Hi guys

I have an existing 5 kVA inverter with 3x US3000C Pylontechs. It's an Axpert type inverter and although it has performed without problems for 2 years, I would like to replace it with 2 Sunsynk 5kVAs and add 3 more batteries.  My question is, the manuals say that only 3 batteries can be connected using the standard cable (25mm^2), so how do you connect 6 batteries? My 3 are currently connected as per standard in parallel with the positive coming off the master and the negative off the 3rd battery, with the standard interlink cables between the 3.  

Thanks

Greg

Link to comment
Share on other sites

9 hours ago, greghayter said:

Hi guys

I have an existing 5 kVA inverter with 3x US3000C Pylontechs. It's an Axpert type inverter and although it has performed without problems for 2 years, I would like to replace it with 2 Sunsynk 5kVAs and add 3 more batteries.  My question is, the manuals say that only 3 batteries can be connected using the standard cable (25mm^2), so how do you connect 6 batteries? My 3 are currently connected as per standard in parallel with the positive coming off the master and the negative off the 3rd battery, with the standard interlink cables between the 3.  

Thanks

Greg

For US3000C, you can have as much as 16 x Batteries in one bank. The standard battery cable for pylontec is capable of carrying 120A, doubling the cable will increase that to 240A. BTW, This information is there in the manual😀

Link to comment
Share on other sites

3 hours ago, Piper said:

Hi greghayter 

You can have 16 us3000c in a parallel config. Current draw limit to 100A per cable. 
So a good config for you would be 2 packs of 3 batteries each on 2 pairs of cable. 

 

IMG_5898.jpg

Please share,... where do you get the 100A per cable from? the documentation say 120A

 

image.thumb.png.c3b0a8a1e662756210347d37c8643029.png

Link to comment
Share on other sites

Nice , i was just thinking another option to avoid a expensive busbar solution would be to make two packs of 3 batteries wire them to the inverters and then just parallel the 2 packs of 3 with the leftover ports on the batteries(with say 2 one meter cables),so then all 6 batteries will function as one pack as required and each inverter can do 100/120 amps easily.

Link to comment
Share on other sites

1 hour ago, hoohloc said:

Please share,... where do you get the 100A per cable from? the documentation say 120A

 

image.thumb.png.c3b0a8a1e662756210347d37c8643029.png

Have a look see .

Maybe they updated the cable specs as this is what my manual shows.They changed the constant to a 100A.

This must be what I was thinking about.But yes the cables are good for 120A under normal ops.  My Bad..

Screenshot (7).png

Edited by Piper
Link to comment
Share on other sites

Regarding the Parallel topic.

I just made 2 short cables and connected them to the bottom of the fuse holders.(Needed 2 fuse holders because the one I Had was only rated to 160A)

If you have one of those 250A fuse holders you should be able to connect both cables to it no problem.

Edited by Piper
Link to comment
Share on other sites

14 minutes ago, hoohloc said:

ok, I thought you had bridged the two fuse holders at the bottom. 

I did  

Look closely and you will see there is 2 cables in each port

If you look closely at the Orange cable you will see that I used white heat shrink on the link cable. On the black link I used black heat shrink so cant really see it.

 

 

IMG_5899.jpg

Screenshot (8).png

Edited by Piper
Link to comment
Share on other sites

Hi Everyone

Thanks for all the responses. 

So some follow up questions and some comments. As per the image posted by Piper, the interconnect cables are 180mm in length - I have a 4 battery cabinet and plan to get another identical cabinet to put on top or alongside to house the additional batteries, with the aim of getting to 8 batteries eventually. Any suggestions on where to get a cable long enough to parallel all the batteries - the jump between cabinets will be longer than the standard cable? 

The full story behind my change in inverter is that we installed it 2 years ago as a load shedding solution in our house under a stairwell, and then decided to build a cottage for my parents who have just moved in. So they are on grid power at the moment - I have installed a main DB in the new garage which then feeds the house and cottage so I plan to install the bank of inverters and batteries in the garage to feed both house and cottage.

So after that long winded explanation, the issue is I want to parallel the new inverters and my understanding is that running them off a common bus on the DC side is the best solution so the charging duty is split between between inverters, and on the AC side the idea is to also feed a common AC DB which will feed the main DB. I just think that it is a much more flexible approach.

I want to install 2 inverters initially, but with 2 households there is the possibility of needing a third. Are there any thoughts on the pros/cons of running 2x 8 kVAs vs 3x 5 kVAs? The one limit is that Sunsynk only allow 3 single phase in parallel, so using the 8 kVA allows for expansion to 24 kVA at a later point, whereas 3x 5s is already maxed out. However 3x 5s are a lot more cost effective than 2x 8s.

As a note, my geysers and oven are still on Eskom, but the plan going forward is to either:

a) connect them to the inverter system, probably necessitating at least 15 kVA capacity

b) go to either vacuum tube or

c) go the DC element route with its own panels

Any comments on these options?

Thanks again for all the feedback

Edited by greghayter
Link to comment
Share on other sites

You will always end up with a spare set of those 180 mm link cables.Nothing prevents you from chopping them in half and extending them with the same type cable.Proper ferrules and a hydraulic crimper would be required though , OR  buy an additional set of cables.

The other thing is that KVA is is apparent power.

So 8kva at a power factor of 1.0 is 8000 watt but at a power factor of 0.8 it will only be 6400 watt.

My 10kva system is only good for 8000 watt. Keep this in mind when you shop for inverters.

 

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...