creyneke Posted December 20, 2018 Share Posted December 20, 2018 Hi I have two Axpert 5K in verters set up in parallel using grid power to charge the batteries and rely on this in the event of load shedding. My question is that only the slave is putting out power and when it get to 4Kva it overlaods, however the master inverter only puts out 44V? Is this a setting I have wrong? Can somebody please help me "shed some light on the matter" Quote Link to comment Share on other sites More sharing options...
Coulomb Posted December 20, 2018 Share Posted December 20, 2018 13 minutes ago, creyneke said: however the master inverter only puts out 44V? I assume you mean 44 VA. It sounds like your master isn't paralleled with the slave at all, and isn't providing any of the load. Check your AC output wiring and breakers. ___ 1 Quote Link to comment Share on other sites More sharing options...
creyneke Posted December 20, 2018 Author Share Posted December 20, 2018 Can you please advise what the wiring should look like, I have had it installed by a contractor. How will I know if it is indeed paralleled, it does show the master as well as the slave but the master is not giving any load. I know the live and neutral (feed) come into the master and then a live and neutral is taken to the slave. The live and neutral (load) also comes out of the master with a live and neutral wire going from the master to the slave. Obviously there is also the communication cables joining the two inverters. Does anything sound out of the ordinary Quote Link to comment Share on other sites More sharing options...
___ Posted December 20, 2018 Share Posted December 20, 2018 1 hour ago, Coulomb said: I assume you mean 44 VA. It sounds like your master isn't paralleled with the slave at all, and isn't providing any of the load. Check your AC output wiring and breakers. I've had two support calls already from people with the new Multiplus who didn't parallel up the outputs correctly. Because this inverter is grid parallel, it ends up pushing half the power out of the input... leading to hilarious results: Whatever you draw on the output of the one, the other feeds the exact same amount into the grid :-) Quote Link to comment Share on other sites More sharing options...
creyneke Posted December 20, 2018 Author Share Posted December 20, 2018 How do I sort this out, can you please pm me your number Quote Link to comment Share on other sites More sharing options...
___ Posted December 20, 2018 Share Posted December 20, 2018 43 minutes ago, creyneke said: How do I sort this out, can you please pm me your number Coulomb is in Australia and I'm a Victron guy :-) Quote Link to comment Share on other sites More sharing options...
creyneke Posted December 20, 2018 Author Share Posted December 20, 2018 Does anybody perhaps have pictures of an installation so I can see if it is wired correctly please. Thanks in advance Quote Link to comment Share on other sites More sharing options...
Chris Hobson Posted December 20, 2018 Share Posted December 20, 2018 Here is a parallel of a 4kW installation I assume pretty much the same Parallel-installation-AxpertKS+MKS-4K-5K-20141014.pdf ___ and Fazil 2 Quote Link to comment Share on other sites More sharing options...
creyneke Posted December 20, 2018 Author Share Posted December 20, 2018 Hi Chris It is wired exactly as described in the document you provided (thanks!) but still only drawing load from the one inverter. I thought that maybe there was a setting to tell it to draw load from both of the inverters? Quote Link to comment Share on other sites More sharing options...
Chris Hobson Posted December 20, 2018 Share Posted December 20, 2018 That is weird. Are you sure that the two machines are paralleled? You need to switch off the unit when programming it to get it into parallel mode. Quote Link to comment Share on other sites More sharing options...
creyneke Posted December 20, 2018 Author Share Posted December 20, 2018 Yes setting 28 is set to PAL. When you switch on one of the units shows H5 (Master) and the other shows SL (Slave) Quote Link to comment Share on other sites More sharing options...
creyneke Posted December 20, 2018 Author Share Posted December 20, 2018 Quote Link to comment Share on other sites More sharing options...
creyneke Posted December 20, 2018 Author Share Posted December 20, 2018 As you can see it is definitely in parallel, however no load on the "Master" inverter Quote Link to comment Share on other sites More sharing options...
Chris Hobson Posted December 20, 2018 Share Posted December 20, 2018 Ok so the only thing I can think is physical. If you switch the slave off does the master take over the load? ___ 1 Quote Link to comment Share on other sites More sharing options...
___ Posted December 20, 2018 Share Posted December 20, 2018 Don't these things also have current sharing cabling? A problem on those might make it THINK that the second one is working while it isn't? In which case I concur with Chris. Switch off the slave and see if the power drops out or not. Quote Link to comment Share on other sites More sharing options...
