You will still have a solar connection/daily charge option. The registration(form completion) of the generator connection is a must I see for COCT.
  14. Will do my homework.Thank you Plonkster.
  15. So if 600v DC is maximum for each MPPT, I should stay below (at 550v) for summer radiation when it's at its highest? So my thoughts would be using a solar tracker for arguments sake, you would also be in trouble and touch the 11A mark.
  16. Thank you Plonkster. If the panel rating is (Short Circuit Current (Isc): 9.45A) , would this be too close to the Inverters Max.input current(A)11+11 levels ?
  17. Input Side Max.DC Power(kw)5.3 Max.DC input voltage(V)600 (per string or in total) ? Start-up voltage(V)120 MPPT voltage range(V)100-500 (per string/per mppt) ? Max.input current(A)11+11 (in series that's the current panel current) ? MPPT number/Max input strings number2/2 Output side Rated output power(KW)4.6 Max. apparent output power(kVA) 5 (4.6 for VDE4105) Max. output power(kW) 5 (4.6 for VDE4105) Rated grid voltage(V)230 Grid voltage range(V)160-285 Rated grid frequency(Hz)50/60 Operating phaseSingle Rated grid output current(A)20 Max.AC output current(A) 23.8 (21.7 for AUS) What is the maximum input DC voltage per string for the device ?
  18. ESC463 I assume will be the standard on an offgrid/UPS connection. The assumption is that it will be the operation mode(normally open) when utility is UP/ON ? (Type of contacts: 4NO) Can I assume the inverter will energize the coil on the contactor disconnecting the Utility connection and will remain until Utility is restored. What will determine the restoration phase(Utility restored)?
  19. Am I correct by saying the GTI will always face the utility and the Axpert will get its source from the GTI supply to make things legal?
  20. Is it not as easy as putting a Grid tie inverter in front of it?
  21. @pilotfish are these inline fuses (MC4)at the end of the string connections and nothing at the PV isolator?
  22. Rufus Version 2.14.1086 is the one that worked eventually. Found lots of errors (250 were ism) on Kingston media (16gb). Ran a bad block check while installing the ICC image suspect a power outage when COCT where cutting trees in the area.
  23. It has been like this for a couple of weeks.I have done a rufus and another image.It worked for a day and I know this because mails do not arrive in my inbox. Any ideas Thanks
  24. On https://lime-technology.com/search/ They use the same engine. I can search for any three letter word or acronym and ...... they are on Tapatalk.
  25. I think this is related to DNS on the network connection(wifi) as the update software option does not list the previous updates for ICC either. My observation too.

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.