Justice MM Posted June 23, 2021 Share Posted June 23, 2021 Hi. I have just installed a Shoto 5.18MWh and Deye 5-kW inverter and since March I have been struggling to get it working problem. The setup is used as loadshedding buster. During the Grid events, it works fine for a few hours and then trip after a few hours. The fault is "F40 Batt_Over_Current". I have since noticed that the inverter is not communicating with the battery and have tried a number of permutations to get it working. Kindly advise where I am making a mistake. Quote Link to comment Share on other sites More sharing options...
Yellow Measure Posted June 23, 2021 Share Posted June 23, 2021 10 minutes ago, Mphiliseni said: Hi. I have just installed a Shoto 5.18MWh and Deye 5-kW inverter and since March I have been struggling to get it working problem. The setup is used as loadshedding buster. During the Grid events, it works fine for a few hours and then trip after a few hours. The fault is "F40 Batt_Over_Current". I have since noticed that the inverter is not communicating with the battery and have tried a number of permutations to get it working. Kindly advise where I am making a mistake. Looking at the Dye manual, the Shoto isn't supported. You would need to contact Dye / Shoto or the dealer that sold it to you for support. I also see from the manual that the Dye can support various Lithium batteries, and that you must specify a type in "Lithium mode". Did you buy the inverter and the battery from the same supplier? Leshen 1 Quote Link to comment Share on other sites More sharing options...
Leshen Posted June 23, 2021 Share Posted June 23, 2021 5 hours ago, Mphiliseni said: Hi. I have just installed a Shoto 5.18MWh and Deye 5-kW inverter and since March I have been struggling to get it working problem. The setup is used as loadshedding buster. During the Grid events, it works fine for a few hours and then trip after a few hours. The fault is "F40 Batt_Over_Current". I have since noticed that the inverter is not communicating with the battery and have tried a number of permutations to get it working. Kindly advise where I am making a mistake. Hi. Have you tried using AGM V with voltage? Quote Link to comment Share on other sites More sharing options...
Justice MM Posted June 26, 2021 Author Share Posted June 26, 2021 The Shoto battery is made by Shuangdeng. I contacted the supplier and they sent me the communication setup which says I must use CAN and set it on 00. I have attached the document. Deye Inverter communication set up.pdf Scubadude 1 Quote Link to comment Share on other sites More sharing options...
Justice MM Posted June 26, 2021 Author Share Posted June 26, 2021 I tried to use these settings but same thing happened. The temperature probe doenst work either. It reads -100 Quote Link to comment Share on other sites More sharing options...
Yellow Measure Posted June 26, 2021 Share Posted June 26, 2021 That document is straight out of the Deye manual (Appendix I). As per the Deye manual page 31, this is the screen where you set it: If comms is good then you should see something like this in your LiBMS screen: If you don't, then it could be a cable fault, try swapping out the cable. If this does not work then I suggest returning the battery to the dealer. Alternatively you can try to use voltage to determine SoC, but you will need these very specific voltage settings from the manufacturer. It's also not the greatest way to do things, and will probably affect your battery life. Quote Link to comment Share on other sites More sharing options...
TheoVogel Posted September 14, 2021 Share Posted September 14, 2021 Hi, Did you get these two play together in the end. I am about to have a Deye 8kw with 2 Shoto 5.2kwh's installed I questioned the comms issue with the installer and he assured me that this is not a problem, but I's like some confirmation. Quote Link to comment Share on other sites More sharing options...
abd7 Posted September 14, 2021 Share Posted September 14, 2021 (edited) In advance I can advise you to rather go for pylontech. My installer didnt even know the inverter & batteries werent communcating. Shoto comms standards seem to vary between batteries. If I had the option I would have gone pylontech. See my recent thread for further info. Although if you trust your installer enough ... maybe Edited September 14, 2021 by Hansa Quote Link to comment Share on other sites More sharing options...
Solarcrazy Posted May 16, 2022 Share Posted May 16, 2022 On 2021/09/14 at 7:53 PM, TheoVogel said: Hi, Did you get these two play together in the end. I am about to have a Deye 8kw with 2 Shoto 5.2kwh's installed I questioned the comms issue with the installer and he assured me that this is not a problem, but I's like some confirmation. Hello, did you come right with the comms? I just installed a system this weekend and want to know how to connect the two batteries together and what cable to use? Quote Link to comment Share on other sites More sharing options...