July 11, 20223 yr Hi all, I thought I would document my findings of the Tian Power BMS protocol used in my Narada 48NPFC100 battery whilst I was attempting to establish why it did not work with my Deye inverter. Of note is that the exact same battery model is known to use a Shinwa BMS as well, but mine uses a Tian Power one, specifically TP-ND1530. Firstly I wanted to thank @shanghailoz for documenting the same thing here for the Revov batteries, which also use a Tian Power BMS, without which I would have struggled a lot more. Also thank you @zivva for pointing me in the right direction for the BMS manufacturer. I also peeked at the code of the BMS software to decipher how certain fields are calculated. The protocol follows. Preamble Firstly, all data sent appears to have a header, body and CRC check. For example: 7e 01 01 00 fe 0d The first byte is either 7c or 7e according to the software. In my case it is always 7e. The second byte is the DIP switch setting on the battery and corresponds to the following in the software: The third byte is the function code, which you will see several examples of below, such as "read data", "read BMS time", "read BMS version", "read serial number". The fourth byte is the length of the payload supplied as part of the function call - most "read" type functions will not include a payload and this parameter will be 00, but the "write" functions would have a payload. If there is a payload, it would follow this byte. The last two bytes are the CRC check. The response is structured in a similar way: 7e 01 01 56 ... f2 0d The first three bytes are an echo of what the request was, the fourth byte indicates the response length followed by the response bytes, and finally we have the CRC check. Function 1 - Read data 7e 01 01 00 fe 0d This allows you to read almost everything that is displayed on the first tab of the BMS software. The response will look as follows: 7e 01 01 56 01 0f 0c e1 0c e2 0c e2 0c e3 0c e3 0c e5 0c e5 0c e4 0c e4 0c e4 0c e2 0c e2 0c e2 0c e3 0c e5 02 01 75 30 03 01 16 74 04 01 27 10 05 06 00 44 00 45 00 45 00 44 40 46 20 45 06 05 00 00 00 00 00 00 00 00 00 00 07 01 00 81 08 01 13 54 09 01 27 10 0a 01 00 00 f2 0d The response body for this function is a data map structured as follows: data entry index, number of high/low byte pairs, the high/low byte pairs. Data 1 - Cell count and cell voltages 01 0f 0c e1 0c e2 0c e2 0c e3 0c e3 0c e5 0c e5 0c e4 0c e4 0c e4 0c e2 0c e2 0c e2 0c e3 0c e5 The second byte is the number of cells - this is 15 for a 15 cell battery like mine or 16 cells for Revov. The individual cell voltages follow as high/low pairs which need to be divided by 1000, for example, 0ce1 maps to 3297 which means 3.297V. Since my battery has 15 cells, there would be 15 individual cell voltages. Data 2 - Current 02 01 75 30 This is a tricky one. 7530 hex maps to 30000 decimal. The BMS software works it out as: current_in_amps = (30000 - value_of_item_2) / 100 This item therefore has an offset of 30000 and a scaling factor of 0.01. So when the charge current is 0, the BMS will return 30000, therefore (30000 - 30000) / 100 = 0 amps. When the charge current is 10 amps, the BMS would return 29000, therefore (30000 - 29000) / 100 = 10 amps. When the charge current is -10 amps, the BMS would return 31000, therefore (30000 - 31000) / 100 = -10 amps. Furthermore, charge/discharge time remaining is calculated based on max battery capacity in amps divided by current in amps. Data 3 - Remaining capacity 03 01 16 74 This value needs to be divided by 100 to get Ah. In this case I have 1674 hex or 5748 decimal, so 57.48Ah left of my 100Ah battery, therefore the SOC is 57.48%. Data 