June 17, 20233 yr 4 minutes ago, Eurard said: Okay found some 6mm done black on A1 Ok, with relay still out, switch the grid supply on and test for 220vac across A1 and A2. Edited June 17, 20233 yr by BritishRacingGreen
June 17, 20233 yr 7 minutes ago, BritishRacingGreen said: Ok, with relay still out, switch the grid supply on and test for 220vac across A1 and A2. Yup 230 across A1/2 relay out
June 17, 20233 yr 2 minutes ago, Eurard said: Yup 230 across A1/2 relay out Ok with no cables yet on the klippon terminals : 1 switch grid off 2. Insert relay. Relay is supposed to have a LED. Relay should be down (off) 3. Switch grid on. Relay should be up (on). 4. Now check for continuity with meter between klippon terminal N and E. There should be none. 5.switch grid off 6.Now check for continuity with meter between klippon terminal N and E. There should be close to 0 ohm (short) .
June 17, 20233 yr 3 minutes ago, BritishRacingGreen said: Ok with no cables yet on the klippon terminals : 1 switch grid off 2. Insert relay. Relay is supposed to have a LED. Relay should be down (off) 3. Switch grid on. Relay should be up (on). 4. Now check for continuity with meter between klippon terminal N and E. There should be none. 5.switch grid off 6.Now check for continuity with meter between klippon terminal N and E. There should be close to 0 ohm (short) . 100% as per above on everything
June 17, 20233 yr Okay I assume one last step. Neutral from inverter to klipons and from klipons to load neutral bar
June 17, 20233 yr This post was recognized by Energy-Jason! BritishRacingGreen was awarded the badge 'Superstar' "25" 2 minutes ago, Eurard said: Okay I assume one last step. Neutral from inverter to klipons and from klipons to load neutral bar Yes, but one last test for safety and the good order: 1. Switch grid off and measure between A1 and A2 that there is nothing. 2. Test for continuity between A1 and klippon L, N and E respectively. You should have open circuit. 3 repeat test 2 but from A2 terminal. If all goes well, conclude by wiring in your inverter output and load netral and earth. Remove relay while doing so. 4. Switch inverter on and test if your loads respond. 5.insert relay. 6 switch on grid 7. Di your bonding test when both in grid and islanding mode. 8 have beer
June 17, 20233 yr 1 minute ago, BritishRacingGreen said: Yes, but one last test for safety and the good order: 1. Switch grid off and measure between A1 and A2 that there is nothing. 2. Test for continuity between A1 and klippon L, N and E respectively. You should have open circuit. 3 repeat test 2 but from A2 terminal. If all goes well, conclude by wiring in your inverter output and load netral and earth. Remove relay while doing so. 4. Switch inverter on and test if your loads respond. 5.insert relay. 6 switch on grid 7. Di your bonding test when both in grid and islanding mode. 8 have beer Dude you are a BLOODY legend! I will drink that beer with a smile! I will finalize, need to go get some lesser sized wires, for final step. I have enough for Inverter to kilppon but need from klippon to Load neutral bar. I cannot thank you enough and with your blessings I will make a slide that details these steps for other users and future use.
June 17, 20233 yr My setup is quite unique as well as my mains ac goes to a breaker, then through a smart switch, then through a over under breaker and then to inverter. The AC from mains to A1 and A2 was taken from output of the over under, so that it incorporates all protective devices. I have so much protection it isnt even funny lol.
June 17, 20233 yr 31 minutes ago, Eurard said: Dude you are a BLOODY legend! I will drink that beer with a smile! I will finalize, need to go get some lesser sized wires, for final step. I have enough for Inverter to kilppon but need from klippon to Load neutral bar. I cannot thank you enough and with your blessings I will make a slide that details these steps for other users and future use. Thanks, if you create a nice slide thats wonderfull. We are here to support and share, thats the spirit.
June 17, 20233 yr Sorry to hijack this thread, but would one require the neutral earth bonding box for a Growatt or Luxpower inverter?
June 17, 20233 yr 2 hours ago, BritishRacingGreen said: Thanks, if you create a nice slide thats wonderfull. We are here to support and share, thats the spirit. Tested all now and .... Drum roll .... Eskom off, L-N 230V, L-G 230V, E-N 0V
June 17, 20233 yr 3 hours ago, PsyCLown said: Sorry to hijack this thread, but would one require the neutral earth bonding box for a Growatt or Luxpower inverter? With the help of someone who has a Growatt it seems both do have internal bonding. @zsde
June 17, 20233 yr 3 hours ago, BritishRacingGreen said: Thanks, if you create a nice slide thats wonderfull. We are here to support and share, thats the spirit. Another very helpful discussion. Well done @BritishRacingGreen
June 17, 20233 yr 4 hours ago, PsyCLown said: Sorry to hijack this thread, but would one require the neutral earth bonding box for a Growatt or Luxpower inverter? I don't know the Growatts or LuxPower , but if it is reasonably late models , then I will be surprised if they haven't got internal bonding. The last two generations of Axperts have built-in bonding arrangements . There is a quick-and-dirty way of gauging whether there is built in bonding .Remove all wires from the input and output terminals , switch the inverter off , and measure for continuity between input neutral and output neutral . If there is none then measure for continuity between output neatral and inverter earth terminal . If there is continuity then there exist internal bonding. But this must be functionally verified in the final analysis , by using a plug tester on the inverter load output . The test button button on RCD is not good enough , because it does not prove earth leakage , only residual current. The plug tester is a must.
June 18, 20233 yr 29 minutes ago, Eurard said: Just as a follow up, all ghosting gone! Thanks again @BritishRacingGreen Good news, it must also be said that if the person at the other end is competent like you then it makes life an order of magnitude easier.
June 19, 20233 yr On 2023/06/17 at 7:44 PM, BritishRacingGreen said: I don't know the Growatts or LuxPower , but if it is reasonably late models , then I will be surprised if they haven't got internal bonding. The last two generations of Axperts have built-in bonding arrangements . There is a quick-and-dirty way of gauging whether there is built in bonding .Remove all wires from the input and output terminals , switch the inverter off , and measure for continuity between input neutral and output neutral . If there is none then measure for continuity between output neatral and inverter earth terminal . If there is continuity then there exist internal bonding. But this must be functionally verified in the final analysis , by using a plug tester on the inverter load output . The test button button on RCD is not good enough , because it does not prove earth leakage , only residual current. The plug tester is a must. Thanks, will give this a try when I get my install done. Appreciate the info and assistance. On 2023/06/17 at 5:51 PM, Scorp007 said: With the help of someone who has a Growatt it seems both do have internal bonding. @zsde That is good to know, makes life easier and simpler
June 19, 20233 yr 7 hours ago, Eurard said: Hi @Eduard this is very well done , thanks for your support !