May 1, 20242 yr Today I visited a site where a previous installer had worked. This customer has a 16Kw Deye and has a 5.5Kw generator as a supplement when there isn’t enough solar. The way the previous installer got around this issue described above was by setting the Gen port as a Microinverter input. I’m not saying this is the correct way to do it, but it works for this customer. The generator runs happily without dipping at all. I do notice that you cannot adjust how much power is drawn from the generator, but it sits at 3Kw for hours without any problems.
May 2, 20242 yr Author @Gandalf thanks. The current generator though is wired into grid not the gen port.
May 12, 20242 yr Author So, just an update we have obtained a 9KVA Kipor KDE12STA Diesel generator and had the electrician connect it to the gen port and it now charges the batteries when the grid is disconnected. However is it possible to get the generator to charge the batteries while the grid is connected? We are currently trying to source a auto start for the generator to start it if the solar stops producing and batteries are below 100%, this would also depend on the time of day, as an example between 5PM and 8PM gen can run to charge batteries, but after 8PM it must not do anything unless the battery gets to a critical level of 15% and there is no solar production Does anyone have any experience with auto starts on these generators? Is it possible to do a diy solution using a sonoff device maybe?
May 13, 20242 yr 14 hours ago, Mercadian said: We are currently trying to source a auto start for the generator to start it if the solar stops I have used DSE controllers with great success you can shop around for these untis but i know Bundu Power stock some of the DSE(Deep Sea) models. https://www.deepseaelectronics.com/genset/manual-auto-start-control-modules Edited May 13, 20242 yr by TaliaB
May 13, 20242 yr Author 4 hours ago, TaliaB said: I have used DSE controllers with great success you can shop around for these untis but i know Bundu Power stock some of the DSE(Deep Sea) models. https://www.deepseaelectronics.com/genset/manual-auto-start-control-modules Thank you. Will check it out.
May 13, 20242 yr Hello. I encountered a problem when connecting the generator to my DEYE 8kW inverter single phase. The frequency of the generator was 53 HZ. I connect the generator of 8000 W single phase, and after few seconds i heard something pops inside the inverter, the inverter still operating correctly, i didn't saw the generator icon on the screen, the SOC of the battery show 0% but the voltage is 53V. I shut down the inverter and after restart the SOC shows 100% and everything is correct. I would like to know if the inverter got damaged or partially after this pop. it's safe to use again the GEN port.? I am afraid to connect again the generator, Thank you in advance.
May 14, 20242 yr 15 hours ago, ELIAS E said: The frequency of the generator was 53 Hz. The generator needed to synchronise to the 50 Hz of the grid first. It may or may not have this capability. You can't just connect two AC sources together, unless they are carefully designed for this. It's possible that the generator is damaged as well. There is a fuse or breaker inside the inverters at the AC-in port. It might just be that this tripped and nothing else, if you were very lucky.
December 19, 20241 yr We have a strange issue with Deye Sun-30k. There is no sun, so the PV is not working, there is no grid, so we have to charge from a generator with a capacity of 18KW. In the battery settings we set Start at 70% (for testing), A is 30 A, Gen Charge is on, Gen Signal is on, in Gen Port Use we set Generator Input Rated Power to 15KW. And when the battery charge drops to 70%, the generator turns on and charges the batteries, but not to 100%, but only to 75% and turns off. Later, when the battery drops to 70% again, the generator turns on and charges the battery to 73% or 77% and so on. What could be wrong?
January 5, 20251 yr On 2024/12/19 at 1:36 PM, support said: We have a strange issue with Deye Sun-30k. There is no sun, so the PV is not working, there is no grid, so we have to charge from a generator with a capacity of 18KW. In the battery settings we set Start at 70% (for testing), A is 30 A, Gen Charge is on, Gen Signal is on, in Gen Port Use we set Generator Input Rated Power to 15KW. And when the battery charge drops to 70%, the generator turns on and charges the batteries, but not to 100%, but only to 75% and turns off. Later, when the battery drops to 70% again, the generator turns on and charges the battery to 73% or 77% and so on. What could be wrong? Nothing is wrong, "Start at 70%" means generator will start working when charge is 70% or below. So when your battery SoC is above 70% inverter will stop charging from generator. By the way, I have a costumer in offgrid and sometimes he need charge the batteries with inverter, its a 6kW DEYE inverter and he uses a old 3kVA Honda generator, with very unstable frequency. What make very hard put it charging batteries. After a while working with it I found: Frequency gets big drops each time a load is connected/disconnected. Solution for it was: Start charging with 4A (200W) and increasing gradually 4A (200W) each time. For this generator I found that I can get until 1000W without have it gets too unstable. But for example at 900W it is a bit unstable. So basically I think when you use a weak generator is important do a "soft start" with it and test where is his comfortable power. Edited January 5, 20251 yr by JFFP94