4 - Full capacity 04 01 27 10 Divide by 100 to get full battery capacity in Ah. 2710 in hex is 10000 in decimal, so I have a 100Ah battery. Data 5 - Temperatures 05 06 00 44 00 45 00 45 00 44 40 46 20 45 In my case there are 6 temperatures corresponding to the following screenshot: In the Revovs the number of temperatures listed are different. The last two appear to be important ones. Each temperature value is calculated as: temp_value = (bms_temp_value & 0xFF) - 50 Data 6 - Alarm bits 06 05 00 00 00 00 00 00 00 00 00 00 These can be mapped to (a) very specific alarm code(s). I can get these if there is interest. Data 7 - Cycles 07 01 00 81 This represents the number of cycles of the battery, so 129 in my case. Data 8 - Voltage 08 01 13 54 The total voltage of the battery. The number needs to be divided by 100, so 49.48V in my case. Data 9 - State of Health 09 01 27 10 The SOH of the battery. Needs to be divided by 100, so 100% in my case. Data 10 - ALM bytes 0a 01 00 00 This corresponds to the ALM light on the battery and what it means. Function 67 - Read protection parameters Request: 7e 01 43 00 fe 0d Response: 7e 01 43 94 00 02 0e 10 01 02 03 e8 02 02 0d ac 03 02 0a f0 04 02 03 e8 05 02 0c 1c 06 02 15 4a 07 02 03 e8 08 02 14 c8 09 02 11 94 0a 02 03 e8 0b 02 13 88 0c 02 1f 40 0d 02 03 e8 0e 02 1b 58 0f 02 1f 40 10 02 03 e8 11 02 1b 58 12 02 00 69 13 02 0f a0 14 02 00 5f 15 02 00 32 16 02 0f a0 17 02 00 3c 18 02 00 69 19 02 0f a0 1a 02 00 5f 1b 02 00 32 1c 02 0f a0 1d 02 00 3c 1e 02 00 8c 1f 02 0f a0 20 02 00 87 21 02 00 0a 22 02 00 0f 23 02 03 20 24 02 01 f4 de 0d This is another data map which ultimately gets translated into the following, with the necessary scaling factors applied: { "cell_ov_start": 3.6, "cell_ov_delay": 1000, "cell_ov_stop": 3.5, "cell_uv_start": 2.8, "cell_uv_delay": 1000, "cell_uv_stop": 3.1, "pack_ov_start": 54.5, "pack_ov_delay": 1000, "pack_ov_stop": 53.2, "pack_uv_start": 45.0, "pack_uv_delay": 1000, "pack_uv_stop": 50.0, "charge_oc_start": 80.0, "charge_oc_delay": 1000, "charge_oc_stop": 70.0, "discharge_oc_start": 80.0, "discharge_oc_delay": 1000, "discharge_oc_stop": 70.0, "cell_ot_start": 55, "cell_ot_delay": 4000, "cell_ot_stop": 45, "cell_ut_start": 0, "cell_ut_delay": 4000, "cell_ut_stop": 10, "env_ot_start": 55, "env_ot_delay": 4000, "env_ot_stop": 45, "env_ut_start": 0, "env_ut_delay": 4000, "env_ut_stop": 10, "mos_ot_start": 90, "mos_ot_delay": 4000, "mos_ot_stop": 85, "capacity_low_start": 10, "capacity_low_stop": 15, "volt_diff_start": 800, "volt_diff_stop": 500 } Function 51 - Read BMS version The request is as follows: 7e 01 33 00 fe 0d The response body is a string, such as: 7e 01 33 18 54 50 2d 4e 44 31 35 33 30 2d 31 35 53 31 30 30 41 2d 56 31 2e 30 2e 30 2e 0d Which in my case maps to: TP-ND1530-15S100A-V1.0.0 Function 66 - Read PCB barcode Request: 7e 01 42 00 fc 0d Response body is a string as above. Function 220 - Read serial number Request: 7e 01 dc 03 06 00 00 c2 0d Response body is a string as above. Function 69 - Read BMS time Request: 7e 01 45 00 fe 0d Response: 7e 01 45 06 16 07 08 14 3b 16 48 0d To convert the above to a valid date time, prepend "20" and then concatenate the rest of the bytes which represent yy, MM, dd, hh, mm, ss, so in the above example: 2022-07-08 20:59:22. There are many "write"-type functions too but I would be wary of using those. I hope the above is useful to someone. I will post more useful ones if I find any. Edited September 13, 20223 yr by SolarConvert Clarified charge current and temperatures, added protection data
August 17, 20223 yr Nicely done. I should revisit some of the values on mine, see if i can map more fields to actual values.
