June 9, 20233 yr I'm in the process of completing my sseg application and looking for assistance from those who has done this before. Please see my attached diagram as i see that it is a requirement. Please advise if it is correct or am i missing anything. My applicaton will be for OFF-GRID (separated and not interconnected with electrical installation). Your help will be appreciated.
June 9, 20233 yr Off-Grid means you not connecting to GRID at all , no changeover needed and no Incoming COCT Your drawing is showing STANDBY SSEG with Grid support Here is an example of the line drawing guide on the City of Cape Town website https://resource.capetown.gov.za/documentcentre/Documents/Procedures, guidelines and regulations/Embedded generation schematic drawings SK5276.pdf
June 9, 20233 yr Author 6 minutes ago, Dieter said: Off-Grid means you not connecting to GRID at all , no changeover needed and no Incoming COCT Your drawing is showing STANDBY SSEG with Grid support Here is an example of the line drawing guide on the City of Cape Town website https://resource.capetown.gov.za/documentcentre/Documents/Procedures, guidelines and regulations/Embedded generation schematic drawings SK5276.pdf Thanks for the info. So i will need to ammend my application to standyby sseg with grid support as its definately getting power from the grid as well. I will have a look at your link.
June 9, 20233 yr Add more info on the change over switch or transfer process to prove the connection is setup as passive , the connection only switches over on grid loss they can request site visit to check the hydrid inverter is not setup as grid tied Edited June 9, 20233 yr by Dieter
June 9, 20233 yr A comment I had after submitting an application to CoCT was that an Earth Leakage breaker must be fitted to protect plug circuits supplied by the inverter. This must come after the changeover switch so the same plug circuits have earth-leakage protection The electrical contractor who prepared the drawing did not know how to wire this since the earth-leakage neutral is different from the lighting and stove neutral. The inverter neutral uses this neutral
June 11, 20233 yr On 2023/06/09 at 9:25 PM, chrisc said: Earth Leakage breaker must be fitted to protect plug circuits supplied by the inverter. If your electrical contractor did not know this, then I would look for somebody else.
June 11, 20233 yr I have had 2 guys here who tell me the same thing The municipal power earth-leakage controls plugs attached to the unit The inverter power earth-leakage controls plugs attached to the inverter But the lighting circuit is not on earth-leakage The problem arises using the 2-pole changeover switch. This shunts the AC input of the inverter to the output from the inverter and disconnects the AC input When the changeover is in the municipal power mode, the inverter's earth leakage is not in circuit (and neither is the municipal power earth leakage)
April 5, 20251 yr How and where can I determine the status of a current SSEG application with the CoCT Municipality?
April 14, 20251 yr On 2025/04/05 at 11:39 PM, Hennik said:How and where can I determine the status of a current SSEG application with the CoCT Municipality?On e-services if it was done online.My father submitted his while they still took emailed applications, just under 2 years to allow commissioning and there was 0 way to track it.My application was smooth so far. Sparky did initial application, I installed the system, he came through and connected everything up and gave it all a look over, issued COC, Engineer came out and spent a whole 5 minutes, noted 1 thing that needed to be changed which was promptly done, and he's now submitted his documents.