December 20, 20187 yr Hi I have two Axpert 5K in verters set up in parallel using grid power to charge the batteries and rely on this in the event of load shedding. My question is that only the slave is putting out power and when it get to 4Kva it overlaods, however the master inverter only puts out 44V? Is this a setting I have wrong? Can somebody please help me "shed some light on the matter"
December 20, 20187 yr 13 minutes ago, creyneke said: however the master inverter only puts out 44V? I assume you mean 44 VA. It sounds like your master isn't paralleled with the slave at all, and isn't providing any of the load. Check your AC output wiring and breakers.
December 20, 20187 yr Author Can you please advise what the wiring should look like, I have had it installed by a contractor. How will I know if it is indeed paralleled, it does show the master as well as the slave but the master is not giving any load. I know the live and neutral (feed) come into the master and then a live and neutral is taken to the slave. The live and neutral (load) also comes out of the master with a live and neutral wire going from the master to the slave. Obviously there is also the communication cables joining the two inverters. Does anything sound out of the ordinary
December 20, 20187 yr 1 hour ago, Coulomb said: I assume you mean 44 VA. It sounds like your master isn't paralleled with the slave at all, and isn't providing any of the load. Check your AC output wiring and breakers. I've had two support calls already from people with the new Multiplus who didn't parallel up the outputs correctly. Because this inverter is grid parallel, it ends up pushing half the power out of the input... leading to hilarious results: Whatever you draw on the output of the one, the other feeds the exact same amount into the grid :-)
December 20, 20187 yr 43 minutes ago, creyneke said: How do I sort this out, can you please pm me your number Coulomb is in Australia and I'm a Victron guy :-)
December 20, 20187 yr Author Does anybody perhaps have pictures of an installation so I can see if it is wired correctly please. Thanks in advance
December 20, 20187 yr Here is a parallel of a 4kW installation I assume pretty much the same Parallel-installation-AxpertKS+MKS-4K-5K-20141014.pdf
December 20, 20187 yr Author Hi Chris It is wired exactly as described in the document you provided (thanks!) but still only drawing load from the one inverter. I thought that maybe there was a setting to tell it to draw load from both of the inverters?
December 20, 20187 yr That is weird. Are you sure that the two machines are paralleled? You need to switch off the unit when programming it to get it into parallel mode.
December 20, 20187 yr Author Yes setting 28 is set to PAL. When you switch on one of the units shows H5 (Master) and the other shows SL (Slave)
December 20, 20187 yr Author As you can see it is definitely in parallel, however no load on the "Master" inverter
December 20, 20187 yr Ok so the only thing I can think is physical. If you switch the slave off does the master take over the load?
December 20, 20187 yr Don't these things also have current sharing cabling? A problem on those might make it THINK that the second one is working while it isn't? In which case I concur with Chris. Switch off the slave and see if the power drops out or not.
December 20, 20187 yr 6 hours ago, creyneke said: I have had it installed by a contractor. I think you need to get him/her back. 6 hours ago, creyneke said: How will I know if it is indeed paralleled, it does show the master as well as the slave but the master is not giving any load. What you see is pretty much what I'd expect if the connection from master to slave on the AC outputs wasn't connecting somehow. It could be as simple as a terminal not screwed tight. If you're not familiar with electrical work, don't attempt to fix it yourself. I'm not hearing anything about breakers at the AC inputs or outputs. Those should be there (three total; the AC inputs can share a higher current breaker). A photo of the wiring might show something obvious. I agree with others that the most important test is to switch off the slave to see if the master can power the load on its own. There could be something with the current sharing cables, as others have also mentioned. You could be justifiably cranky about the installation not being properly tested.
December 21, 20187 yr Author Does anybody know somebody in the Benoni area I could call out to come take a look please?
December 21, 20187 yr 6 minutes ago, creyneke said: Yes that doesn't help much. I can come take a look if you want to? I am in the area, so to speak, will send you a PM
December 21, 20187 yr If you snipped the cable ties and just opened up that one strip below the inverters, I bet that'd be enough to see something. But the fault might still be inside the lower sides of the inverters too (eg loose screw terminal).
December 22, 20187 yr I'm kind of surprised that no one has mentioned the fact there is no inverting going on here. The Axperts are in bypass. So they have no way of controlling how load current is shared between them. Their current-sharing cables make no difference in bypass mode. So it's not the Axpert's fault, unless the master has a failed relay, which seems unlikely. There has to be a high resistance, or open circuit, in that part of the path from the master's AC output to the loads, that is not shared by the slave. There is a load switch on the bottom right of each inverter. Turning it off will disconnect that inverter from the loads. If everything was working correctly, you could turn off either one and the loads would still be powered via the relays in the other inverter. But if the above is correct, turning off the load switch on the bottom of the master will make no difference, however turning off the load switch on the bottom of the slave will cause the loads to brown-out, or lose power completely. If they brown out, you should turn the load switch back on immediately. And in any case, consult an electrician.
January 10, 20197 yr On 2018/12/22 at 3:40 AM, weber said: I'm kind of surprised that no one has mentioned the fact there is no inverting going on here. The Axperts are in bypass. So they have no way of controlling how load current is shared between them. Their current-sharing cables make no difference in bypass mode. So it's not the Axpert's fault, unless the master has a failed relay, which seems unlikely. There has to be a high resistance, or open circuit, in that part of the path from the master's AC output to the loads, that is not shared by the slave. There is a load switch on the bottom right of each inverter. Turning it off will disconnect that inverter from the loads. If everything was working correctly, you could turn off either one and the loads would still be powered via the relays in the other inverter. But if the above is correct, turning off the load switch on the bottom of the master will make no difference, however turning off the load switch on the bottom of the slave will cause the loads to brown-out, or lose power completely. If they brown out, you should turn the load switch back on immediately. And in any case, consult an electrician. I had a look at the inverters and it seems the one inverter is faulty. Even in single mode without the comms and current sharing cables, there was no voltage on the AC output terminals. I had a quick look inside and couldn't see any visible signs of failure though and suspect a faulty motherboard.