August 19, 20223 yr Author Thanks @shanghailoz One command that the Deye inverter does issue is the following, but I have yet to decipher what this one does. Command: 7e 01 43 00 fe 0d Response: 7e 01 43 94 00 02 0e 10 01 02 03 e8 02 02 0d ac 03 02 0a f0 04 02 03 e8 05 02 0c 1c 06 02 15 4a 07 02 03 e8 08 02 14 c8 09 02 11 94 0a 02 03 e8 0b 02 13 88 0c 02 1f 40 0d 02 03 e8 0e 02 1b 58 0f 02 1f 40 10 02 03 e8 11 02 1b 58 12 02 00 69 13 02 0f a0 14 02 00 5f 15 02 00 32 16 02 0f a0 17 02 00 3c 18 02 00 69 19 02 0f a0 1a 02 00 5f 1b 02 00 32 1c 02 0f a0 1d 02 00 3c 1e 02 00 8c 1f 02 0f a0 20 02 00 87 21 02 00 0a 22 02 00 0f 23 02 03 20 24 02 01 f4 de 0d I can see the data map but do not yet know what each item means. Reformatted: 7e 01 43 94 00 02 0e 10 01 02 03 e8 02 02 0d ac 03 02 0a f0 04 02 03 e8 05 02 0c 1c 06 02 15 4a 07 02 03 e8 08 02 14 c8 09 02 11 94 0a 02 03 e8 0b 02 13 88 0c 02 1f 40 0d 02 03 e8 0e 02 1b 58 0f 02 1f 40 10 02 03 e8 11 02 1b 58 12 02 00 69 13 02 0f a0 14 02 00 5f 15 02 00 32 16 02 0f a0 17 02 00 3c 18 02 00 69 19 02 0f a0 1a 02 00 5f 1b 02 00 32 1c 02 0f a0 1d 02 00 3c 1e 02 00 8c 1f 02 0f a0 20 02 00 87 21 02 00 0a 22 02 00 0f 23 02 03 20 24 02 01 f4 de 0d Since this is the first call that the inverter makes to the BMS, these must be the parameters that the inverter expects back from the BMS. When I have time I will try to dig deeper, just posting it here for now.
September 12, 20223 yr Hey, can you please elaborate on that current calculation with an example .. its not making sense to me ? I assume this could be negative (discharging) or positive (charging) ? But I cant follow your logic ? Thx
September 13, 20223 yr Author So to get the current in amps, you need the following formula Current = (30000 - value_of_item_2) / 100 30000 is a static value from which you need to subtract the value of item 2 returned by the BMS. I assume that Tian Power did this so that only unsigned values are returned by the BMS when queried, therefore some items not only have a scaling factor but also an offset to subtract from, if that makes sense? I'll update the first post with the latest info I have - there is a lot of new info.
September 13, 20223 yr Author On 2022/08/19 at 3:43 PM, SolarConvert said: One command that the Deye inverter does issue is the following, but I have yet to decipher what this one does. Command: 7e 01 43 00 fe 0d I have managed to decode the response and have amended my first post to include BMS protection data.
September 13, 20223 yr 3 hours ago, SolarConvert said: So to get the current in amps, you need the following formula Current = (30000 - value_of_item_2) / 100 30000 is a static value from which you need to subtract the value of item 2 returned by the BMS. I assume that Tian Power did this so that only unsigned values are returned by the BMS when queried, therefore some items not only have a scaling factor but also an offset to subtract from, if that makes sense? I'll update the first post with the latest info I have - there is a lot of new info. Awesome, got it now .. thx
December 20, 20223 yr I am trying to send command 7e 01 01 00 fe 0d to BMS in c+ programming language. But all that sin received was silence. I have reached the end. Hope to get help from you
January 25, 20233 yr On 2022/07/12 at 3:08 AM, SolarConvert said: Hi all, I thought I would document my findings of the Tian Power BMS protocol used in my Narada 48NPFC100 battery whilst I was attempting to establish why it did not work with my Deye inverter. Of note is that the exact same battery model is known to use a Shinwa BMS as well, but mine uses a Tian Power one, specifically TP-ND1530. Firstly I wanted to thank @shanghailoz for documenting the same thing here for the Revov batteries, which also use a Tian Power BMS, without which I would have struggled a lot more. Also thank you @zivva for pointing me in the right direction for the BMS manufacturer. I also peeked at the code of the BMS software to decipher how certain