  1. Hi Cassie. You need to tick use timer on the stystem mode page to make use of the battery instead of the grid
  2. Hi Steve. That’s nothing. I have seen AC breakers used between batteries and inverters. I’m still not sure why one would use a breaker and a fuse as the way the fuse is designed is to act as a breaker as well. Obviously good practice dictates that there should never be current flowing when the fuses are opened or closed.
  3. There is no such setting on the inverter. I’m not sure why it’s on this app that you have.
  4. Can u send a pic of all the settings on the inverter.
  5. Limit to load will limit PV and battery power to essentials only.
  6. At this stage, it seems like the only 1C 6000cycle battery around
  7. Then you can get the SOLARMAN dongle. SOLARMAN is definitely not real time though
  8. I wish you were here when we were having this debate a while ago
  9. If it’s a new Sunsynk inverter then it comes with a Sunsynk dongle and that requires you to download the Sunsynk app. It’s quite clear in the user manual
  10. Just a couple. Less wiring and generator functionality
  11. It weighs 50kgs. Luckily it comes with a mounting bracket lol
  12. Another 16kw Sunsynk, 3 x 7kwh BSLs and 24 x 455w panels
  13. Seems like you don’t have the driver for the cable
  14. The issue is that you will still have 50 meters of PV cable going to the inverter via some some of PV combiner which will have DC SPDs and breakers/fuses etc. Lightning can still travel via the positive or negative cable and those SPDs in the PV combiner needs an earth input and that’s mostly taken from the main DB. I haven’t seen any installation where that earth is wired to a separate earth spike.
  15. Also people forget that there is only ONE earth. Some tend to talk about an AC vs DC earth. I think that before doing anything, there needs to be an understanding in why exactly it is done in a certain way.
  16. I have always earthed the PV array to the main earth of the home and have never had any issues. Still not sure what’s the fascination with earth spikes when there is already an earth in place.
  17. It’s either that or the Atess 50kw.
  18. You can set it to 0w. It won’t affect your meter.
  19. Hi David. The 6.5kva will work. Just know that the generator needs to supply the essential load as well as charge the battery so limit the charge current to the battery and you will be fine. Best to wire it into the AUX port
  20. Do you want to use the battery at night?
  21. The Metasole brackets from Renusol for IBR and Corrugated Iron works great
  22. 16kw Sunsynk paired with 4 x 7kwh BSL batteries and 24 x 455w panels. Changed from 3 to 1 phase, 80A main breakers and 16mm wiring.
×
×