May 14May 14 5 hours ago, jdido87 said:The battery has been on 64% all day. It was on 65% just prior to the solar taking over the house load. The installer updated the firmware as well earlier on but no change. The moment turn on the pool pump the solar generation increases to match the load but no excess solar are going to the batteries.Also, I enabled grid charge and turned off time of use. The batteries aren't charging from the grid either. This worked fine a day ago with the storms.Switch OFF lithium/BMS communication and use “Lead Acid/User Defined”.Manually enter safe lithium voltages ONLY as a short test. If the battery immediately starts charging the problem is definitely BMS communications or permissions.This is one of the fastest ways to isolate the fault.Based on the symptoms, my suspicion order would now be battery BMS charge inhibit1.CAN/RS485 comm issue after firmware update2.Max charge current accidentally set to 0A3.Corrupted TOU/force-charge stateLess likely: actual PV issueThe fact that PV instantly ramps when the pool pump starts is actually very good news the solar side itself appears healthy.Then Fully restart BOTH battery and inverterNot just the inverter.Proper sequence:Turn off PV isolatorTurn off AC breaker/inputTurn off inverterTurn off battery breaker/powerWait 5 minutesThen restart:Battery firstWait until battery fully bootsInverter secondAC inputPV lastThis often restores CAN/BMS comms.
May 15May 15 Author 18 hours ago, TaliaB said:Switch OFF lithium/BMS communication and use “Lead Acid/User Defined”.Manually enter safe lithium voltages ONLY as a short test. If the battery immediately starts charging the problem is definitely BMS communications or permissions.This is one of the fastest ways to isolate the fault.Based on the symptoms, my suspicion order would now be battery BMS charge inhibit1.CAN/RS485 comm issue after firmware update2.Max charge current accidentally set to 0A3.Corrupted TOU/force-charge stateLess likely: actual PV issueThe fact that PV instantly ramps when the pool pump starts is actually very good news the solar side itself appears healthy.Then Fully restart BOTH battery and inverterNot just the inverter.Proper sequence:Turn off PV isolatorTurn off AC breaker/inputTurn off inverterTurn off battery breaker/powerWait 5 minutesThen restart:Battery firstWait until battery fully bootsInverter secondAC inputPV lastThis often restores18 hours ago, TaliaB said:Switch OFF lithium/BMS communication and use “Lead Acid/User Defined”.Manually enter safe lithium voltages ONLY as a short test. If the battery immediately starts charging the problem is definitely BMS communications or permissions.This is one of the fastest ways to isolate the fault.Based on the symptoms, my suspicion order would now be battery BMS charge inhibit1.CAN/RS485 comm issue after firmware update2.Max charge current accidentally set to 0A3.Corrupted TOU/force-charge stateLess likely: actual PV issueThe fact that PV instantly ramps when the pool pump starts is actually very good news the solar side itself appears healthy.Then Fully restart BOTH battery and inverterNot just the inverter.Proper sequence:Turn off PV isolatorTurn off AC breaker/inputTurn off inverterTurn off battery breaker/powerWait 5 minutesThen restart:Battery firstWait until battery fully bootsInverter secondAC inputPV lastThis often restores CAN/BMS comms.Thank you very much. I will give this a go when I get home.
May 15May 15 On 2026/05/14 at 4:32 PM, jdido87 said:I find this really weird. 64% @ 55.19V with almost 1 amp going out. Something does not add upThe BMSbattery current limit to 0 might be stopping the inverter charging Edited May 15May 15 by Stefan Cornelissen
May 15May 15 1 hour ago, Stefan Cornelissen said:I find this really weird. 64% @ 55.19V with almost 1 amp going out. Something does not add upThe BMSbattery current limit to 0 might be stopping the inverter chargingYes I agree the 55.2v = 100% Soc. @jdido87 i will get the installer involved to get the batteries tested by the supplier. Insist on getting al 3 modules tested in parallel with communication enabled to ensure data packages are not dropped.Example of a healthy CAN network communication from a Victron System. Edited May 15May 15 by TaliaB
May 17May 17 Author Thanks guys.The issue was resolved. According to the installer the system detected moisture and the batteries shutdown to protect itself. Apparently he had a lot of similar call outs after the storms in Cape Town last week. I installed more vents in my solar room today. Going to get a smart thermometer and humidity sensor that intend to connect to and extractor fan to control the climate a bit better. New to all of this so the learning curve is steep. I tried to control temperatures in the solar room but forget about the humidity.