fields are calculated. The protocol follows. Preamble Firstly, all data sent appears to have a header, body and CRC check. For example: 7e 01 01 00 fe 0d The first byte is either 7c or 7e according to the software. In my case it is always 7e. The second byte is the DIP switch setting on the battery and corresponds to the following in the software: The third byte is the function code, which you will see several examples of below, such as "read data", "read BMS time", "read BMS version", "read serial number". The fourth byte is the length of the payload supplied as part of the function call - most "read" type functions will not include a payload and this parameter will be 00, but the "write" functions would have a payload. If there is a payload, it would follow this byte. The last two bytes are the CRC check. The response is structured in a similar way: 7e 01 01 56 ... f2 0d The first three bytes are an echo of what the request was, the fourth byte indicates the response length followed by the response bytes, and finally we have the CRC check. Function 1 - Read data 7e 01 01 00 fe 0d This allows you to read almost everything that is displayed on the first tab of the BMS software. The response will look as follows: 7e 01 01 56 01 0f 0c e1 0c e2 0c e2 0c e3 0c e3 0c e5 0c e5 0c e4 0c e4 0c e4 0c e2 0c e2 0c e2 0c e3 0c e5 02 01 75 30 03 01 16 74 04 01 27 10 05 06 00 44 00 45 00 45 00 44 40 46 20 45 06 05 00 00 00 00 00 00 00 00 00 00 07 01 00 81 08 01 13 54 09 01 27 10 0a 01 00 00 f2 0d The response body for this function is a data map structured as follows: data entry index, number of high/low byte pairs, the high/low byte pairs. Data 1 - Cell count and cell voltages 01 0f 0c e1 0c e2 0c e2 0c e3 0c e3 0c e5 0c e5 0c e4 0c e4 0c e4 0c e2 0c e2 0c e2 0c e3 0c e5 The second byte is the number of cells - this is 15 for a 15 cell battery like mine or 16 cells for Revov. The individual cell voltages follow as high/low pairs which need to be divided by 1000, for example, 0ce1 maps to 3297 which means 3.297V. Since my battery has 15 cells, there would be 15 individual cell voltages. Data 2 - Current 02 01 75 30 This is a tricky one. 7530 hex maps to 30000 decimal. The BMS software works it out as: current_in_amps = (30000 - value_of_item_2) / 100 This item therefore has an offset of 30000 and a scaling factor of 0.01. So when the charge current is 0, the BMS will return 30000, therefore (30000 - 30000) / 100 = 0 amps. When the charge current is 10 amps, the BMS would return 29000, therefore (30000 - 29000) / 100 = 10 amps. When the charge current is -10 amps, the BMS would return 31000, therefore (30000 - 31000) / 100 = -10 amps. Furthermore, charge/discharge time remaining is calculated based on max battery capacity in amps divided by current in amps. Data 3 - Remaining capacity 03 01 16 74 This value needs to be divided by 100 to get Ah. In this case I have 1674 hex or 5748 decimal, so 57.48Ah left of my 100Ah battery, therefore the SOC is 57.48%. Data 4 - Full capacity 04 01 27 10 Divide by 100 to get full battery capacity in Ah. 2710 in hex is 10000 in decimal, so I have a 100Ah battery. Data 5 - Temperatures 05 06 00 44 00 45 00 45 00 44 40 46 20 45 In my case there are 6 temperatures corresponding to the following screenshot: In the Revovs the number of temperatures listed are different. The last two appear to be important ones. Each temperature value is calculated as: temp_value = (bms_temp_value & 0xFF) - 50 Data 6 - Alarm bits 06 05 00 00 00 00 00 00 00 00 00 00 These can be mapped to (a) very specific alarm code(s). I can get these if there is interest. Data 7 - Cycles 07 01 00 81 This represents the number of cycles of the battery, so 129 in my case. Data 8 - Voltage 08 01 13 54 The total voltage of the battery. The number needs to be divided by 100, so 49.48V in my case. Data 9 - State of Health 09 01 27 10 The SOH of the battery. Needs to be divided by 100, so 100% in my case. Data 10 - ALM bytes 0a 01 00 00 This corresponds