Deye 5kW tripping essential load earth leakage

Featured Replies

Hallo,

My 5kW Deye keeps on tripping the essential loads earth leakage when connected to the grid. When grid is disconnected and running from battery everything is fine.

I am getting ac power from the main db after the main earth leakage. According to the wiring diagram in the manual there is not supposed to be a earh leakage. 

Don't have solar installed yet.

Thanks 

Ferdie

  • Author

Feedback: I did connect input to inverter before main earth leakage and I did disconnect the earth wire on the essential load of the inverter. 

Still tripping the earth leakage I installed in the new inverter db box. Not sure if it is the cheaper Major Tech trip switch? The other trip switch is almost three times more expensive. 

 

Thanks

28 minutes ago, Ferdie K said:

Feedback: I did connect input to inverter before main earth leakage and I did disconnect the earth wire on the essential load of the inverter. 

Still tripping the earth leakage I installed in the new inverter db box. Not sure if it is the cheaper Major Tech trip switch? The other trip switch is almost three times more expensive. 

 

Thanks

You have a shared neutral somewhere ,i had the same problem and it took me months to find it lol.

1 hour ago, Ferdie K said:

Shared neutral? Sorry for the dumb questions. Has basic knowledge. 

Thanks 

It helps if you read the Deye/SunSynk installation manual and understand the requirements in full prior to the installation.

Edited by PowerUser

2 hours ago, Ferdie K said:

Shared neutral? Sorry for the dumb questions. Has basic knowledge. 

Thanks 

It means somewhere in your house there is a neutral shared/connected between essential and non essential circuits.

17 hours ago, Ferdie K said:

Feedback: I did connect input to inverter before main earth leakage and I did disconnect the earth wire on the essential load of the inverter. 

Still tripping the earth leakage I installed in the new inverter db box. Not sure if it is the cheaper Major Tech trip switch? The other trip switch is almost three times more expensive. 

 

Thanks

I had the same issue. connected inverter before main earth leakage and replaced the earth leakage in the new db box with a good brand, CBi.

Do not disconnect the earth from the essential load. 

 

  • Author

Feedback: Took 4 hours to identify all neutral wires and rewire main db box with 2 neutral bars. One for essentials and one for non essentials. Install earth leakage again in inverter db box. Everything working 100%. Thanks to everyone fot your participation and knowledge to steer me in the right direction. Cheers.

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.