July 7Jul 7 Author Hi GuysI need some advise on the smart load function of the Deye inverter.I have excess solar pv capacity and would like to direct that to my electic geyser in order to save on gas. The main geyser for the house is gas. I enable the smartload feature however it shows that on 1w is going there. On the image the UPS is the house load and the house in the bottom right corner is the load of the electric geyser when turned it on. Can someone please help me make sense of this image. Why would the geyser load be indicated seperately from the house (UPS) load but also not in the smartload icon.I want to use my electric geyser as my solar array is completely oversized for my day to day needs. I wanted it this way for cloudy days. Ideally I do not want extra smart switch but rather just rely on the inverter to take care of all the switching. Edited July 7Jul 7 by jdido87
July 7Jul 7 38 minutes ago, jdido87 said:Hi GuysI need some advise on the smart load function of the Deye inverter.I have excess solar pv capacity and would like to direct that to my electic geyser in order to save on gas. The main geyser for the house is gas. I enable the smartload feature however it shows that on 1w is going there. On the image the UPS is the house load and the house in the bottom right corner is the load of the electric geyser when turned it on. Can someone please help me make sense of this image. Why would the geyser load be indicated seperately from the house (UPS) load but also not in the smartload icon.I want to use my electric geyser as my solar array is completely oversized for my day to day needs. I wanted it this way for cloudy days. Ideally I do not want extra smart switch but rather just rely on the inverter to take care of all the switching.It is normal to show a low 1W if in fact the value is zero.These are the options on a Sunsynk. The Deye might just use different descriptions. On this form untick the Gen option and tick the Aux Load setting. Also supply a value like over 500W for a test. This can the be changed later. Also try with a wider setting for between which levels PV should provide a output to the Aux port. Hope this helps. 41 minutes ago, jdido87 said:Hi GuysI need some advise on the smart load function of the Deye inverter.I have excess solar pv capacity and would like to direct that to my electic geyser in order to save on gas. The main geyser for the house is gas. I enable the smartload feature however it shows that on 1w is going there. On the image the UPS is the house load and the house in the bottom right corner is the load of the electric geyser when turned it on. Can someone please help me make sense of this image. Why would the geyser load be indicated seperately from the house (UPS) load but also not in the smartload icon.I want to use my electric geyser as my solar array is completely oversized for my day to day needs. I wanted it this way for cloudy days. Ideally I do not want extra smart switch but rather just rely on the inverter to take care of all the switching.
Tuesday at 12:295 days 57 minutes ago, jdido87 said:Hi GuysI need some advise on the smart load function of the Deye inverter.I have excess solar pv capacity and would like to direct that to my electic geyser in order to save on gas. The main geyser for the house is gas. I enable the smartload feature however it shows that on 1w is going there. On the image the UPS is the house load and the house in the bottom right corner is the load of the electric geyser when turned it on. Can someone please help me make sense of this image. Why would the geyser load be indicated seperately from the house (UPS) load but also not in the smartload icon.I want to use my electric geyser as my solar array is completely oversized for my day to day needs. I wanted it this way for cloudy days. Ideally I do not want extra smart switch but rather just rely on the inverter to take care of all the switching.The Smart load uses a separate port. Please confirm, or check whether the geyser is connected to the "GEN" port on the underside of the inverter.It might be that it's just connected as a non-essential load, ie. on the Main switch as a household load, but excluded from the backed up home circuits on the LOAD port.