to the ALM light on the battery and what it means. Function 67 - Read protection parameters Request: 7e 01 43 00 fe 0d Response: 7e 01 43 94 00 02 0e 10 01 02 03 e8 02 02 0d ac 03 02 0a f0 04 02 03 e8 05 02 0c 1c 06 02 15 4a 07 02 03 e8 08 02 14 c8 09 02 11 94 0a 02 03 e8 0b 02 13 88 0c 02 1f 40 0d 02 03 e8 0e 02 1b 58 0f 02 1f 40 10 02 03 e8 11 02 1b 58 12 02 00 69 13 02 0f a0 14 02 00 5f 15 02 00 32 16 02 0f a0 17 02 00 3c 18 02 00 69 19 02 0f a0 1a 02 00 5f 1b 02 00 32 1c 02 0f a0 1d 02 00 3c 1e 02 00 8c 1f 02 0f a0 20 02 00 87 21 02 00 0a 22 02 00 0f 23 02 03 20 24 02 01 f4 de 0d This is another data map which ultimately gets translated into the following, with the necessary scaling factors applied: { "cell_ov_start": 3.6, "cell_ov_delay": 1000, "cell_ov_stop": 3.5, "cell_uv_start": 2.8, "cell_uv_delay": 1000, "cell_uv_stop": 3.1, "pack_ov_start": 54.5, "pack_ov_delay": 1000, "pack_ov_stop": 53.2, "pack_uv_start": 45.0, "pack_uv_delay": 1000, "pack_uv_stop": 50.0, "charge_oc_start": 80.0, "charge_oc_delay": 1000, "charge_oc_stop": 70.0, "discharge_oc_start": 80.0, "discharge_oc_delay": 1000, "discharge_oc_stop": 70.0, "cell_ot_start": 55, "cell_ot_delay": 4000, "cell_ot_stop": 45, "cell_ut_start": 0, "cell_ut_delay": 4000, "cell_ut_stop": 10, "env_ot_start": 55, "env_ot_delay": 4000, "env_ot_stop": 45, "env_ut_start": 0, "env_ut_delay": 4000, "env_ut_stop": 10, "mos_ot_start": 90, "mos_ot_delay": 4000, "mos_ot_stop": 85, "capacity_low_start": 10, "capacity_low_stop": 15, "volt_diff_start": 800, "volt_diff_stop": 500 } Function 51 - Read BMS version The request is as follows: 7e 01 33 00 fe 0d The response body is a string, such as: 7e 01 33 18 54 50 2d 4e 44 31 35 33 30 2d 31 35 53 31 30 30 41 2d 56 31 2e 30 2e 30 2e 0d Which in my case maps to: TP-ND1530-15S100A-V1.0.0 Function 66 - Read PCB barcode Request: 7e 01 42 00 fc 0d Response body is a string as above. Function 220 - Read serial number Request: 7e 01 dc 03 06 00 00 c2 0d Response body is a string as above. Function 69 - Read BMS time Request: 7e 01 45 00 fe 0d Response: 7e 01 45 06 16 07 08 14 3b 16 48 0d To convert the above to a valid date time, prepend "20" and then concatenate the rest of the bytes which represent yy, MM, dd, hh, mm, ss, so in the above example: 2022-07-08 20:59:22. There are many "write"-type functions too but I would be wary of using those. I hope the above is useful to someone. I will post more useful ones if I find any. I want Alarm code message. from Alarm code byte and Alarm bit. thank you
March 18, 20233 yr Thanks so much for this post @SolarConvert – this was key in getting prometheus hooked up to my system. Have you (or anybody else here) been able to reverse engineer the CRC or checksum algorithm? I've spent hours on this and have been totally defeated. Right now I have a hardcoded map of requests I care about for each battery address, which I just copied from the software... but it's a very dirty way to go about things.
November 14, 20241 yr public static byte[] gabyCRCHi = new byte[256] { 0, 193, 129, 64, 1, 192, 128, 65, 1, 192, 128, 65, 0, 193, 129, 64, 1, 192, 128, 65, 0, 193, 129, 64, 0, 193, 129, 64, 1, 192, 128, 65, 1, 192, 128, 65, 0, 193, 129, 64, 0, 193, 129, 64, 1, 192, 128, 65, 0, 193, 129, 64, 1, 192, 128, 65, 1, 192, 128, 65, 0, 193, 129, 64, 1, 192, 128, 65, 0, 193, 129, 64, 0, 193, 129, 64, 1, 192, 128, 65, 0, 193, 129, 64, 1, 192, 128, 65, 1, 192, 128, 65, 0, 193, 129, 64, 0, 193, 129, 64, 1, 192, 128, 65, 1, 192, 128, 65, 0, 193, 129, 64, 1, 192, 128, 65, 0, 193, 129, 64, 0, 193, 129, 64, 1, 192, 128, 65, 1, 192, 128, 65, 0, 193, 129, 64, 0, 193, 129, 64, 1, 192, 128, 65, 0, 193, 129, 64, 1, 192, 128, 65, 1, 192, 128, 65, 0, 193, 129, 64, 0, 193, 129, 64, 1, 192, 128, 65, 1, 192, 128, 65, 0, 193, 129, 64, 1, 192, 128, 65, 0, 193, 129, 64, 0, 193, 129, 64, 1, 192, 128, 65, 0, 193, 129, 64, 1, 192, 128, 65, 1, 192, 128, 65, 0, 193, 129, 64, 1, 192, 128, 65, 0, 193, 129, 64, 0, 193, 129, 64, 1, 192, 128, 65, 1, 