Causes of high voltage neutral-ground? (Axpert)
I think that there is still a problem with though, if a generator is used. A generator presumably bonds its neutral output to earth, so that some of the generator neutral current would travel through the earth conductors. I think the GFCI won't trip, though these things do my head in when I can't see the whole schematic. I don't know the answer to that one. Especially when the generator can be disconnected. [ Edit: apart from an external earth to AC-out neutral relay. ]
-
Causes of high voltage neutral-ground? (Axpert)
There are actually a few 120 V Axpert models, but you have to buy two of them to make a split phase system. This is possibly one of the reasons that Axperts are not all that common in the USA. So yes, I can confidently say that bonding AC-out neutral to earth on a single Axpert inverter won't blow it up.
-
Causes of high voltage neutral-ground? (Axpert)
That only happens in very unusual inverters with split phase outputs (for those legacy countries still using 120 V), and when they also internally bond one of the phases to the metal case and to earth. As @plonkster told me recently (thanks!).
-
Causes of high voltage neutral-ground? (Axpert)
Heh. I see you have labelled your AC out with + and —. I friend of mine told me that in countries that use black for neutral and red for active (most house wiring in Australia is like that), there are plenty of electricians that believe this to be literally true, i.e. active is always positive with respect to neutral. In Australia, we use the international colours of brown / light blue / green-yellow for active / neutral / earth, in our flexible cables. But for reasons that escape me completely, our house wiring is red / black / green-yellow. @Nuno, I hope that you realise that AC (Alternating Current) also implies Alternating Voltage, even though we never call it that. So half the time, the red wires are negative with respect to the red ones. And a hundred times per second, they cross zero.
-
Causes of high voltage neutral-ground? (Axpert)
As @Javi Martínez suggests, that covers a lot of models: older 4 kW models, newer 5 kW models, 450 V MPPT models or 145 V MPPT models, Value models and standard models, and so on. The only models I'm fairly certain that have the AC out neutral to ground relay contact are the ones that come with main firmware 73.00. If you're off-grid, you can probably get away with connecting neutral AC out to earth. The GFCI breaker relies on a neutral to earth connection somewhere.
-
Correct battery setup for 2x 48v banks
I haven't, though I haven't looked seriously. It seems to me that the energy density is nowhere near that of batteries, and although the power density is quite good, you don't need power density for a solar energy system. There are also some scam products out there (huge thread). There is some question about self-discharge. Finally, the legitimate products seem to be very expensive, compared to batteries. But their cycle life is excellent (again, except for the scam products that are actually batteries anyway).
-
Pylon US2000B alarm again
All LFP cells look close when the cell voltage is at the 3.33 V plateau. It's mainly at the high and low ends that you can see an SOC difference as a significant difference in voltage. So your cells might not be as close as you think. I'm not saying you do this, but it's a classic beginners mistake to say "Wow! My cells are really well balanced! They're all within a millivolt of 3.333 V! It must have been my awesome balancing technique."
-
Mecer/Axpert Inverter Settings
Since the charging LED is flashing, you're still in the bulk or absorb stage. So the relevant setting is the absorb (misnamed as bulk/CV) setting. I presume that it's at least 56 V. The float voltage setting only becomes relevant when charging is over (and the charging LED is on solid). The inverter's reporting of state of charge (SOC) is very rough. Monitoring software will report the same SOC as the inverter, unless you have something like a BMV external battery monitor that counts coulombs, and the software is set up to read that. Even then, the external battery monitor relies on the battery getting full regularly, so that it can reset its SOC counter to 100%, and you don't seem to be getting there. What voltage is the battery reaching during charging? Certainly, 54.21 V when charging is nowhere near 100% SOC. What is the capacity (in amp-hours) of your battery? What is the nominal power rating (in watts or kilo-watts) of your solar panels? What is the voltage of your individual batteries making up your main battery? Often, it's 4 nominally 12 V modules in series; please measure each one. There is a chance that you have a shorted cell, in which case one or more modules will have a voltage about 2 V lower than the others. That would cause your symptoms of never stopping charging, since the battery voltage would never reach the absorb setting. Finally, is there a chance that your inverter is a clone? Some clones seem to have problems with dropping out the Solar Charge Controller. Is the solar panel indicator on the LC Display always on when the sun is shining?
