Solar Panel Cable Size


Recommended Posts

Hallo!

So, according to Wiring Unlimited from Victron (https://www.victronenergy.com/upload/documents/The_Wiring_Unlimited_book/43562-Wiring_Unlimited-pdf-en.pdf), if I have a 30Amp PWM and I want to add panels, I need to have a 35mm2 cable when I have 15meters:

image.thumb.png.7d7c0454c8eeeb1eb3542901f6962b31.png

 

But in the same manual, they say Solar Cable is 4mm2 or 6mm2.

The MC4 connecters looks like 4mm2 as well?

So how do I size my cable when I am pulling 30amps over +- 30meters?

 

Link to comment
Share on other sites

On 2023/06/07 at 2:08 PM, McGuywer said:

Hallo!

So, according to Wiring Unlimited from Victron (https://www.victronenergy.com/upload/documents/The_Wiring_Unlimited_book/43562-Wiring_Unlimited-pdf-en.pdf), if I have a 30Amp PWM and I want to add panels, I need to have a 35mm2 cable when I have 15meters:

image.thumb.png.7d7c0454c8eeeb1eb3542901f6962b31.png

 

But in the same manual, they say Solar Cable is 4mm2 or 6mm2.

The MC4 connecters looks like 4mm2 as well?

So how do I size my cable when I am pulling 30amps over +- 30meters?

 

Have your combiner close to the charge controller. Then only use 6mm cable once strings are combined. 

Link to comment
Share on other sites

On 2023/06/07 at 2:08 PM, McGuywer said:

Hallo!

So, according to Wiring Unlimited from Victron (https://www.victronenergy.com/upload/documents/The_Wiring_Unlimited_book/43562-Wiring_Unlimited-pdf-en.pdf), if I have a 30Amp PWM and I want to add panels, I need to have a 35mm2 cable when I have 15meters:

image.thumb.png.7d7c0454c8eeeb1eb3542901f6962b31.png

 

But in the same manual, they say Solar Cable is 4mm2 or 6mm2.

The MC4 connecters looks like 4mm2 as well?

So how do I size my cable when I am pulling 30amps over +- 30meters?

 

This table is for the cable between your battery and inverter and battery fuse. I prefer to spend the couple of R extra to get thicker battery cable due to less losses. The losses will still be there, long after the R150 saved was spent on something else.

I used 6mm² pv cable, even when the string only deliver about 11A max at 220v DC. 

Edited by Vaal
Link to comment
Share on other sites

I used 10mm cable when 12 panels were wired in 6 groups of 2 in series.  The current flow from the panels in full sunshine could be 60 amps.   The owner was using a Solar Charge controller with a low maximum PV voltage input

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...