Coulomb Posted December 20, 2018 Share Posted December 20, 2018 6 hours ago, creyneke said: I have had it installed by a contractor. I think you need to get him/her back. 6 hours ago, creyneke said: How will I know if it is indeed paralleled, it does show the master as well as the slave but the master is not giving any load. What you see is pretty much what I'd expect if the connection from master to slave on the AC outputs wasn't connecting somehow. It could be as simple as a terminal not screwed tight. If you're not familiar with electrical work, don't attempt to fix it yourself. I'm not hearing anything about breakers at the AC inputs or outputs. Those should be there (three total; the AC inputs can share a higher current breaker). A photo of the wiring might show something obvious. I agree with others that the most important test is to switch off the slave to see if the master can power the load on its own. There could be something with the current sharing cables, as others have also mentioned. You could be justifiably cranky about the installation not being properly tested. ___ 1 Quote Link to comment Share on other sites More sharing options...
creyneke Posted December 21, 2018 Author Share Posted December 21, 2018 Does anybody know somebody in the Benoni area I could call out to come take a look please? Quote Link to comment Share on other sites More sharing options...
SilverNodashi Posted December 21, 2018 Share Posted December 21, 2018 Can you send a pic of the wiring? Quote Link to comment Share on other sites More sharing options...
creyneke Posted December 21, 2018 Author Share Posted December 21, 2018 its all in trunking Quote Link to comment Share on other sites More sharing options...
creyneke Posted December 21, 2018 Author Share Posted December 21, 2018 Quote Link to comment Share on other sites More sharing options...
SilverNodashi Posted December 21, 2018 Share Posted December 21, 2018 6 minutes ago, creyneke said: Yes that doesn't help much. I can come take a look if you want to? I am in the area, so to speak, will send you a PM Chris Hobson 1 Quote Link to comment Share on other sites More sharing options...
creyneke Posted December 21, 2018 Author Share Posted December 21, 2018 thank you so much Quote Link to comment Share on other sites More sharing options...
___ Posted December 21, 2018 Share Posted December 21, 2018 If you snipped the cable ties and just opened up that one strip below the inverters, I bet that'd be enough to see something. But the fault might still be inside the lower sides of the inverters too (eg loose screw terminal). Quote Link to comment Share on other sites More sharing options...
weber Posted December 22, 2018 Share Posted December 22, 2018 I'm kind of surprised that no one has mentioned the fact there is no inverting going on here. The Axperts are in bypass. So they have no way of controlling how load current is shared between them. Their current-sharing cables make no difference in bypass mode. So it's not the Axpert's fault, unless the master has a failed relay, which seems unlikely. There has to be a high resistance, or open circuit, in that part of the path from the master's AC output to the loads, that is not shared by the slave. There is a load switch on the bottom right of each inverter. Turning it off will disconnect that inverter from the loads. If everything was working correctly, you could turn off either one and the loads would still be powered via the relays in the other inverter. But if the above is correct, turning off the load switch on the bottom of the master will make no difference, however turning off the load switch on the bottom of the slave will cause the loads to brown-out, or lose power completely. If they brown out, you should turn the load switch back on immediately. And in any case, consult an electrician. ___ and Gabriel_2018 2 Quote Link to comment Share on other sites More sharing options...
SilverNodashi Posted January 10, 2019 Share Posted January 10, 2019 On 2018/12/22 at 3:40 AM, weber said: I'm kind of surprised that no one has mentioned the fact there is no inverting going on here. The Axperts are in bypass. So they have no way of controlling how load current is shared between them. Their current-sharing cables make no difference in bypass mode. So it's not the Axpert's fault, unless the master has a failed relay, which seems unlikely. There has to be a high resistance, or open circuit, in that part of the path from the master's AC output to the loads, that is not shared by the slave. There is a load switch on the bottom right of each inverter. Turning it off will disconnect that inverter from the loads. If everything was working correctly, you could turn off either one and the loads would still be powered via the relays in the other inverter. But if the above is correct, turning off the load switch on the bottom of the master will make no difference, however turning off the load switch on the bottom of the slave will cause the loads to brown-out, or lose power completely. If they brown out, you should turn the load switch back on immediately. And in any case, consult an electrician. I had a look at the inverters and it seems the one inverter is faulty. Even in single mode without the comms and current sharing cables, there was no voltage on the AC output terminals. I had a quick look inside and couldn't see any visible signs of failure though and suspect a faulty motherboard. Quote Link to comment Share on other sites More sharing options...