-
CB Solar - PV1800 5KVA Schematic
Voltronic Power are the manufacturers of the genuine Axperts, which come by a wide variety of names. Must Power is the first of the clone manufacturers. I think your only hope is to convince them that it's an off-grid system. They are in fact sold as off-grid systems. The model PV1800 ususally indicates that it's a clone manufactured by Must Power. See my page Do I Own a Clone? Clone manufacturers usually don't provide technical documents of any sort, let alone a schematic or even a block diagram. If even genuine Axperts, say a Mecer, has to provide a block diagram from a service manual with the Mecer name and model on it, that's unlikely to happen, and a lot of owners are going to be in a lot of trouble. Many of the service manuals are completely unbranded. The following block diagram, which sounds like what you want, is from a service manual that is branded Voltronic Power: The above suggests that it's one of the first clones ever made, possibly serial number 0044, made in 2015/June/22. The first warning about the Must Power clones appeared in November 2015. Good luck finding your technical documentation; I think you're going to need it (the luck). At least, Must Power is a fairly large manufacturer in their own right. Perhaps start at this page, with the "downloads" tab, or talk to one of the online assistants: https://www.mustpower.com/pv1800-mpk-series-high-frequency-solar-inverter-1kva-5kva/
-
New member
[ Sorry for the late reply. ] Yes, use a pre-charge resistor! It can even be wired to a switch, or for the ultimate luxury, to a contactor or relay controlled by a small computer. All rated for at least 60 VDC, of course. I prefer a smaller valued resistor, like 3.3 Ω, for a nice quick start. It needs to be about a 50 W, high pulse power model (aluminium cased). Regardless of resistance, they all dissipate the same energy, the same amount of energy that is stored in the capacitors. So you may as well have a fairly quick pre-charge, as long as your switch / relay / contactor can handle the current. As well as being bad for the capacitors, the high surge current is also hard on the fuse contacts, or wherever the arc happens. Eventually, it can tarnish and lose metal and the contact can become high resistance. When I press my green start button, no less than seven contactors come on in quick succession (clack clack ... clack). One of those is for pre-charging the inverter capacitors. It's not good for the capacitors to charge at thousands of amps, as well as the other hazards. When I mash my big red switch™, there is a big clunk and they all drop out together, isolating AC in, AC out, PV in (both poles, both solar charge controllers). At the same time, a contactor in the main switchboard (DB) drops out and my house switches over to mains. All automatic. It did cost a bit for all the contactors, and took a while to wire up.
-
Axpert stay in BYPASS
Yes, assuming you keep this model, and get it going. You could even add one more panel and just wire it in series anywhere. High voltage MPPTS do simplify things on the roof. But there are safety considerations; these inverters don't do insulation monitoring.
-
LiFE battery charging using Bulk and float as with Lead Acid
I find I often have to select the "paste as plain text instead" (or similar) option that turns up after a second or so. Especially links to pages in the files section. It does seem silly not to allow fancy linking to pages on your own forum.
-
Axpert stay in BYPASS
I've seen the sticker; this is a genuine Voltronic Power inverter. It irritates me how Voltronic Power encourage their resellers to make up model names. As mentioned earlier, it's also a 450 V MPPT version.
-
Axpert stay in BYPASS
I wish I saw this post in time. Because it's an Axpert MKS II, as opposed to an Axpert MKS (non II), it's a model that has the higher voltage (450 V max Voc) MPPT. These models have incompatible hardware compared to the 145 V MPPT versions. There is no firmware update for the 450 V MPPT models, patched or otherwise, that I'm aware of. Unfortunately, the reflash tool doesn't stop you from updating with 73.00 (patched or not), and in this case the results are disasterous. I received a frantic PM from @kobus joubert this morning (my time). For the sake of other readers: please read the download instructions carefully! Usually, the major firmware version numbers have to match. The exceptions are the 72.XX series (XX ≥ 40), which replaced early 52.YY series, and are replaced by 73.00 (so far). 71.XX is for high voltage MPPT models. There are no firmware update files for these models. PF1 models and PF0.8 models (see below) have different, incompatible firmware. There is patched firmware for PF1 models (with all the patched firmware features, such as AussieView™, Dynamic Charge Control, Dynamic Load Control, and KettleKomp™), but ONLY (so far) for those PF1 models with the 64 V option. If you want patched firmware, double check when ordering a new machine that it has the 64 V option (whether you actually need that feature or not). It may cost a few percent more for this option. Weber and I are debating how to upgrade the warnings that precede the download files, to try and minimise this misfortune in future. This is normal. Nearly everything in the world, of all quality grades, is manufactured in mainland China. Voltronic Power have some 100 people in Taipai for Research and Development, but some 3200 people in China manufacturing the equipment. Yes, all the new 5 kA models are capable of 5 kW now; these are so-called PF1 models (unity Power Factor). The older models were PF0.8. So the battery-side converters are no longer the bottleneck. Voltronic seem to tweak the fan control logic frequently. That's probably because it's designed for higher voltage panels, at less current. I wondered why you got a high voltage MPPT model to replace your 145 V clone. Was this supposed to be a direct replacement, only genuine? In that case, you've really had a bad run.