192, 128, 65, 0, 193, 129, 64, 0, 193, 129, 64, 1, 192, 128, 65, 0, 193, 129, 64, 1, 192, 128, 65, 1, 192, 128, 65, 0, 193, 129, 64 }; public static byte[] gabyCRCLo = new byte[256] { 0, 192, 193, 1, 195, 3, 2, 194, 198, 6, 7, 199, 5, 197, 196, 4, 204, 12, 13, 205, 15, 207, 206, 14, 10, 202, 203, 11, 201, 9, 8, 200, 216, 24, 25, 217, 27, 219, 218, 26, 30, 222, 223, 31, 221, 29, 28, 220, 20, 212, 213, 21, 215, 23, 22, 214, 210, 18, 19, 211, 17, 209, 208, 16, 240, 48, 49, 241, 51, 243, 242, 50, 54, 246, 247, 55, 245, 53, 52, 244, 60, 252, 253, 61, 255, 63, 62, 254, 250, 58, 59, 251, 57, 249, 248, 56, 40, 232, 233, 41, 235, 43, 42, 234, 238, 46, 47, 239, 45, 237, 236, 44, 228, 36, 37, 229, 39, 231, 230, 38, 34, 226, 227, 35, 225, 33, 32, 224, 160, 96, 97, 161, 99, 163, 162, 98, 102, 166, 167, 103, 165, 101, 100, 164, 108, 172, 173, 109, 175, 111, 110, 174, 170, 106, 107, 171, 105, 169, 168, 104, 120, 184, 185, 121, 187, 123, 122, 186, 190, 126, 127, 191, 125, 189, 188, 124, 180, 116, 117, 181, 119, 183, 182, 118, 114, 178, 179, 115, 177, 113, 112, 176, 80, 144, 145, 81, 147, 83, 82, 146, 150, 86, 87, 151, 85, 149, 148, 84, 156, 92, 93, 157, 95, 159, 158, 94, 90, 154, 155, 91, 153, 89, 88, 152, 136, 72, 73, 137, 75, 139, 138, 74, 78, 142, 143, 79, 141, 77, 76, 140, 68, 132, 133, 69, 135, 71, 70, 134, 130, 66, 67, 131, 65, 129, 128, 64 }; private byte check(byte[] buf, byte len) { byte b = 0; byte b2 = 0; int num = 0; for (b = 0; b < len; b++) { b2 ^= buf[b]; num += buf[b]; } return (byte)((uint)(b2 ^ num) & 0xFFu); } private ushort checkcrc(byte[] buf, int len) { byte b = byte.MaxValue; byte b2 = byte.MaxValue; for (int num = len; num > 0; num--) { byte b3 = (byte)(b ^ buf[len - num]); b = (byte)(b2 ^ gabyCRCHi[b3]); b2 = gabyCRCLo[b3]; } ushort num2 = b; num2 <<= 8; return (ushort)(num2 + b2); }
November 14, 20241 yr Delphi function TShotoBMS.CheckCRC(Buf: PByteArray; Len: Integer): Word; var b, b2, b3: Byte; num2: Word; i: Integer; begin b := $FF; b2 := $FF; for i := Len downto 1 do begin b3 := b xor Buf[Len - i]; b := b2 xor gabyCRCHi[b3]; b2 := gabyCRCLo[b3]; end; num2 := b; num2 := num2 shl 8; Result := num2 + b2; end; function TShotoBMS.Check(Buf: PByteArray; Len: Byte): Byte; var b, b2: Byte; num: Integer; begin b2 := 0; num := 0; for b := 0 to Len - 1 do begin b2 := b2 xor Buf^[b]; num := num + Buf^[b]; end; Result := Byte((b2 xor num) and $FF); end;
January 22, 20251 yr Has anybody managed to find out how CRC is calculated here? Keep in mind that the last two algorithms posted by@Diego Carrilho are not for this particular protocol, CRC here is only 1 byte, which is located before 0D Function 0x01 Read Data Start of the message always starts with 7C DIP switch setting* Function CRC-check End of the message Reply 7C 00 01 00 00 0D 7C00017401100CFB0CF90CFB0CFA0CFA0CFA0CFA0CFA0CFA0CFA0CFB0CFB0CFA0CFA0CFA0CFB020175300301233F0401298705060048004800480048404B2049060600000000000000000000000007010001080114C3090127100A0100000B020000006F1002000015FF0C02000000001101150C1201404BEE0D 7C 01 01 00 02 0D 7C 01 01 74 01 10 0D 01 0C FF 0D 01 0D 00 0D 00 0D 00 0D 01 0D 01 0D 00 0D 00 0D 01 0D 00 0D 01 0D 00 0D 01 0D 02 02 01 75 30 03 01 24 19 04 01 29 87 05 06 00 47 00 47 00 47 00 47 40 49 20 48 06 06 00 00 00 00 00 00 00 00 00 00 00 00 07 01 00 01 08 01 14 CD 09 01 27 10 0A 01 00 00 0B 02 00 00 00 6F 10 02 00 00 15 FF 0C 02 00 00 00 00 11 01 15 17 12 01 40 49 4A 0D 7C 02 01 00 00 0D 7C02017401100CFB0CF90CFB0CF90CFA0CFA0CFA0CFA0CFA0CFA0CFB0CFB0CFA0CFA0CFA0CFB020175300301233F0401298705060048004800480048404A2049060600000000000000000000000007010001080114C3090127100A0100000B020000006F1002000015FF0C02000000001101150C1201404AEC0D 7C 03 01 00 FE 0D 7C03017401100CFB0CF90CFA0CFA0CFA0CFA0CFA0CFA0CFA0CF90CFB0CFB0CFA0CF90CFA0CFB02017530030123310401298705060048004800480048404A2049060600000000000000000000000007010001080114C3090127100A0100000B020000006F1002000015FF0C02000000001101150C1201404A120D 7C 04 01 00 F8 0D 