Earth neutral bond

Featured Replies

That looks like a permanent bond to me and I believe SANS states that one should not have a permanent Earth / Neutral bond.

A relay would be required so that the bond is only there when there is no grid - when there is grid then the bond must not be in place.

 

I assume the connection is on the output side of the inverter, correct?

 

That looks like a permanent bond to me and I believe SANS states that one should not have a permanent Earth / Neutral bond.

A relay would be required so that the bond is only there when there is no grid - when there is grid then the bond must not be in place.

 

I assume the connection is on the output side of the inverter, correct?

He asked it is was safe, not is it complied with legal requirements.

Also, in order to answer if it is legal or not one needs to understand if his neutrals have been split or not. If all his loads are on the UPS side of the inverter then that is legal ito SANS.

What is the aim of such a Bond? To get the Earth Leakage to be functional during loadshedding. It is Safe, it is not ideal & compliant but it get the Earth leakage to work & that is important & safe. 

We can split hairs until the crows fly home...

1st Prize 🏆 - Earth Neutral Relay Bond (safe & Compliant) = Working Earth Leakage during loadshedding 

2nd Prize - Permanent bond (safe & Non Compliant) = Working Earth leakage during loadshedding

3rd Prize - leave the Neutral floating (unsafe & Non compliant) = Earth leakage not working.

If someone asked me which is better I'd say choose the option that gets the earth Leakage to work. 

Let's ask another question: 

Would you remove your earth leakage from your DB box & wire your plugs from raw power? 

Most will say no...So 3rd Prize is probably the worst of all.

 

  • Author

Awesome thank you. 

My brother had his system installed by a reputable company.  Part of the deal was to have it registered with COCT.  Alas, after 8 months no registration (blaming city for incompetence).  After considerable pressure from his side eventually he got his letter of approval. 

Engineer came to sign off installation and guess what!!!!! It didn't pass.... Don't have all the details but earth leakage doesn't trip when tested... Apparently something to do with earthing.  Company installed 2x 2 meters earthing rods but still no joy.  Could this be related to earth neutral bonding not being in place? 

 

 

What is the aim of such a Bond? To get the Earth Leakage to be functional during loadshedding. It is Safe, it is not ideal & compliant but it get the Earth leakage to work & that is important & safe. 

We can split hairs until the crows fly home...

1st Prize 🏆 - Earth Neutral Relay Bond (safe & Compliant) = Working Earth Leakage during loadshedding 

2nd Prize - Permanent bond (safe & Non Compliant) = Working Earth leakage during loadshedding

3rd Prize - leave the Neutral floating (unsafe & Non compliant) = Earth leakage not working.

If someone asked me which is better I'd say choose the option that gets the earth Leakage to work. 

Let's ask another question: 

Would you remove your earth leakage from your DB box & wire your plugs from raw power? 

Most will say no...So 3rd Prize is probably the worst of all.

 

Hi Steve, is option 2 still non compliant if signed off by the municipality?  What is the risk of a relay bond failing?

Are there other mitigations one could put in place?

 

Hi Steve, is option 2 still non compliant if signed off by the municipality?  What is the risk of a relay bond failing?

Are there other mitigations one could put in place?

@Haggers i am not aware of any municipality that signs off a COC. Did you present the coc to the municipality for their records. Permanent neutral bond is not legal and also stated as such in the regulations sans10142. The electrician that did the coc should have rectified the permanent bond before issuing the coc 

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.