-
Wind turbine
When you three-phase rectify (a bridge with 6 diodes) a three phase AC source, you do get close to DC, with a peak value of √2 (1.414) times the phase-to-phase voltage. But there is about 6% ripple (13% peak to peak); that's small enough to be neglected in some situations. But the power factor has to be terrible. Other than at the instant of phase "commutation", one phase always has zero current (the one phase that isn't the most positive or the most negative at any instant won't have either diode conducting). That can't be the best way to extract power from the wind turbine, and extracting maximum power is what a wind turbine is all about, right? So I would hope that a "real" 3-phase charge controller would actually have three boost converters that work on one of the three pairs of inputs. Each of these would be like the "PFC" stage (Power Factor Correction, but it's a terrible term for what it does), so that the current is nearly sinusoidal. It seems to me that these would have to be isolated from one another, so three high frequency transformers would be needed. This would seem moderately expensive. The big wind turbine farms would have to do this, I would think, but what about the smaller controllers? A quick web search seems to indicate that they just 3-phase rectify the output, with all the problems that this entails. Does anyone happen to know how it's actually done? Perhaps having current flow 2/3 of the time isn't considered so bad. Even though the current will fall from 86.6% of peak to zero for 120° of the cycle, then step to -86.6% of peak. I saw a paper suggesting that LC filter networks and a single boost converter (for the 6% ripple) can dramatically improve the power factor, so perhaps that's how it's done. But that was for fixed frequency, and high power low-frequency inductors are bulky and expensive, and with the variable frequency... it doesn't seem practical. As a total off-topic aside, we used to have trams (they would be called light rail these days) in Brisbane, Australia. These worked on nominally 600 VDC. We have 240 VAC power here, so three phase is 240 x √3 = 415 V phase to phase. They used to use mercury arc rectifiers to convert three phase 415 VAC to DC for the trams. 415 x √2 = 587 V, which rounds to 600 VDC. There is a tram museum here where enthusiasts still run a few trams over a short track, and the tour guide gives a history of the trams. There is even a "Who Killed the Electric Tram" side to the story: there was a suspicious depot fire near the end of the tram era, that soon saw the tram tracks ripped up and diesel buses took over. Back to the topic a little: they must not have cared much about power factor back in those days.
-
fuse blown again... any ideas?
And then the fuse won't be lonely any more. Sorry if I was a bit too subtle with my wisecrack.
-
Axpert stay in BYPASS
I guess the clones are surprising some of the suppliers as much as the owners. If only all suppliers were as accommodating. Well done.
-
fuse blown again... any ideas?
I think it's dying of loneliness Perhaps a fuse per string would be in order.
-
Inverter Internal Failure
+1. There are a bunch of small power supplies in there. One of them is the "main" power supply that provides +15 V, +5 V, and ±12 V. It's supplied on the primary side via three diodes (D9/D11/D14 in the SS 3 kW+ service manual, Figure 4.3). These diodes connect to two other power supplies, to derive power from the battery or AC in, or from BUS+ (which includes PV power). I don't know if either of these three power supplies is part of the Battery/DC-DC board or the AC board, and two of these small power supplies is all you need to power the processor and display from AC input. So as @Jaco de Jongh pointed out, running the display isn't a clear indication of the health of either of the two big power boards. In the model I worked on briefly, there seemed to me more than one "main" power supply as well, just to add confusion to the mix.
-
Inverter Internal Failure
This service manual for a 3 kW machine has pictures of the various boards. It should help, even though it's not quite the right machine. I had a 4 kW model for inspection for a while, and it seems to me that there are two big boards, the main board and the battery (perhaps also called DC-DC) board. Between them, these two boards are 90% of the electronics. The comms board is very small. There are many sub (daughter?) boards on both the larger boards, not plug-in but rather soldered in. I assume that these would come with the larger boards that they connect to. https://powerforum.co.za/files/file/10-1-phase-3kw-plus-hybrid-solar-inverter/
-
AC charger for Pylontech batteries
All Axpert models that I'm aware of have only one AC input, so the question (as it relates to Axperts) is moot. The AC input would connect to either the utility or a generator, never both.
- Gordon B
-
Axpert Settings
There are no dip switches or passwords. What brand and model of inverter do you have?
-
Axpert VM II 5KVA Inverter [Programming]
His machines (Axpert VM II then changed to Axpert MKS II) all have the higher voltage MPPT (450 or 500 V). The three panel limit (sometimes two) is for the models that have the 145 V maximum MPPT.
-
Axpert stay in BYPASS
We've established that your machine is a clone. Unfortunately, it's looking like the ones that come with main firmware version LC1 72.70c can't be updated, possibly due to a lack of bootloader code. So the good news is that you have the premature float bugs fixed. The bad news is it looks like you'll have to live with the other glitches that are presumably a result of imperfect copying. Sorry.