7C04017401100CFB0CF90CFA0CFA0CFA0CFA0CFA0CFA0CFA0CFA0CFB0CFA0CFA0CFA0CFA0CFB02017530030123300401298705060048004800480048404A2049060600000000000000000000000007010001080114C3090127100A0100000B020000006F1002000015FF0C02000000001101150C1201404A140D 7C 05 01 00 FA 0D 7C05017401100CFB0CF90CFA0CFA0CFA0CFA0CFA0CF90CFA0CF90CFB0CFA0CFA0CFA0CFA0CFB02017530030123300401298705060048004800480048404A2049060600000000000000000000000007010001080114C3090127100A0100000B020000006F1002000015FF0C02000000001101150A1201404A100D Function 0x06 Start of the message always starts with 7C DIP switch setting* Function CRC-check End of the message Reply 7C 00 06 00 00 0D 7C00060400000F0AE40D 7C 01 06 00 02 0D 7C01060400000EA6EC0D 7C 02 06 00 FC 0D 7C02060400000F0AD80D 7C 03 06 00 FC 0D 7C03060400000F0ADA0D 7C 04 06 00 F8 0D 7C04060400000F0ADC0D 7C 05 06 00 F8 0D 7C05060400000F0ADA0D Can you help me?
January 22, 20251 yr 1 hour ago, Kaveh said: Has anybody managed to find out how CRC is calculated here? Keep in mind that the last two algorithms posted by@Diego Carrilho are not for this particular protocol, CRC here is only 1 byte, which is located before 0D Function 0x01 Read Data Start of the message always starts with 7C DIP switch setting* Function CRC-check End of the message Reply 7C 00 01 00 00 0D 7C00017401100CFB0CF90CFB0CFA0CFA0CFA0CFA0CFA0CFA0CFA0CFB0CFB0CFA0CFA0CFA0CFB020175300301233F0401298705060048004800480048404B2049060600000000000000000000000007010001080114C3090127100A0100000B020000006F1002000015FF0C02000000001101150C1201404BEE0D 7C 01 01 00 02 0D 7C 01 01 74 01 10 0D 01 0C FF 0D 01 0D 00 0D 00 0D 00 0D 01 0D 01 0D 00 0D 00 0D 01 0D 00 0D 01 0D 00 0D 01 0D 02 02 01 75 30 03 01 24 19 04 01 29 87 05 06 00 47 00 47 00 47 00 47 40 49 20 48 06 06 00 00 00 00 00 00 00 00 00 00 00 00 07 01 00 01 08 01 14 CD 09 01 27 10 0A 01 00 00 0B 02 00 00 00 6F 10 02 00 00 15 FF 0C 02 00 00 00 00 11 01 15 17 12 01 40 49 4A 0D 7C 02 01 00 00 0D 7C02017401100CFB0CF90CFB0CF90CFA0CFA0CFA0CFA0CFA0CFA0CFB0CFB0CFA0CFA0CFA0CFB020175300301233F0401298705060048004800480048404A2049060600000000000000000000000007010001080114C3090127100A0100000B020000006F1002000015FF0C02000000001101150C1201404AEC0D 7C 03 01 00 FE 0D 7C03017401100CFB0CF90CFA0CFA0CFA0CFA0CFA0CFA0CFA0CF90CFB0CFB0CFA0CF90CFA0CFB02017530030123310401298705060048004800480048404A2049060600000000000000000000000007010001080114C3090127100A0100000B020000006F1002000015FF0C02000000001101150C1201404A120D 7C 04 01 00 F8 0D 7C04017401100CFB0CF90CFA0CFA0CFA0CFA0CFA0CFA0CFA0CFA0CFB0CFA0CFA0CFA0CFA0CFB02017530030123300401298705060048004800480048404A2049060600000000000000000000000007010001080114C3090127100A0100000B020000006F1002000015FF0C02000000001101150C1201404A140D 7C 05 01 00 FA 0D 7C05017401100CFB0CF90CFA0CFA0CFA0CFA0CFA0CF90CFA0CF90CFB0CFA0CFA0CFA0CFA0CFB02017530030123300401298705060048004800480048404A2049060600000000000000000000000007010001080114C3090127100A0100000B020000006F1002000015FF0C02000000001101150A1201404A100D Function 0x06 Start of the message always starts with 7C DIP switch setting* Function CRC-check End of the message Reply 7C 00 06 00 00 0D 7C00060400000F0AE40D 7C 01 06 00 02 0D 7C01060400000EA6EC0D 7C 02 06 00 FC 0D 7C02060400000F0AD80D 7C 03 06 00 FC 0D 7C03060400000F0ADA0D 7C 04 06 00 F8 0D 7C04060400000F0ADC0D 7C 05 06 00 F8 0D 7C05060400000F0ADA0D Can you help me? for sending data , you shift all the bytes thru the checksum below starting from the first 0x7C/0x7E character to the end of payload. You then append the checksum byte as well as an 0x0D character. uint8_t nerada_485_checksum(uint8_t *buf, uint8_t len) { uint8_t b = 0; uint8_t b2 = 0; int num = 0; for (b = 0; b < len; b++) { b2 ^= buf[b]; num += buf[b]; } return (uint8_t)((uint)(b2 ^ num) & 0xFFu); } When receiving data , you shift all the bytes thru the checksum starting at the first character up to and excluding the checksum byte and the 0x0D character. You then compare your calculated checksum against the received check sum , and also check that the last character is indeed 0x0D.
