Axpert 5K - Pylontech US3000


Recommended Posts

Posted

Please if anyone can assit.  I have Axpert  5Kva connected via BMS unit to Pylontech..  Only change made on Axpert is to change batt type to User.. I am not sure what rest must be.  My issue is on Axpert battery shows full but on Pylontech it seems to charge constantly second last light flickering and first light off (Charge indicator).  Indicating battery never full.  How do i get it to charge fully and sync the two.  Any assitance is appreciated.

Thanks

 

Posted
14 hours ago, AntonDj said:

I have Axpert  5Kva connected via BMS unit to Pylontech.

Which Axpert model exactly do you have? Most ones cannot talk to the BMS directly - so you probably need to manually set the charging parameters (52.2V Bulk and 51.8V Float) as well as the other voltage settings (Back to Grid, Back to Battery, Low DC Cutoff)

If your Axpert cannot talk directly with the Pylon BMS, I would strongly recommend ICC to be able to switch the Axpert based on the accurate BMS info instead of the Axpert's voltage readings

Posted
2 hours ago, wolfandy said:

Which Axpert model exactly do you have? Most ones cannot talk to the BMS directly - so you probably need to manually set the charging parameters (52.2V Bulk and 51.8V Float) as well as the other voltage settings (Back to Grid, Back to Battery, Low DC Cutoff)

If your Axpert cannot talk directly with the Pylon BMS, I would strongly recommend ICC to be able to switch the Axpert based on the accurate BMS info instead of the Axpert's voltage readings

I've seen some people set the Bulk charge to 52.5v. Has it been proven that 52.2v is sufficient? Maybe i missed the memo. lol

Posted
16 minutes ago, PurePower said:

I've seen some people set the Bulk charge to 52.5v. Has it been proven that 52.2v is sufficient? Maybe i missed the memo. lol

Sorry - typo 🥴 Was supposed to be 52.5V

Posted
11 hours ago, PurePower said:

I've seen some people set the Bulk charge to 52.5v. Has it been proven that 52.5v is sufficient?

Basically, yes. That's still more than I use for my 16S LFP battery (scaled by 16/15).

Posted
On 2021/02/05 at 8:28 PM, wolfandy said:

Which Axpert model exactly do you have? Most ones cannot talk to the BMS directly - so you probably need to manually set the charging parameters (52.2V Bulk and 51.8V Float) as well as the other voltage settings (Back to Grid, Back to Battery, Low DC Cutoff)

If your Axpert cannot talk directly with the Pylon BMS, I would strongly recommend ICC to be able to switch the Axpert based on the accurate BMS info instead of the Axpert's voltage readings

Thnx will check  maybe add some pics of the setup 

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...