Good Day All
I have a recently installed Mecer 5kva inverter with 3kva lithium battery.
I noticed a 60 error fault, did some research and realized the inverter and been setup up to run parallel.
Instead of contacting the supplier and listening to the little voice in my head.
I decided to Google and I located a thread, the thread mentioned changing setting 28 to SnG on the menu. I did not find that exact setting and used S1G, turned on power, heard a pop, smelt a burnt smell and the batter is also in alarm mode.
My question, will it be possible to repair the inverter? Or have I maybe damaged the battery. I'm not even sure what I did. Anyway your input and feedback is appreciated.
You need to provide more information than that.  What is the exact model number
"E60 Power Feedback Protection"
Changing a setting on the menus shouldn't damage the inverter.  However looking at @Coulomb post here:
It sounds like SnG mode disables the e60 protection.  So the grid fed straight into your inverter and blew it up.
Probably but you'll need to find someone that can actually fix it.  From what I've read, that can be a mission
It is possible, but try turning the battery off and on again.  If it still does it, then yes you probably fried some of the "battery" internals too (ie. went through the inverter into the battery)
If I had to guess, I would say you probably wired your inverter "output" to the grid power.  It had nothing to do with Parallel or not.  It just so happened that setting SnG just disabled the Inverter's protection against wiring your grid to output.
So in short, your wiring was/is wrong.  Did you install it yourself?
Edited by Gnome
Huh. I never noticed that I got that wrong. It's actually SIG (letter capital I, as opposed to numeral 1). I've edited the post and the FAQ.
I'm sorry to hear that. The fault code was trying to tell you something.
I agree with Gnome's guess. Can you confirm wiring utility to AC-out instead of AC-in?
Hi Guys
Thanks for the feedback. I have managed to book the unit in for repair. A few transistors were blown in the inverter. Definately disabled the protection with that setting change.
I had an eelctrician wire the unit for me, we definately had the AC input and AC output wired correctly. We are not using solar, so purely mains to recharge the battery for now.
I think the issue is after reading your advise, we have a seperate ciruit to power select plugs, but it is wired incorrectly. That circuit is getting AC from utility as well, which is causing the AC to travel up into the AC out of the inverter. I could be wrong but i will ask the electrician to check.
That would be greatly appreciated. Google delivers little in that area and the manual received with the unit, is very small and the size 8 font doesnt help matters.
I have one question, you mention a 50A breaker in both input and output AC paths. However, an inverter usually specifies the Amps that it can supply to those loads.
Its not 50A, mine is only 20A to backup loads (a few lights, plugs; when escom is down) but where it gets confusing is the "passthrough" current/A, where does that fit into the picture ?
Is the inverter able to "pass through" from grid to backup loads as well, hence the 50A or how does it work?
5 minutes ago, 87 Dream said:
It might be a SANS code requirement but I think it's reasonable to want such protection.
Yes , and also usefull when you need to remove/replace the inverter, or do some maintenance on it.  Life in the DB board must continue, ESKOM supply permitting🙂
☝️ Those are almost as old as me 🤣 Mine were of same vintage…..