Inverter Neutral Earth bonding
On 2024/09/18 at 12:43 AM, burgduino said:
Since the inverter does not have a dry contact, is it logical to assume it has the internal relay for PE/N bonding in battery mode?
No. The two relays are not related. Usually, if the inverter automatically connects AC-out neutral to earth, you should find with nothing connected to the inverter that AC-out neutral connects to earth, but AC-in neutral does not.
All Axpert inverters since about 2015 have this feature, but your diagram does not look like an Axpert inverter.
I would not use an RCD at the input of the inverter, due to the high likelihood of nuisance tripping. If you must have one for whatever reason, use one with a higher trip current than the usual 30mA. Definitely use an RCD on the output, as your diagram shows.
  • Replies 200
  • Views 61.1k
  • As another electrically inclined South African looking to stave off loadshedding and reliance on the incumbent utility, I also find myself trying to make sense of the Earth-Neutral bonding story
  • We have been around the block so many times regarding permanent neutral earth bonding. It is not allowed and is dangerous. A TN-S system shall not be converted to a TN-C system and all installations d
  • The E/N bond is only done at the inverter wires and it can be a relay in a DB. It is essential that this bond is only in place when running from battery. It is thus not a permanent bond.