January 22, 20251 yr I have a question regarding the Nerada protocol . Does anyone know the alarm bit details as supplied in subcommand 6 and subcommand 10 of main main command 1 ( read analogue data) ?
January 22, 20251 yr 5 hours ago, BritishRacingGreen said: for sending data , you shift all the bytes thru the checksum below starting from the first 0x7C/0x7E character to the end of payload. You then append the checksum byte as well as an 0x0D character. uint8_t nerada_485_checksum(uint8_t *buf, uint8_t len) { uint8_t b = 0; uint8_t b2 = 0; int num = 0; for (b = 0; b < len; b++) { b2 ^= buf[b]; num += buf[b]; } return (uint8_t)((uint)(b2 ^ num) & 0xFFu); } When receiving data , you shift all the bytes thru the checksum starting at the first character up to and excluding the checksum byte and the 0x0D character. You then compare your calculated checksum against the received check sum , and also check that the last character is indeed 0x0D. Thank you for providing this, its been a while I am thinking about this!
January 22, 20251 yr 5 hours ago, BritishRacingGreen said: I have a question regarding the Nerada protocol . Does anyone know the alarm bit details as supplied in subcommand 6 and subcommand 10 of main main command 1 ( read analogue data) ? Not sure what command are you talking about, can you explain a bit more?
January 22, 20251 yr On 2022/07/11 at 10:08 PM, SolarConvert said: Function 67 - Read protection parameters by the way, this command is worng, 0x43 is to read alarm Params, not protection parameters
January 23, 20251 yr On 2025/01/22 at 10:11 AM, BritishRacingGreen said: I have a question regarding the Nerada protocol . Does anyone know the alarm bit details as supplied in subcommand 6 and subcommand 10 of main main command 1 ( read analogue data) ? Now I got what you mean, here is what you see more in detail I do not have an answer to your question! 7C 02 01 74 01 10 0CFA 0CF8 0CFA 0CF9 0CF9 0CF9 0CFA 0CF9 0CF9 0CF9 0CFA 0CFA 0CF9 0CF9 0CF9 0CFB 02 01 7530 03 01 22E5 04 01 2987 05 06 0048 0048 0048 0048 404A 2049 06 06 0000 0000 0000 0000 0000 0000 07 01 0001 08 01 14C2 09 01 2710 0A 01 0000 0B 02 0000 006F 10 02 0000 15FF 0C 02 0000 0000 11 01 150C 12 01 404A 9E 0D 7C 01 01 74 01 10 0CF9 0CF8 0CFA 0CFA 0CFA 0CFA 0CFA 0CFA 0CF9 0CFA 0CFA 0CFA 0CFA 0CF9 0CF9 0CFA 02 01 7530 03 01 2383 04 01 299F 05 06 0047 0047 0047 0047 404A 2048 06 06 0000 0000 0000 0000 0000 0000 07 01 0001 08 01 14C2 09 01 2710 0A 01 0000 0B 02 0000 006E 10 02 0000 15CC 0C 02 0000 0000 11 01 14D3 12 01 404A 4A 0D Does anybody know why the order of these data are like this? particularly after 0B, I would expect 0C, but there is 10, 0B 10 0C 11 12 Edited January 23, 20251 yr by Kaveh
April 15, 20251 yr Hi, thank you so much for the effort of getting this info. I have written a small c# prpgram to decode the data. I am going to put a small panel on my wall to display all of my betteries'parameters. I did start this because i have one battery that come up with a non serious error all the time and i needed to find out where the problem is. So far all the data looks good , but i would like to try and find out what the error is. Can you still get hold of the data for the specific bits ?